What is considered a decent weather curve for running weather compensation?
Hi there,
I'm trying to get my system running as close to its design of max flow temp of 40C at -3C ambient.
However one of my zones isn't getting to desired temps.
I'm adjusting max and min flow temps to try and find a balance. Living rooms at 20C in slightly warmer temperatures feels ok, 21C in colder temperatures feels better, so really it's at the lower end of the ambient temps I want to hit 21C in living rooms.
Currently I've had to push the system up to 44C at -3C and 30C at 17C. Living rooms are mid 20s so pretty much there this morning (suspect be warmer later in the day), however that puts my max flow temp a good 10% above design (something I'm arguing with the installers on as we've had a rad upsize to try and fix this and it's still not great).
My question is, how bad/good is that weather curve? Is there a big cost implication over time with this?
I seem to recall people saying ideal is 35C at an ambient of 7C being a good marker. Currently my WC puts it at 37C at 7C ambient, so a good 2C above that. Having the WC at 35.5C at 7C ambient, living rooms are around 19.5-20C in mornings (I have a set back to avoid heat going upstairs and overheating us). So that's not too bad, but short of really crushing the WC not sure how to get a good balance.
Here's a screenshot of what flow temps my Grant ASHP runs at with ambient temps with current WC setting.
Something I'm trying to do is as I change the WC, I note the ambient and flow temps and subsequent room temps so over time can map the curve against what works. This is what I have so far:
Is that a viable approach?
It's really the 5C and below that it feels like the system needs a push. I haven't yet got a figure of when we wouldn't want any heating, 17C feels about right but may not be 100%.
To me it looks like your system is pretty much meeting the design.
You are having to increase the temp above the design as you have a setback for X hours overnight so you are having to put more heat back into the house above its heat loss to increase the temp.
40C flow temp at -3C is what it takes to maintain house temp, you would have to run hotter than that to increase the house temp which is what you are seeing in your curve.
Rule of thumb is that every 1C in flow temp is 2-3% difference in electricity consumption.
Thanks Gary, I'll then look at killing off the setback to see if can run it lower (I say it switches off, I have the hallway panel it go down from 23C to 20.5C between 10pm and 4:30am).
4C = 8-12% cost is not something I want to incur over time.
Main issue is upstairs performs so well and underfloor at rear of downstairs is fine, they barely call for heat and the higher flow temps makes it easy for upstairs to overheat, I'm having to use TRVs upstairs to stop that even with the panel set 20C in day to 19C at night. Could simply the effect of having upstairs lower than downstairs causes the increase to as the heat rises anyway?
Thanks Gary, I'll do that with the Drayton balancing key. I know the plumbers turned down the actual lock shield a bit as well so combined should really reduce it. I think main issue is upstairs is so oversized now as was just under with K1s that are now K2s.
Mean to say, I did do this at one point, but the other half kept complaining it was still too hot upstairs
So with a flow temp maxing at 42C, managed to get living rooms to almost 21C at points in the day. 44C started to overheat one of the rooms so some good news.
It's been around 6-7C ambient. At 7C – it runs at 36C so quite pleased with that.
That's by balancing down one living room further (that has the air locked rad), and 1 rad in the other living room slightly. And now no TRVs used upstairs (all set to Max). First floor rads are closed quite down heavily. The main bedroom still getting a bit too warm at 19.5-20C. I've now got that at 1/6 with Drayton Balancing key (not a TRV setting). So I'm hoping installers will come and sort the airlocked rad so I can pull the flow temp down slightly.
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 206 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Configuring third party dongle for Ecodan local control
A 12 month subscription to Mel Pump will cost me £26, w...
By Sheriff Fatman , 14 minutes ago
-
@rikiarn At the risk of contradicting @jamespa!😳...
By Toodles , 23 minutes ago
-
RE: MELcloud scheduling misbehaviour
Without disagreeing with anything you've said there, @r...
By Majordennisbloodnok , 23 minutes ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@meehow Try to check the temperature of TH3 if your uni...
By ThunderMink , 4 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas Thanks Henri. I take your point, but feel that wh...
By DavidAlgarve , 4 hours ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
The Thermo Off (not Thermal Off) only relates to the la...
By trebor12345 , 4 hours ago
-
RE: Flow rate discrepancy between ASHP and manifold
Ok, I think I have got to the bottom of the problem... ...
By AshRolls , 5 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
@editor OVO: 'Sorry, we aren't installing heat pumps in...
By stevettweed , 5 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@bash — I also agree, an image based installation is th...
By cathodeRay , 6 hours ago
-
RE: Signenergy AI Mode - How long does it take to learn a usage pattern?
@grantmethestrength What I mentioned is just out of ...
By Batpred , 6 hours ago
-
RE: Electricity price predictions
I assume a lot of people have already seen this. I have...
By Jeff , 7 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Very true, that is the standard method (and the one I u...
By cathodeRay , 7 hours ago
-
RE: Our journey through Octopus tariffs 2020-2025
@tim441 guess "every little helps". I plan to let Sol...
By Batpred , 14 hours ago
-
RE: Solar panels on side of house to heat water
Mine is grey but perhaps with a few cans of white paint...
By Batpred , 15 hours ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
If it is combined with the BUS and they make it all goo...
By Batpred , 22 hours ago
-
RE: Advice on reading thermal images
@editor Thanks Mars, better price from the website and ...
By colinc , 1 day ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
To be blunt, I wouldn't choose. If we were to move to...
By Majordennisbloodnok , 1 day ago
-
RE: Diagnostic Data Needed for Repeatedly Failing Tesla Powerwall 3 System
Yes, some queries were raised on github recently: ...
By Batpred , 1 day ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@cold123456 Mitsubishi has failed to respond to my com...
By Ecoste , 1 day ago