What is considered a decent weather curve for running weather compensation?
Hi there,
I'm trying to get my system running as close to its design of max flow temp of 40C at -3C ambient.
However one of my zones isn't getting to desired temps.
I'm adjusting max and min flow temps to try and find a balance. Living rooms at 20C in slightly warmer temperatures feels ok, 21C in colder temperatures feels better, so really it's at the lower end of the ambient temps I want to hit 21C in living rooms.
Currently I've had to push the system up to 44C at -3C and 30C at 17C. Living rooms are mid 20s so pretty much there this morning (suspect be warmer later in the day), however that puts my max flow temp a good 10% above design (something I'm arguing with the installers on as we've had a rad upsize to try and fix this and it's still not great).
My question is, how bad/good is that weather curve? Is there a big cost implication over time with this?
I seem to recall people saying ideal is 35C at an ambient of 7C being a good marker. Currently my WC puts it at 37C at 7C ambient, so a good 2C above that. Having the WC at 35.5C at 7C ambient, living rooms are around 19.5-20C in mornings (I have a set back to avoid heat going upstairs and overheating us). So that's not too bad, but short of really crushing the WC not sure how to get a good balance.
Here's a screenshot of what flow temps my Grant ASHP runs at with ambient temps with current WC setting.
Something I'm trying to do is as I change the WC, I note the ambient and flow temps and subsequent room temps so over time can map the curve against what works. This is what I have so far:
Is that a viable approach?
It's really the 5C and below that it feels like the system needs a push. I haven't yet got a figure of when we wouldn't want any heating, 17C feels about right but may not be 100%.
To me it looks like your system is pretty much meeting the design.
You are having to increase the temp above the design as you have a setback for X hours overnight so you are having to put more heat back into the house above its heat loss to increase the temp.
40C flow temp at -3C is what it takes to maintain house temp, you would have to run hotter than that to increase the house temp which is what you are seeing in your curve.
Rule of thumb is that every 1C in flow temp is 2-3% difference in electricity consumption.
Thanks Gary, I'll then look at killing off the setback to see if can run it lower (I say it switches off, I have the hallway panel it go down from 23C to 20.5C between 10pm and 4:30am).
4C = 8-12% cost is not something I want to incur over time.
Main issue is upstairs performs so well and underfloor at rear of downstairs is fine, they barely call for heat and the higher flow temps makes it easy for upstairs to overheat, I'm having to use TRVs upstairs to stop that even with the panel set 20C in day to 19C at night. Could simply the effect of having upstairs lower than downstairs causes the increase to as the heat rises anyway?
Thanks Gary, I'll do that with the Drayton balancing key. I know the plumbers turned down the actual lock shield a bit as well so combined should really reduce it. I think main issue is upstairs is so oversized now as was just under with K1s that are now K2s.
Mean to say, I did do this at one point, but the other half kept complaining it was still too hot upstairs
So with a flow temp maxing at 42C, managed to get living rooms to almost 21C at points in the day. 44C started to overheat one of the rooms so some good news.
It's been around 6-7C ambient. At 7C – it runs at 36C so quite pleased with that.
That's by balancing down one living room further (that has the air locked rad), and 1 rad in the other living room slightly. And now no TRVs used upstairs (all set to Max). First floor rads are closed quite down heavily. The main bedroom still getting a bit too warm at 19.5-20C. I've now got that at 1/6 with Drayton Balancing key (not a TRV setting). So I'm hoping installers will come and sort the airlocked rad so I can pull the flow temp down slightly.
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 32 Online
- 5,656 Members
Podcast Picks
Latest Posts
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 3 hours ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 5 hours ago
-
RE: Anyone still weathering it out with Agile?
Yes, but now try finding a working phone box….
By Majordennisbloodnok , 20 hours ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 23 hours ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 1 day ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 2 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 3 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 3 days ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 3 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 5 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 5 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 5 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 6 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 6 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 6 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 7 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 1 week ago