Refrigerant Leak: A Wasted Year of Heating
Before I go off into a rant about my heat pump experience I have to say generally I am pleased I’ve had a heat pump installed! I love the even heat of the house, it is saving me money ( i have batteries and solar so can take advantage of cheaper tariffs ) and of course green.
However I should have seen the bad omens from the start! First day of installation we had a cold snap and it started to snow! However by the end of the week heating was up and running and house was once again warm! I still had some issues pipes weren’t properly insulated and the MMI Wi-Fi connection wasn’t working. Few months later after lots of head scratching and visits MMI was replaced and all was working OK bar poor performance, HW 1.3 COP, Heating 2.6 COP, when questioned i was told this was ok! What ever i did with the weather curve didn’t seem to make any difference.
So when in January I had my first Daikin service I wasn’t surprised when the engineer knocked on the door saying the unit had a refrigerant leak, he showed me the rusty coloured oily substance at the bottom of the unit and came back a few days later to re charge the refrigerant. Apparently i only had 1.2 kg instead of the 3.6 kg required. He indicated this was more than likely supplied like this and a nut probably not tightened up enough in the factory.
Since then my HW COP is about 2 and my heating COP 3.5 , also the pump is much quieter. The only thing I’m still not completely happy about is I have a Daikin pre plumbed tank which is running in the buffer configuration which I’m thinking of changing to a volumiser when I’ve finished with the heating this year. The buffer tank seems so small (30lt ) and the temperature going to the radiators is 5 c less than pump leaving water temperature. I’ve only one zone and really can’t understand what the buffer tank is doing apart from making the pump have to work harder. Would be interested to know if anyone else has changed their buffer tanks to volumiser and what outcomes were achieved?
Hi @john-castle , I’m new here too. I also have a Daikin. It’s the altherma 3 8kw. My system is a little different from yours because I have a mixergy tank rather than the Daikin, because of low water pressure. When originally set up I had a buffer tank and to go with that a second pump, which you may have too. This caused all sorts of conflicts and there has been a reconfiguration removing the second pump and converting the buffer to a volumiser. The quiet is now deafening, as they say. That second pump was a noisy beast. I have noticed a marginal uptick in cop.
There are lots of briefing papers on this site about various things,and the heat geek site can be very helpful too. It appears that unless you have a very large property or maybe an unusual configuration buffers are no longer considered helpful and to the contrary are a burden on the system and reduce efficiency. I should add as a bye the way, the second pump would not have had its power consumption measured by the heat pump, so whatever reduction in power I had from that being removed is also a bonus.
like you I just have one zone and Trv’s are set to max, hopefully meaning they aren’t interfering with anything.
what size pump do you have? And what is your heatloss calc and associated temp range?
@john-castle, I’m surprised that with that level of refrigerant loss, you weren’t seeing any error codes on your control panel. Refrigerant loss often manifests as unusual or erratic errors.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Mars, so was the Daikin engineer but no errors came up on the MMI ! My understanding is there isn’t a pressure gauge on these units so unless you see a leak ( rusty oil like substance ) you wouldn’t know the state of your refrigerant! Slightly worrying as he seemed to think it came out of the factory like this. I asked the question about checking the refrigerant when serviced and my understanding from what he said the only way was to weigh it. Having said that I am deaf and rely on a cochlear implant for hearing and don’t always catch everything correctly!
@john-castle thanks for the explanation. My only reason for asking is because defrost errors (in the absence of defrosting) can be an indicator that there's been a loss of refrigerant which is what I covered to some degree here:
In our case, we didn't have a refrigerant leak, it was the sensor, but it could have been the refrigerant.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@terry1812 unfortunately I have the 9kw pump ( if only I new what I know now ) I know a 8kw pump would work more efficiently for my house. It’s been running for a little over a year now with only a third of the refrigerant and not once has the house felt cold! We have a wood burning stove in the lounge which we like to use on cold winter nights , none of the installers take this into account ( I assume regulations say you can’t) so consequently I have a pump that’s over sized and can’t modulate down below 900w consumption! I had three surveys and they all came in about 8-8.5kw.
The buffer tank on the pre plumbed Daikin unit is quite easily turned into a volumiser and only appears to be about 30ltrs and appears very little separation of outlets, basically if the leaving water temperature of pump is 40c the pump flow pipe is 39.5, flow to radiators is 35c return from rads is 30c , return to pump 35c. So basically the heat pump at 40c heats the buffer to 35c. I’ve only got one zone, loads of big radiators design temp 45c @ -3 can’t understand why I shouldn’t be sending the heat straight from the pump to the radiators and so not having the pump having to work so hard.
@editor interesting, so I think now the pump frosts up differently, it appears to be a finer frost on it. So the first time since we had the pump ( just over a year ) my wife comes running up to me in the office panicking saying the pump is still broken I think it’s on fire it’s smoking and feels hot! Might be a coincidence but this never happened before the refrigerant was changed. The pump would have a thicker ice on it would drip more but not steam!
@john-castle Yes that does sound problematic, I very rarely touch 900w and if I do I am wondering what the problem is? Who did your install. There is a guy who had an octopus install and they swapped out his 9kw for the 8kw. If your installers aren’t helpful you could talk to Daikin, they may be able to help you reconfigure. Did you get the grant? One of the issues with the grant can be that if your heat loss comes out as yours did, you have to put a pump in at least equal to the heatloss. Which when you are borderline like you are is tough. Tough because amongst other things there are factors that Don’t get taken into account with the heat loss. So for example if you have heat retaining curtains, and use them, the heatloss avoided can be quite significant. However they can’t take it into account because they are part of the fabric of the house.( Pun intended). So the next occupants may not have them…etc etc. The other reason it’s problematic is because esp with the jump from the 8kw model to the 9kw, is that practically you only need that little extra for the bottom end of the temp zone, which is a very short period. Also because they have to quote 21c ( either for total house or certain parts depending on age of property) for MCs rules and to get the grant.
Could be worth a conversation with the installer or Daikin, and with Daikin I think you do have cause for complaint/ leverage because of the refrigerant issue. Also did they give you details of the heatloss calc, have you verified it?
@terry1812 it was one of bigger installers, not octopus or BG. The cost was very competitive, may be I should have paid more and gone with a valiant 7kw which one company quoted. However the price difference would have taken 10 years plus to recuperate. I’m finding if I’m not careful I’m getting obsessed with the pump efficiency which in fact if I got it closer to a cop of 4 ( at the moment it’s 3.5 ) would financially make a difference of less than £100. I’m fairly confident changing the buffer into a volumiser during the summer will make a 10-15% increase in efficiency. I have to partly drain the system down as the installers put the inline filter in the wrong way round anyway. Probably do it myself really finding it all to much effort and agro to get trades to sort out sadly. I’ve done quite a bit of plumbing in the past so fairly confident! I want bother to try and get it changed as once it’s reached the desired temperature it just switches off for a hour or so till temp drops again and isn’t using much more electricity than an 8kw unit. Will probably report back next year on what difference the change made!
@john-castle Yes, I too have become somewhat obsessed, trying to comprehend what should in essence be something simple. As soon as external temps reach 15-16c , hopefully by mid April I’ll turn the heating off and put it back on again end Sept early Oct. just let it deal with the occasional demand for DHW.
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 173 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@bash, I agree with @batpred here. The various paths fo...
By Majordennisbloodnok , 17 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — your flow rate still shows a step pattern, al...
By cathodeRay , 19 minutes ago
-
RE: Signenergy AI Mode - How long does it take to learn a usage pattern?
@batpred yeah I have fully integrated the system into h...
By Grantmethestrength , 1 hour ago
-
RE: Our journey through Octopus tariffs 2020-2025
@tim441 guess "every little helps". I plan to let Sol...
By Batpred , 7 hours ago
-
RE: Solar panels on side of house to heat water
Mine is grey but perhaps with a few cans of white paint...
By Batpred , 8 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
What I amazed is how easily they assume the 7.5k is a f...
By Batpred , 8 hours ago
-
RE: Configuring third party dongle for Ecodan local control
Update: I'm getting refreshed views of data showing me ...
By Sheriff Fatman , 9 hours ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
@jamespa Apologies I did know that but I seem to have r...
By Sim0n0 , 11 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas Hello Henri, I know that we have had an exchange ...
By DavidAlgarve , 12 hours ago
-
RE: MELcloud scheduling misbehaviour
@downfield my understanding is that you can have a maxi...
By Richard24738 , 14 hours ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
If it is combined with the BUS and they make it all goo...
By Batpred , 15 hours ago
-
RE: Electricity price predictions
Before I dive into the issue of a strategy which helps ...
By Transparent , 17 hours ago
-
RE: Advice on reading thermal images
@editor Thanks Mars, better price from the website and ...
By colinc , 20 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
To be blunt, I wouldn't choose. If we were to move to...
By Majordennisbloodnok , 21 hours ago
-
RE: Diagnostic Data Needed for Repeatedly Failing Tesla Powerwall 3 System
Yes, some queries were raised on github recently: ...
By Batpred , 21 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@cold123456 Mitsubishi has failed to respond to my com...
By Ecoste , 21 hours ago
-
RE: Grant Aerona Short Cycling
@steam-powered I'm currently running 30@-7 23@15 so cur...
By damonc , 1 day ago
-
RE: What a Bad Heat Pump Installation Looks Like
That's pretty impressively incompetent. In our develo...
By Steelbadger , 1 day ago
-
RE: Marginal pricing and UK electricity costs
@judith I just realised he’s the guy with the ‘minimum ...
By Lucia , 1 day ago