Vaillant Arotherm Settings for New Installation
Im just helping my brother in law with his new 7kW Arotherm installation. I looked at a few youtube videos and found my way around the controller but Im unsure about a couple of things and the COP of the unit for heating is currently poor at about 3 (DHW is OK at 2.5).
Firstly the current room temperature on the controller seems to bear no resemblance to the actual room temperature. (see pic). Is this an issue or just annoying?
Next the unit is set up for pure weather compensation, but i can see the option for using room temperature modulation as well, has anyone any experience of this?
The current curve is 0.85, am I right in assuming that the upper and lower limits of the WC can be set separately to the curve?
Any other tips welcome 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Just to say, that we have managed to set up the unit now. 22C target indoor temperature and a heat curve of 0.6. High internal temp but the wife is a freezer and room temperature is a constant cause of marital strife.
Currently running on pure weather compensation so I would still be interested to hear from anyone who uses the room temperature compensation feature.
Heating COP appears low still, but Im not sure how much the Vaillant reporting system can be trusted after reading a few online reports.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Hi there,
Would need a few more details of your BIL's install. Radiators, UFH, number of emitters, how many zones, size of property, size of water tank, number of pumps in the system, LLH etc.
- How are you calculating the COP? Vaillant use a different formula from everyone else.
- The Vaillant reporting seems pretty accurate in my experience, well for us anyway.
- We only use pure weather compensation, we even go as far as using the adaptive heat curve, letting the Vaillant software decide the best heat curve for the property.
- Regarding the temp reading, ours is always bob on. Were you sat with the sensocomfort unit in your hands or on your lap for a while, they are quite sensitive units. We've had first hand experience of this.
- As for adjusting the heat curve end points, this is not possible with Vaillant as far as I am aware.
Hope this helps.
Drew
Hi Drew. Thanks for the reply. I’ll post his installation details asap.
The work is neatly done and all the radiators were changed as per the installers spec.
There is no LLH or buffer but they did insist on a volumiser and are using glycol instead of water and anti freeze valves.
Im getting the COP from the app but am aware of the quirk with the way Vaillant describes their energy figures and hence the odd COP calculation.
I haven’t seen the adaptive curve feature but have found a formula for calculating the correct curve for the desired room temperature. I can see how this all works now, very different from the Samsung setup.
I wondered about handling the controller and the temperature reading but that didn’t seem to be the issue. In fact it seems to have stabilised now.
If the displayed COP is correct then that is a worry and needs some investigation.
thanks Mark
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
sounds like you are slowly getting there. From the checks I have done, the COP in the app seems to be fairly accurate, others have confirmed this to. We used to have to do the calc using the figures in the controller. Once you have the system info it will be good to get a look at it for you. Are the radiator valves all fully open?
Drew
@drew-pa Ive attached the performance estimate Drew, that is all I have. There is no UFH.
Also attached are some images of the installation. Other than the things I've already mentioned, the only other thing I wouldnt have done was run the external pipework as far as they did. BTW its white because his wife insisted on them covering it with tape 🙂
There doesnt seem to be anything obvious as to why his COP is so low, despite the settings, the flow temperature over the last couple of days was under 40C so I would have thought he should have a COP of about 4 judging by the arotherm specs.
My sceptism about the reported COP was based around discussions on Protons for breakfast, Energy Stats Uk and a discussion on the openenergymonitor forum. If its accurate, then its a worry.
Not all the radiator valves are fully open but several are as I was trying to balance the system a bit better and warm up some cold radiators. Annoyingly the installers dont seem to have bothered.
Mark
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Can you open all valves, and reduce flow temp further? Various units have run at low 30s or upper 20s in the past days.
CEO and co-founder at HavenWise
Ive opened all but the bedroom radiator valves, which they want to be cooler. Im running my Samsung at about 42C flow at the moment and still getting a COP of 3.8-4.0 so the Vaillant should really be doing a lot better than it is even at a FT of 38C.
Ive attached the COP as reported by the app and the Arotherm COP figures.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Comparing different units in different homes is not very straightforward...
Is the Vaillant cycling a lot?
CEO and co-founder at HavenWise
Apologies for the delay.
