Vaillant aroTherm 15kW ASHP - problems with council
@mbcool, 7m is a fair old distance. With our ASHP, stepping back 5m reduces sound greatly. Did your neighbour object?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
There are different ways of defining loudness and it's crucial which one is used. Sound pressure level (SPL) is what you hear and what you measure. It depends on the distance from the source and the environment. Sound power level (SWL) is a theorectical measure that depends on neither. It is not measurable but calculated from the sound pressure level.
The SPL of my Ecodan is 53 dB at 1m. It's SWL is 67 dB.
I think MCS says to use SWL but the difference between them is huge in sound terms. Also, doubling the distance from the source theoretically reduces dB by 6. So theoretically @mbcool's 49dB wouldn't even pass if it were 14m away (49-6=43). That seems harsh and would probably rule out a lot of ASHPs out there. I think it's likely that actually measuring the SPL would give a lower number than @mbcool's calculation. If it were 53 dB at 1m like my ASHP, then at 2m it would be 47, at 4 it would be 41, etc. It wouldn't be long before it was just background noise.
Quite a good write up here
https://www.parkerjonesacoustics.com/insights/articles/sound-pressure-sound-power
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 25 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Replacing Worcester oil boiler with an ASHP
Daikin Software Update. I received a software update...
By JulianC , 13 minutes ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
@guydeb The guidelines are possibly written to be defin...
By Toodles , 2 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Yes Octopus only have the £9 a month service plan for t...
By NJT , 2 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
@allyfish Dogs have owners - Cats keep staff. You are o...
By Toodles , 2 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 2 hours ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 8 hours ago
-
RE: Midea ASHP – how to set weather compensation
I think it is a bug in the code, it comes on even when ...
By cathodeRay , 22 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 24 hours ago
-
RE: Buffers, hot water and cooling
@jamespa Your reasonably close! Especially with warmer ...
By dgclimatecontrol , 1 day ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 1 day ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 2 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 2 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 2 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 2 days ago
-
RE: Solar Thermal DHW and ASHP
I was originally contemplating a solar thermal installa...
By jamespetts , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
My system installed in July 2024 has produced 6.4mWh in...
By jamespetts , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@judith thanks for your suggestions. Starting from col...
By GrahamF , 3 days ago
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 3 days ago