@iantelescope this is very interesting but I am at a loss as to what you are trying to prove so please explain 🙂
Posted by: @iantelescopeSwitching and Water Flow rates can be Safely controlled by the PWM inputs rather than Power Relays!
I think you misunderstand regarding the suggestion of using a relay. The relay is to switch the power to the pump on and off not control its speed. You are trying to get a static speed in your secondary pump to achieve the required flow rate around your radiator circuit. The pump needs to be switched on and off by your Samsung controller in order to separate the dependency of the pump from your Honeywell thermostat.
The Samsung controller output is only capable of supplying up to 100W so you need to use a relay to switch the power on and off for a pump that consumes power greater than 100W otherwise it will damage your control board. The pump relay, via this Samsung output, will only be switched on and off in sync with your heat pump compressor etc, which in turn powers your pump on and off, it is not used to produce a pulse train to control the pump speed, merely the electrical power to the rotor.
I am not sure how this secondary PWM pump was controlled before you used your Arduino but I hazard a guess it was running a constant speed when first installed?
If a constant speed configuration is not possible with your PWM pump then you may have to consider a fixed speed pump replacement such as a Wilo pump on which you can manually set the required head pressure and get the desired flow rate.
Regards
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
It would have probably been more useful to show the inlet and outlet temperatures on the primary side of the PHE along with the inlet and outlet temperatures on the secondary side. All on the same chart if possible.
Flow rate and DT are inter-related, though it may be useful if I try to explain using voltage (DT), current (flow rate) and variable resistance to represent heat emitters.
Consider a system that has 10 radiators (10 x 10 Ohm resistors) all connected in parallel. If the supply voltage is 10 volts then 1 amp will flow through each resistor, producing a total supply current of 10 amps. The total amount of power being dissipated by the resistors will be V x I, giving 10 x 10 = 100 watts.
If each resistor is now reduced to 5 Ohms, then at a supply voltage of 10 volts, the total supply current would increase to 20 amps, giving a total power dissipation of 200 watts. To keep the power dissipation at 100 watts it would be necessary to reduce the supply voltage from 10 volts to 5 volts.
If the above is now consider in a slightly different way, in that the current (flow rate) is fixed at say 10 amps, but that the resistance is varied to vary the amount of power dissipated, with the volt drop across the resistors indicating the produced DT.
For a power dissipation of 100 watts the produced volt drop would be 10 volts.
For a power dissipation of 50 watts the produced volt drop would be 5 volts.
For a power dissipation of 20 watts the produced volt drop would be 2 volts.
It is probable that your charts are showing that a similar quantity of thermal energy (power) is being dissipated, but by changing the flow rate (current), the DT (volt drop) is being changed.
Changing the flow rate in either the primary or secondary side of the PHE will change the relevant DT.
For Efficiency , Hot Water Heating DOES NOT NEED the Radiator Motor Water Pump to be AUTOMATICALLY USED.
Many thanks @derek-m
Sensors .....more & More & more!
I am building a permanent box to increase my DS18B20 Temperature Array to 12 X DS18B20 and another Arduino .
I will measure and control the Secondary , Radiator Delta_t ...........in due course.
In limiting the Flow rate , I have greatly increased the Primary Delta_t.
Note that the PWM input to the Grundfoss Motors was used to reduce and control the Flow rates NOT the RELAYS.
Parallel Grundfoss Motor Operation:
For efficiency when Heating Hot Water the Radiator Motor Water Motor SHOULD NOT BE AUTOMATICALLY USED.
Parallel Grundfoss Motor Operation WOULD BRING BOTH PUMPS into operation when ONLY ONE MAY BE REQUIRED!.
Note the different Amplitudes, reflecting the Single or DUAL Motor Operation.
The Thermostat SIGNAL does NOT ALWAYS start the Compressor OR the Primary Grundfoss Water PUMP.
Thermostat Cycling and Weather Compensation Cycling:
During a Cold February my Heat Pump Cycle Time is controlled by BOTH Weather Compensation AND my Thermostat.
The following graphs show the Power , Heat PUMP Output Water Flow Temperature and Radiator Output Water Flow Temperature on 7th February 2023.
The 10 Shorter 10 minute "Short Cycling " is here vividly contrasted with the 1 Hour Cycling Time set by the Weather Compensation Thermostat.
My Conclusion is that Weather Compensation is perfectly capable of controlling BOTH THE Primary AND SECONDARY,RADIATOR Grundfoss Motors!.
I further conclude that , in the absence of my Thermostat 20 minute "Cycle Time " my Heat Pump would revert to Weather Compensation.
