Noob question - sizing of heat pump
Hi all I hope you can help. We have a 5 bed home mostly solid wall with parts of it that were built in the 1700’s. Under the eco4 scheme we have qualified for ashp and internal wall insulation. The heat loss calculation states we need a hump with an output of 16.6kw when it’s -3degrees C but they have proposed to install a Samsung system HHSM- G600016-1 which as far as I can see can’t achieve this output. This system also seems to have been around since 2019 and therefore not as efficient as the latest system. Would there be a reason for this? I am wondering whether a cascade of a newer system comprising a 12 & 6kw system would be better?
as I say I am a noob so any info would be great
Was the heatloss done based on the property’s current fabric or with the internal insulation taken into account? Another point worth mentioning is that regardless of the above, MCS calculations tend to overestimate the heat loss.
Smart Tech Specialist with Octopus Energy Services (all views my own). 4.4kW PV with 9.5kWh Givenergy battery. 9kW Panasonic Aquarea L ASHP
Thanks for your reply. the heat loss was done taking into account the new internal wall insulation.
Posted by: @dannyboyHi all I hope you can help. We have a 5 bed home mostly solid wall with parts of it that were built in the 1700’s. Under the eco4 scheme we have qualified for ashp and internal wall insulation. The heat loss calculation states we need a hump with an output of 16.6kw when it’s -3degrees C but they have proposed to install a Samsung system HHSM- G600016-1 which as far as I can see can’t achieve this output. This system also seems to have been around since 2019 and therefore not as efficient as the latest system. Would there be a reason for this? I am wondering whether a cascade of a newer system comprising a 12 & 6kw system would be better?
as I say I am a noob so any info would be great
A Samsung HHSM- G600016-1 won't produce anything like 16.6kW at -3. The link below suggests more like 12-14kW at these low temperatures.
You should ask your potential supplier to explain why they are recommending an ASHP that can't deliver the calculated heat loss. What is the flow temperature and room temperature at -3 deg ambient in your heat loss calculation?
If your heat loss really is 16.6kW at -3 deg, by the time you factor in hot water and defrosts (the dip in the graphs in the link) you are likely to need a backup heating system or some extra jumpers.
The newer ASHPs may be a bit more efficient but a well designed system matched to your heat loss is more important.
Feel free to share more details of your quote if you want further comments.
From what I have been researching that is exactly what I was thinking. They did at one point suggest cascading two pumps and the latest generation ones seem to be output stable despite external temp or that may be marketing guff. The flow temperature is supposed to be 50 degrees C and internal is 20degrees C.
Posted by: @dannyboyFrom what I have been researching that is exactly what I was thinking. They did at one point suggest cascading two pumps and the latest generation ones seem to be output stable despite external temp or that may be marketing guff. The flow temperature is supposed to be 50 degrees C and internal is 20degrees C.
The ones that can deliver what it says on the badge when it's cold outside will be able to deliver more under the right conditions. A 14kW Ecodan will deliver 14kW when it's cold and can do quite a bit more - over 16kW - under very favourable conditions. Other makes may be similar; I'm only quoting Mitsubishi because I have one. It can all be very misleading.
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 52 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Samsung Heat pump with Yonos Pico circulating pump running all the time
Looks like you have a 25L buffer vessel, so I'm guessin...
By Old_Scientist , 4 hours ago
-
@bontwoody you’re joking! This story gets worse and wor...
By Mars , 5 hours ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
If you do suggest you consider repurposing it as a 2 po...
By JamesPa , 6 hours ago
-
-
RE: Say hello and introduce yourself
Fully agree with @cathoderay. My journey took 2 years ...
By JamesPa , 7 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@editor Agreed. There is another point to be made h...
By JamesPa , 15 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
Tim, Yes ChatGPT thought I could get another...
By Mike Patrick , 15 hours ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
No problem, @richdorm; glad it helps.
By Majordennisbloodnok , 17 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
If that makes you feel happier then go ahead, but it wo...
By JamesPa , 18 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I do already have the same basic setup, all room influe...
By cathodeRay , 18 hours ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK. You dont say whether it is from the feeds to/from ...
By JamesPa , 19 hours ago
-
RE: How can I programme a setback for my Samsung Gen6 8kW heat pump?
Yes, and probably also Adia although the latter has a m...
By JamesPa , 1 day ago
-
@editor I am all in favour of provocati...
By GrahamF , 2 days ago
-
RE: How to Understand Wiring Up a Heat Pump
Morning, On top of what everyone else I would deffo loo...
By Grantmethestrength , 2 days ago
-
RE: Sizing a heat pump: Save me from my headache
Got the results back from the one we’re ...
By Mikeatthezoo , 2 days ago
-
RE: Renewables & Heat Pumps in the News
Thanks Lucia. I'll set aside some time to go through th...
By Transparent , 3 days ago