What is considered a decent weather curve for running weather compensation?
Hi there,
I'm trying to get my system running as close to its design of max flow temp of 40C at -3C ambient.
However one of my zones isn't getting to desired temps.
I'm adjusting max and min flow temps to try and find a balance. Living rooms at 20C in slightly warmer temperatures feels ok, 21C in colder temperatures feels better, so really it's at the lower end of the ambient temps I want to hit 21C in living rooms.
Currently I've had to push the system up to 44C at -3C and 30C at 17C. Living rooms are mid 20s so pretty much there this morning (suspect be warmer later in the day), however that puts my max flow temp a good 10% above design (something I'm arguing with the installers on as we've had a rad upsize to try and fix this and it's still not great).
My question is, how bad/good is that weather curve? Is there a big cost implication over time with this?
I seem to recall people saying ideal is 35C at an ambient of 7C being a good marker. Currently my WC puts it at 37C at 7C ambient, so a good 2C above that. Having the WC at 35.5C at 7C ambient, living rooms are around 19.5-20C in mornings (I have a set back to avoid heat going upstairs and overheating us). So that's not too bad, but short of really crushing the WC not sure how to get a good balance.
Here's a screenshot of what flow temps my Grant ASHP runs at with ambient temps with current WC setting.
Something I'm trying to do is as I change the WC, I note the ambient and flow temps and subsequent room temps so over time can map the curve against what works. This is what I have so far:
Is that a viable approach?
It's really the 5C and below that it feels like the system needs a push. I haven't yet got a figure of when we wouldn't want any heating, 17C feels about right but may not be 100%.
To me it looks like your system is pretty much meeting the design.
You are having to increase the temp above the design as you have a setback for X hours overnight so you are having to put more heat back into the house above its heat loss to increase the temp.
40C flow temp at -3C is what it takes to maintain house temp, you would have to run hotter than that to increase the house temp which is what you are seeing in your curve.
Rule of thumb is that every 1C in flow temp is 2-3% difference in electricity consumption.
Thanks Gary, I'll then look at killing off the setback to see if can run it lower (I say it switches off, I have the hallway panel it go down from 23C to 20.5C between 10pm and 4:30am).
4C = 8-12% cost is not something I want to incur over time.
Main issue is upstairs performs so well and underfloor at rear of downstairs is fine, they barely call for heat and the higher flow temps makes it easy for upstairs to overheat, I'm having to use TRVs upstairs to stop that even with the panel set 20C in day to 19C at night. Could simply the effect of having upstairs lower than downstairs causes the increase to as the heat rises anyway?
Thanks Gary, I'll do that with the Drayton balancing key. I know the plumbers turned down the actual lock shield a bit as well so combined should really reduce it. I think main issue is upstairs is so oversized now as was just under with K1s that are now K2s.
Mean to say, I did do this at one point, but the other half kept complaining it was still too hot upstairs
So with a flow temp maxing at 42C, managed to get living rooms to almost 21C at points in the day. 44C started to overheat one of the rooms so some good news.
It's been around 6-7C ambient. At 7C – it runs at 36C so quite pleased with that.
That's by balancing down one living room further (that has the air locked rad), and 1 rad in the other living room slightly. And now no TRVs used upstairs (all set to Max). First floor rads are closed quite down heavily. The main bedroom still getting a bit too warm at 19.5-20C. I've now got that at 1/6 with Drayton Balancing key (not a TRV setting). So I'm hoping installers will come and sort the airlocked rad so I can pull the flow temp down slightly.
- 21 Forums
- 1,814 Topics
- 39.1 K Posts
- 17 Online
- 2,130 Members
Join Us!
Latest Posts
-
RE: Can you work an ASHP too hard?
As someone with an over-sized HP and the lower level of...
By HarriUp , 3 hours ago
-
RE: Best temperature wave form for best economy and efficiency .
I find the graphs somewhat hard to reconcile against th...
By HarriUp , 4 hours ago
-
RE: ASHP and how it should run and potential kw consumption?
You can help things by putting the DHW on to a timed op...
By Judith , 5 hours ago
-
RE: Vaillant Arotherm ASHP gets noisier when it gets colder outside
Quite possibly. As I mentioned above the 'ideal' produ...
By JamesPa , 5 hours ago
-
RE: Is it crucial to get flow temperatures with heat pumps right?
The bodies of TRVs usually have an arrow on them. If i...
By JamesPa , 5 hours ago
-
RE: Say hello and introduce yourself
Thank you Transparent ...much appreciated 😊 ...
By ivanhoew , 7 hours ago
-
RE: ASHP for small garage and workshop
@transparent Hello. This will not be covered on any gra...
By BobTSkutter , 8 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
Greg Jackson in the Times again just yesterday promotin...
By IanMK13 , 8 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Yeah we have a 40l buffer too. Problem is the App doesn...
By MikeH , 9 hours ago
-
Hi, has anybody got a step-by-step installation guide t...
By Potatoman , 13 hours ago
-
RE: Mitsubishi Ecodan 8.5kW Monobloc (FTC5) Defrost Mode
@gary no set backs. Yes see others in various forums ha...
By AlsoCold123456 , 13 hours ago
-
Looking for homeowner to join our podcast as a guest
We’re looking for a homeowner to join us on the Homeown...
By Mars , 18 hours ago
-
Our system is open no hydraulic separation. The volume ...
By Judith , 19 hours ago
-
RE: Mitsubishi Ecodan ASHP general set-up and efficiency
@gary Morning, yes, both of these are set to 3 on physi...
By ngillam , 19 hours ago
-
If the insulation isn’t wet you can over-cover it. It’s...
By Judith , 1 day ago
-
RE: Is My Midea Heat Pump Inherently Defective?
Sadly I think you are right, until someone develops a c...
By JamesPa , 1 day ago
-
RE: How much radiator capacity do I need for an air source heat pump?
Follow-up: it occurs to me that the difference between ...
By Simonwhiteley , 1 day ago
-
RE: The Definitive Guide to Weather Compensation and Curves for Air Source Heat Pumps
@judith thanks…. Every day a school day. tomorrows le...
By SUNandAIR , 1 day ago
-
RE: The good, the bad and the not that great – my heat pump installation
at the bottom of our installers invoice it said we were...
By NetDonkey , 2 days ago
Latest Topics
-
By Potatoman 13 hours ago
-
By DavidAlgarve 1 day ago
-
ASHP for small garage and workshop
By BobTSkutter 1 day ago
-
By ChandyKris 3 days ago
-
Nibe heatpump comms error when freezing
By Toody 3 days ago
-
Is this normal behaviour for my samsung ashp
By wawyed 4 days ago
-
Can you work an ASHP too hard?
By Simonwhiteley 4 days ago
-
By IRMartini 5 days ago