The Buffer tank Controversy
Given that the Buffer tank appears to provide a Winter "Cycle Time " of one hour, I should Replace the Thermostat with a Simple ON-OFF Thermostat !
Water FLOW RATE Control
Given the proven operation of the PWM in increasing the Heat Exchanger Delta_t WHY are RELAYS BEING Advocated ?
Case 1 , PWM OR Case 2 , RELAY ??
Why SHOULD I USE CASE 1 , the Pulse Width Modulation , PWM Grundfoss Motor Control to control the Primary Water Flow rate as illustrated in the Installation manual?
Why SHOULD I USE CASE 2 , Relay Control , to control the Primary Water Flow rate , as illustrated in the Installation manual?
PWM proving to be MUCH Simpler & Safer !!
@technogeek and @derek_m
Why , on earth are SAMSUNG, Still , in the 21st century using RELAYS ??
My Grundfoss Motors can be Switched OFF AND ON using a PWM Signal :
My Grundfoss motor can return its status:
When used , the PWM Grundfoss motors , case 1 in the SAMSUNG Installation Manual the 240ac are permanently ON ( see installation manual)
Hysteresis:
The PWM signal when operating at 4 khz or 256 us has a Hysteresis from 91% , or 233 us to 95% , or 243 us .
Overheating safety limit :
The PWM signal when operating with a signal < 10% , or 25 us , is fixed at Maximum Speed ensuring maximum speed during Signal failure.
When Signal noise is between 0 and 10% the Motor is driven at maximum speed cooling the water , and motor.
Feedback:
The PWM Motor returns the Alarm and motor Status with current consumption. This is NOT currently used by SAMSUNG.
Speed Control Linearity :
The PWM is linear between the OFF Speed , 256 us Pulse width and the ON Pulse Width of <10 us.
Why , on earth are SAMSUNG, in the 21st century STILL using RELAYS ??
A Simple ON-OFF No-nonsense Radio Controlled Thermostat ?
Where Can I Get a Simple ON-OFF Radio controlled Thermostat ?
Most of the on line Thermostats, on offer, do not have sufficient Technical Information, being aimed at "simplicity of operation " , "Looks" , and "simplicity of installation" !
Samsung's Embarrassment Required:
Following a E-mail exchange with a anonymous Samsung Engineer, he was of the frank opinion that Samsung would Do Nothing about my "Installation " unless embarrassed !.
Without a dose of embarrassment Samsung would , probably, demand payment for their services!
He further commented that 80% of the "Faulty installations " were caused by incompetent "installers",
, with the remaining "probably caused" , as in my case , by Samsung.
I have a Samsung Heat Pump designed by nobody , built by nobody, taking four months to install!
The NIC / MCS "regret that they can DO NOTHING , given that my "installer" has been "STRUCK OFF SEVERAL TIMES in the last TWO Years".
Struck off, and repeatedly re-instated by the MCS themselves!
@derek--m & @technogeek
Have you a Heat Pump with a Heat Exchanger , a Buffer, using BOTH AC Pump AND PWM ?
Controlling Water Samsung Water Pumps:
Water Flow in Samsung Heat Pumps can be controlled by either
1) The INV Option, Case 1 in the Installation manual:
Control: The Water flow is here controlled by a Pulse Width Modulated , PWM signal from a socket on the MIM--E03CN Control PCB.
Range: The Water flow rate is continuously , and linearly , variable between OFF and ON.
Power: The AC power is continuously ON being supplied from pin B6 , Continuous Live , and B7 Neutral.
PWM Range:Driven at 4 Khz , ON has a Pulse width of between 0 an d 25 us, while OFF is a Pulse Width of between ~240 and 256 us.
Cost : PWM Motors are more costly than AC controlled motors..
Safety: PWM Systems, being Semiconductor Technology, Should be much more reliable and safe compared to mechanical Relays used by the AC Pump option:
PWM Motors have Feedback , currently NOT USED by Samsung.
Water Power : To increase water flow rates beyond the current motor power a replacement PWM motor , with increased power would be required.
Zero Check: The Samsung control board checks for excessive power when commanded to switch OFF , issuing a E912 Error if water flow is greater zero.
Run check : The Samsung control board checks for Power less than ~15 lpm when commanded to switch ON , issuing a E911 Error if water flow is less than 15 lpm.
2) The AC Pump option, case 2 in the Installation manual:
Control: The Water flow is here controlled by an Electromechanical Relay on the Control Board.
Range : The Water flow rate is either ON or OFF. No Flow rate variation is possible.
Power: The AC power is continuously Switched being supplied from pin B8 , Live , and B7 Neutral.
