Samsung ASHP scheduling help
@broadsman the #2093 setting should be "Room Temp. only ON / OFF" for the Gen 6 controller.
Please make sure #2091 and #2092 are set to "not use" and any external third party thermostats are disconnected.
I did get an error myself but it looked like a flow interruption if I remember correctly. I think it is caused by the change in mode, I just pressed OK and it cleared then everything was running ok. The error for me was "Indoor (200000) / E121" for your info.
Regards
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
@mike-h I do have the 12Kw Samsung Gen 6 model.
Just to clarify, if you go to the Zone screen you should have the target room or water temp on the left and "Water Outlet" and "Indoor" temperatures on the right. These indicate the actual temperatures the system is seeing
Regards
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
@mike-h my pump does switch off when the room temp goes 0.5C above my target temp but this only happens with solar gain or my hand is near the controller too long. Most of the time it appears to keep the room at the target temp of 20.5C and the pump running continuously.
Here is my firmware version info
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
Posted by: @mike-hI wonder if your ability to keep room temperature at +/- 0.3C is because you have got your water law settings perfectly set rather than feedback from the controller.
I did a little experiment last night and changed my water law setting to a flat 37C (WL-1) to verify if the controller configured as the thermostat still used this water law or calculated its own water temperatures based on the outside temperatures. It appears that the controller still uses the water law set in WL-1 in my case. The pump continuously runs due to the On /Off only setting in #2093 but the water outlet temperature basically stabilised at 37C for an outside temperature of 6.5C (should be around 44Cish).
In my case @mike-h your assumption is correct and my water law is set about right and is still being used.
This is not the behaviour implied in the video I posted in an earlier posting which indicates the pump "looks at the outside temperature and decides the required temperature to set your radiators to to achieve the indoor temperature set point. When the temperature is reached the pump is reduced to maintain the internal temperature set point" (not verbatim). The radiator temperature seems to still be based on the water law settings for the Gen 6 not some implied clever internal feature.
Apologies for misleading anyone 🙂
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 13 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Say hello and introduce yourself
Hi, Thank you for the reply and the associated link, ...
By jarlatheoin , 9 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@heat-pump-newbie Yes you need F Gas engineers like us ...
By dgclimatecontrol , 14 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 18 hours ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 20 hours ago
-
RE: Anyone still weathering it out with Agile?
Yes, but now try finding a working phone box….
By Majordennisbloodnok , 1 day ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 2 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 2 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 3 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 4 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 4 days ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 4 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 5 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 6 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 6 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 6 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 7 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 7 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 1 week ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago