Observation about radiators and weather compensation
@derek-m - yes, it does, thanks, apart from one question/observation: what happens if the secondary pump isn't running, because the room stat isn't calling for heat? Unlikely if things are cold enough to need defrost cycles, but not impossible. At that point there will be nowhere for the heat pump to draw heat from to effect the defrost cycle.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderay@derek-m - yes, it does, thanks, apart from one question/observation: what happens if the secondary pump isn't running, because the room stat isn't calling for heat? Unlikely if things are cold enough to need defrost cycles, but not impossible. At that point there will be nowhere for the heat pump to draw heat from to effect the defrost cycle.
I'm afraid that is one question that I cannot answer, because I don't know how your system is wired and configured to operate. All I can say is that if you have followed previous advice, and have your system set in WC mode with the thermostat set high as an over-temperature stop, then the secondary pump should be running.
I suppose that you could always ask your installer, Freedom or possibly Graham Hendra who used to work for Freedom.
@derek-m - I currently have the system running mostly but not exclusively in WC mode. The room stat is set high-ish (19 degrees) and most of the time the system runs in WC mode (as can be seen in the Midea app) but every now and then the room stat does trip (stops calling for heat) and so the secondary circulating pump stops. But this tends to happen when it is mild and there has been solar gain, ie conditions in which a defrost cycle is not going to happen.
The only time I can see when a defrost cycle could happen when the secondary circulating pump is off is when the system is in DHW mode, but presumably that isn't a problem, as the defrost cycle can get its heat from the hot water in the tank, though the water may not be that hot (which is why the system is in DHW mode). I also have the DHW on a timer (only runs between 1300 and 1400 daily) so it generally will be a warmer part of the day.
Today I am going to go over to 100% weather compensation ie set the room stat very high (30 degrees) and adjust the curve on the Midea controller and perhaps slightly close some of the upstairs TRVs to keep the rooms at design temps. I expect it will take a few days to get it just so, if that can ever be achieved. Once things are good enough, I will then do another monitoring run and see how the COP looks - it may not be 100% accurate, but running the same methodology on the same system should be a good enough relative indicator - to check I have a tolerable COP.
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 16 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: ASHP heat output monitoring
@carlo the 16kw rating refers to output.. afaik? So w...
By Tim441 , 6 hours ago
-
Anyone still weathering it out with Agile?
Being curious, I have continued to monitor the daily ra...
By Toodles , 12 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 16 hours ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 1 day ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 1 day ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 1 day ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 1 day ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 3 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 3 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 4 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 4 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 5 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 5 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 6 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 1 week ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago
Members Online
No online members at the moment