Posted by: @sarahI have also (last night) changed the comp curve to 45 (from 40) - it's not too warm outside today - so I will see if that makes a difference. I've never been able to get this right in the 8 years I've had it - it either uses so much electricity when running that we are at the stage where we have to decide if we can afford to run it or when I make changes it doesn't heat up the area. I really want to like the ASHP but I never have.
I'm assuming that you are not too technical, is that correct?
Could you please post photo's of all the equipment within your system so that we can get some idea about how it has been installed.
When you mention '3 boxes', are these thermostats?
@sarah Hi, the highlighted "-30" your compensation curve is fine. The two highlighted parameters on the graph are just indicating the curve at the marker point, which is the black spot at the bottom left hand corner. You can move this point along the axis using arrow keys, and the highlighted readings will update accordingly. Hope this helps.
Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6+4kW hybrid inverter; 20kWh LFP battery storage
When our Ecodan system was first commissioned we had a low flow rate, very similar to this. The engineer simply cleaned the in-line strainer, and since then our flow rate has been over 20l/min. The strainer gets checked on each annual service and it's remained clean.Posted by: @sarah@gary picture of flow rate
-- Attachment is not available --
I just thought it worth mentioning in case you have something similar going on, especially if your strainer hasn't been checked for some time.
Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6+4kW hybrid inverter; 20kWh LFP battery storage
@derek-m yes not too technical - at least for heating systems!!! I'm having to learn about it though. Yes three thermostats in each room (they are all on same level) - the "slab" (about 70/80 sqmetres) is one level separated with three manifolds for each space (living area/bedroom and bathroom) - there are doors separating the room but they are not always closed.
In the Eng menu there is a pump speed setting from 1 to 5. What is yours set to. If you increase it and go back to the running info what does the flow rate number change to.
How are you running the system hest pumps needs to be on for hours all day especially with ufh if yours is deep in the concrete you will never get the concrete up to temp if you don’t run it for long periods
@sarah With the pump set to 5 the flow rate you are achieving is too low for the heat pump to be working correctly, it won't be transferring enough heat to the UFH circuit.
When the heat pump is running if you go back to eng menu and into thermistor readings this will show us what the flow and return temps of the heat pump are and the outside temp at the time that will help clarify, but at the moment it looks like the heat pump flow rate is too low.
Yes you are correct but room temp is the temp of the location where that controller is.
Is it currently heating hot water as flow and return aren’t in line with your WC curve.
If so check again when it’s doing heating
THW5 is your HW tank temp and TH7 is the outside temp by the heat pump
- 26 Forums
- 2,102 Topics
- 46.2 K Posts
- 71 Online
- 3,388 Members
Join Us!
Latest Posts
-
RE: Ecodan consuming 100kwh per day in new build!!!
From what you say about the radiators upstairs it does ...
By JamesPa , 3 hours ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer pleased you found it!
By JamesPa , 4 hours ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 6 hours ago
-
@heacol, if you're around, can you please provide some ...
By Mars , 9 hours ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 9 hours ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 22 hours ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 22 hours ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 1 day ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 1 day ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 2 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 2 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 2 days ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 4 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 4 days ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 4 days ago
Members Online
No online members at the moment