How is the unit set up to operate? Are they running it a few times a day, or running it manually? We found ours works at its most efficient if it is running in manual mode(water and heating). Just set the temp we want and leave it. Might be worth a try, also try lowering the heat curve a little.
Drew
These are our figures for the month of April. With our settings, and specific to our property of course.
@hcas Hi , I appreciate the problems with comparing different systems, but this installation is relatively simple with no buffer/LLH. The estimated SCOP from the installers is 3.65 for heating so you would expect to beat that in the shoulder heating season.
I have no way of monitoring if it is cycling, but the heat pump isnt oversized for the property so I would be very surprised it it was. Apart from a couple of issues I wouldnt have done (eg gycol), it looks like a good install so Im very surprised to see such a low COP.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 21 Forums
- 1,811 Topics
- 39 K Posts
- 102 Online
- 2,124 Members
Join Us!
Latest Posts
-
ASHP for small garage and workshop
Hello everyone, Just joined the forum and have chipped ...
By BobTSkutter , 37 minutes ago
-
@lucia It would be interesting to know the volume of yo...
By BobTSkutter , 57 minutes ago
-
RE: Is My Midea Heat Pump Inherently Defective?
Sadly I think you are right, until someone develops a c...
By JamesPa , 2 hours ago
-
RE: Is it crucial to get flow temperatures with heat pumps right?
... in theory! If they are all (close to ) perfectly ...
By JamesPa , 2 hours ago
-
RE: How much radiator capacity do I need for an air source heat pump?
Follow-up: it occurs to me that the difference between ...
By Simonwhiteley , 2 hours ago
-
RE: Mitsubishi Ecodan ASHP general set-up and efficiency
@gary Agreed, installer needs to look. I did up the op...
By ngillam , 3 hours ago
-
RE: Can you work an ASHP too hard?
I agree - I think a heat pump is more of a marine diese...
By cathodeRay , 3 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
Meant to add this but have been buried under piles of w...
By Lucia , 5 hours ago
-
RE: The Definitive Guide to Weather Compensation and Curves for Air Source Heat Pumps
@judith thanks…. Every day a school day. tomorrows le...
By SUNandAIR , 6 hours ago
-
RE: The good, the bad and the not that great – my heat pump installation
at the bottom of our installers invoice it said we were...
By NetDonkey , 7 hours ago
-
RE: Samsung E911 intermittent issue
Just a quick update. It looks like it may be the actua...
By NetDonkey , 10 hours ago
-
RE: What to Expect During Your First Winter with a Heat Pump
I wish I had known about you before I had the pump fitt...
By Richard Smith , 12 hours ago
-
RE: Mitsubishi Ecodan 8.5kW Monobloc (FTC5) Defrost Mode
@cold123456 appreciated this thread dates from a while ...
By AlsoCold123456 , 12 hours ago
-
RE: Controversial opinions - pure weather compensation, buffer tank, heat loss, oversized heat pumps
That is really interesting what you mentioned about con...
By benson , 13 hours ago
-
RE: R290 install location and future of R32
@toodles thanks for that toodles. I was hoping you migh...
By SUNandAIR , 1 day ago
-
RE: Totally bewildered with my ECO4 heat pump installation
Do you have a Sensocomfort? it looks like
By Judith , 1 day ago
-
RE: Say hello and introduce yourself
Mars hello there. I plan to go air to water and then i...
By BobTSkutter , 1 day ago
-
@transparent We had one chappie from SGN call at the do...
By Toodles , 1 day ago
-
RE: Reusing existing radiators
@chandykris just give them a good wash out before fitti...
By bontwoody , 1 day ago
Latest Topics
-
ASHP for small garage and workshop
By BobTSkutter 37 minutes ago
-
By ChandyKris 1 day ago
-
Nibe heatpump comms error when freezing
By Toody 2 days ago
-
Is this normal behaviour for my samsung ashp
By wawyed 3 days ago
-
Can you work an ASHP too hard?
By Simonwhiteley 3 days ago
-
By IRMartini 3 days ago
-
R290 install location and future of R32
By AndrewJ 4 days ago
-
hum/whine from Wilo circulation pump
By grumpidoc 5 days ago