What is considered a decent weather curve for running weather compensation?
Hi there,
I'm trying to get my system running as close to its design of max flow temp of 40C at -3C ambient.
However one of my zones isn't getting to desired temps.
I'm adjusting max and min flow temps to try and find a balance. Living rooms at 20C in slightly warmer temperatures feels ok, 21C in colder temperatures feels better, so really it's at the lower end of the ambient temps I want to hit 21C in living rooms.
Currently I've had to push the system up to 44C at -3C and 30C at 17C. Living rooms are mid 20s so pretty much there this morning (suspect be warmer later in the day), however that puts my max flow temp a good 10% above design (something I'm arguing with the installers on as we've had a rad upsize to try and fix this and it's still not great).
My question is, how bad/good is that weather curve? Is there a big cost implication over time with this?
I seem to recall people saying ideal is 35C at an ambient of 7C being a good marker. Currently my WC puts it at 37C at 7C ambient, so a good 2C above that. Having the WC at 35.5C at 7C ambient, living rooms are around 19.5-20C in mornings (I have a set back to avoid heat going upstairs and overheating us). So that's not too bad, but short of really crushing the WC not sure how to get a good balance.
Here's a screenshot of what flow temps my Grant ASHP runs at with ambient temps with current WC setting.
Something I'm trying to do is as I change the WC, I note the ambient and flow temps and subsequent room temps so over time can map the curve against what works. This is what I have so far:
Is that a viable approach?
It's really the 5C and below that it feels like the system needs a push. I haven't yet got a figure of when we wouldn't want any heating, 17C feels about right but may not be 100%.
To me it looks like your system is pretty much meeting the design.
You are having to increase the temp above the design as you have a setback for X hours overnight so you are having to put more heat back into the house above its heat loss to increase the temp.
40C flow temp at -3C is what it takes to maintain house temp, you would have to run hotter than that to increase the house temp which is what you are seeing in your curve.
Rule of thumb is that every 1C in flow temp is 2-3% difference in electricity consumption.
Thanks Gary, I'll then look at killing off the setback to see if can run it lower (I say it switches off, I have the hallway panel it go down from 23C to 20.5C between 10pm and 4:30am).
4C = 8-12% cost is not something I want to incur over time.
Main issue is upstairs performs so well and underfloor at rear of downstairs is fine, they barely call for heat and the higher flow temps makes it easy for upstairs to overheat, I'm having to use TRVs upstairs to stop that even with the panel set 20C in day to 19C at night. Could simply the effect of having upstairs lower than downstairs causes the increase to as the heat rises anyway?
Thanks Gary, I'll do that with the Drayton balancing key. I know the plumbers turned down the actual lock shield a bit as well so combined should really reduce it. I think main issue is upstairs is so oversized now as was just under with K1s that are now K2s.
Mean to say, I did do this at one point, but the other half kept complaining it was still too hot upstairs
So with a flow temp maxing at 42C, managed to get living rooms to almost 21C at points in the day. 44C started to overheat one of the rooms so some good news.
It's been around 6-7C ambient. At 7C – it runs at 36C so quite pleased with that.
That's by balancing down one living room further (that has the air locked rad), and 1 rad in the other living room slightly. And now no TRVs used upstairs (all set to Max). First floor rads are closed quite down heavily. The main bedroom still getting a bit too warm at 19.5-20C. I've now got that at 1/6 with Drayton Balancing key (not a TRV setting). So I'm hoping installers will come and sort the airlocked rad so I can pull the flow temp down slightly.
- 22 Forums
- 2,073 Topics
- 45.5 K Posts
- 42 Online
- 3,351 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Commencing on an ASHP Installation Process
@sheriff-fatman Thank you for a very detailed review of...
By ASHP-BOBBA , 10 hours ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
I believe there's another reason that network upgrades ...
By Transparent , 11 hours ago
-
RE: Why Your MCS-Certified Installer Might Not Be As Competent As You Think
I'm more than happy to try to help. Are you op...
By JamesPa , 15 hours ago
-
RE: What’s the modern take on advised types of insulation?
@jeff I am sorry @jeff if I have misunderstood what you...
By Toodles , 15 hours ago
-
RE: 5 Star Service from Havenwise
@sheriff-fatman Good post. I am also considering Hav...
By Morgan , 20 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@editor Cobbler’s Mantra that!
By Toodles , 21 hours ago
-
RE: Radiators downstairs are cooler at the bottom after ASHP install
@melonbuffet This is great assuming now the down stairs...
By ASHP-BOBBA , 2 days ago
-
RE: Renewables & Heat Pumps in the News
Australia Blue, the first wind farm in Western Victoria...
By Morgan , 2 days ago
-
RE: Flow rate discrepancy between ASHP and manifold
That's useful thanks, I hadn't seen that table before. ...
By AshRolls , 2 days ago
-
In principle I agree, @johnmo, but with provisos. The...
By Majordennisbloodnok , 3 days ago
-
RE: Heat pump installation and BUS Grant timings
@jamespa Thats how I understood it too. 🙂
By ASHP-BOBBA , 3 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@sallyl That sounds about right if they are re-filling ...
By Brendon Uys , 3 days ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
I would switch it off and see if anyone noticed. We use...
By Anonymous 5011 , 3 days ago
-
I wouldn't be so sure about that. Heat pump designers ...
By JamesPa , 4 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@toodles they're a rowdy bunch!
By Mars , 4 days ago
-
RE: Home energy storage & battery register
@jamespa To a certain extent, by exporting to the grid ...
By Toodles , 5 days ago
-
RE: Forum updates, announcements & issues
@editor Fairy Nuff Mars, I doubt that my ramblings woul...
By Toodles , 6 days ago
-
RE: Confusion about heat pump sizing
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 6 days ago
-
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 6 days ago