Cost : AC Motors are cheaper, and more readily available compared tp PWM controlled motors.
Safety: AC Relays Systems, being Electro-mechanical , are much Less reliable with reduced and safety compared to PWM Solid state controls.
Water Power : To increase water flow rates beyond the current motor power another motor can be operated in parallel with the current motor. Another Relay would, however be required.
Zero Check: The Samsung control board checks for excessive flow rate when commanded to switch OFF , issuing a E912 Error if water flow Rate is greater than zero.
Run check : The Samsung control board checks for Power less than ~15 lpm when commanded to switch ON , issuing a E911 Error if water flow is less than 15 lpm.
Who else has a system like mine, A Heat Pump with a Heat Exchanger , a Buffer with BOTH AC Pump AND PWM used?
Posted by: @iantelescopeHave you a Heat Pump with a Heat Exchanger , a Buffer, using BOTH AC Pump AND PWM ?
I have a 12Kw Samsung connected to standard radiators via a low loss header. The primary water circuit to the low loss header is pumped using a PWM Grundfoss pump and the secondary circuit pumped to the radiators is a fixed speed Wilo pump set with an approx 10 metre head as it is supplying 13 rads in a 5 bedroom house.
Samsung is capable of controlling 1 PWM pump only and 1 fixed speed pump simultaneously.
Regards
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
Again Many Many thanks............................@technogeek
My Samsung , fitted with a PWM Grundfos motor is fed from a Faulty PWM Unloaded Output signal.
This is the PWM signal when Not connected to the Grundfos Motor:
Clearly the Signal exists But never drops to Zero!
When connected to the Grundfos motor I get :
Clearly , my PWM Source is Faulty never dropping to Zero Volts.
The Grundfos PWM Input to the Primary PWM motor works flawlessly, when sourced from an Arduino::
As does my Radiator , Secondary when fed from an Arduino :
I speculate that Someone has tried to connect the PWM Source on the Samsung PCB to something other than a motor !.
I will have to replace the Samsung PCB to get the PWM System working .
The Secondary , Radiator Pump will have to use either the Thermostat connected to the 240 ac
OR a Arduino Generated Control again ONLY switched ON / OFF by the Thermostat .
many thanks
Can you measure the DC PWM Reference pin voltage on your Samsung PCB?
Hi @technogeek:
Given that my Samsung PCB produces a passable output PWM signal , is it possible that the "PWM Reference" pin on my Samsung PCB is wrongly connected?
Could you measure the DC PWM Reference pin voltage on your Samsung PCB?
My PWM Signal is being killed by my Grundfos!.
Hi Again, thanks for your patience!
What are your Samsung Inverter Pump settings Field bits, 4051 :
1) Used or Not used
2) 70 % Modulation
3) 100 % Modulation
4) Target Delta T
5 ) Control factor
My "Home made" Arduino continues to generate a similar Inverter motor performance.
My Samsung inverter Motor control continues to fail when driven by my Samsung PWM PCB output .
My PWM Signal is being killed by the Grundfos motor PWM itself.
any ideas?
P.S. It is NOT Cable polarity !
@iantelescope I could be completely wrong when I say this but the first 2 photographs look to me as the classic floating neutral. That maybe why it never gets to zero in the first photo and gets pulled up to the rail when connected to the motor in the second. Is your neutral correctly wired to the correct pcb terminal and making a good connection?
My system is set to 100% modulation for PWM and a delta T of 5 degrees C. Leave the control factor at default
Regards
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 14 Online
- 5,662 Members
Join Us!
Podcast Picks
Latest Posts
-
Sanity check please. Battery storage and inverter sizing.
I had one installer essentially wanting to install a ti...
By AdamK , 7 hours ago
-
Why so many sigenergi installer recommendations?
I’m curious as to why I’m seeing so many YouTube vids a...
By AdamK , 7 hours ago
-
RE: Rodents! A word of warning for heat pump owners
The gaps and holes have reduced on heat pumps over the ...
By dgclimatecontrol , 13 hours ago
-
RE: Ecodan & MelCloud scheduling
I couldn't agree more. I might go so far as to change t...
By Majordennisbloodnok , 13 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: EGP01 Manufacturer: Samsung Model: 8K...
By EGP01 , 16 hours ago
-
Thanks for the heat geek info. I've fitted my own heat ...
By bontwoody , 17 hours ago
-
RE: Does anyone have experience of a smart water meter?
Just to give a sense of scale, I've used the CCW water ...
By Majordennisbloodnok , 18 hours ago
-
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 2 days ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 3 days ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 4 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 4 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 4 days ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 5 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 6 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 7 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 7 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 1 week ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 1 week ago