Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Minimum ASHP outputs?
Posted by: @sunandairSo to summarise:- Of the 365 days of the year our heat pumps will try to operate for 160 days at less than 20% capacity. (If they can cope with the modulation, that is.)
On the other side of the coin - although not the subject of this topic - the heat pump will operate at greater than 80% capacity on only 12 days. Although an installer can be expected to design a system capable of meeting the heating requirements on these days, other influences are likely to lead to over-specification. Without over-specification, the customer may be prepared to accept a handful of days when heat pump is struggling (e.g. to avoid a planning application, avoid a double-fan unit, avoid radiator replacement, etc). This is a variant of the '80/20 rule' - 80% of what you want for 80% fewer issues.
Posted by: @sunandairPosted by: @robsWhat was the total output capacity of your radiators at a flow temperature of 30C? Is it less than the minimum output of your heat pump at 30C flow temperature?
At a 21kw combined rad load
30c LWT = 1.785kw total output
35c LWT = 3.47kw total output
The first issue I recall, was to notice that the manufacturers correction charts do not go down low enough or fine enough to take account of 5c circuit DT (temp drop) and 30c LWT.
...
So after a bit of trial and error I was left thinking the 30c outlet temperature at under 2 kw output it was the reason for the cycling we encountered.
Yes, your figures correlate well with your heat pump having a minimum output of about 3kW at these outside temperatures. Have you tried your heat pump at a 34C flow temperature?
Posted by: @robsyour figures correlate well with your heat pump having a minimum output of about 3kW at these outside temperatures. Have you tried your heat pump at a 34C flow temperature?
At first I tried 32c for about 10days. It was ok but still cycling a bit too much. So I took it straight to 35c.
But you make a valid point. A small reduced flow temp, by 1 or 2 degrees, may give improved efficiency without increased cycling.
I will do this and let you know how I get on. Thanks for your useful observations.
Behaviour of compressor is subtly different as flow temperature is dropped to 34 and 33c. The original lowest flow temp of 35c as set on weather compensation which was the set flow temp for all outdoor Ambients 10c and above.
At 34c the cycling increases to 4 per hour with short 5 minute pauses.
At 33c the cycling drops to 3 per hour but the temperature drop appears to be done by creating longer pauses of 10 minutes.
In all cases the flow temperature still registers 35 or 36c. It appears to use variable pauses in operation to reduce the average energy input to 33c.
This operation seems to still be within acceptable Mitsubishi operating tolerances.
To clarify, these graphs are from a radiator only system with a total RAD DT50 capacity of 21kw. Which is greatly reduced to 3.4kw when operating at flow temp 35c. These graphs are specific to our setup and not necessarily typical.
- 27 Forums
- 2,774 Topics
- 65.4 K Posts
- 790 Online
- 7,177 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
@mrkfm, I’m definitely not trying to put anyone off get...
By Mars , 7 hours ago
-
RE: Cooling using an air to water heat pump
I agree, which is why I am currently resisting buying a...
By JamesPa , 7 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
Is there any expected time frame for an update to be ab...
By Singlespeed , 11 hours ago
-
RE: Why are ASHP installs so expensive?
Posted by: @springswood I confess to becoming a litt...
By Rob of York , 12 hours ago
-
Analysis of the economics of switching to an A2W ASHP compared to other heat sources
This post aims to analyse the economics of installing, ...
By Rob of York , 16 hours ago
-
RE: Cooling with air to water heat pumps
@editor does that mean you have to have two separate ex...
By mrkfm , 1 day ago
-
RE: Starting Our Heat Pump Journey: 1962 build 3 bed detached house
Posted by: @ian-s Could always use the money saved o...
By Rob of York , 1 day ago
-
Depends on what controls the pump! Thats the whole poi...
By JamesPa , 2 days ago
-
The positive reviews keep coming in for Britain's Heat ...
By Mars , 2 days ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
I have one of these fitted which also allows you to reg...
By Old_Scientist , 3 days ago
-
RE: Recommendations in Ely (Cambs) area for Full setup checks on Nibe HP setup for House.
If they can't don't give up. Heat pumps are, in reali...
By JamesPa , 4 days ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes that's what would happen by turning down the lsv to...
By JamesPa , 4 days ago
-
RE: Grant R290 DHW Cycle Interuption
It looks like some sort of short pre-run. The question...
By JamesPa , 4 days ago
-
RE: Cascade System or larger single unit
@renewables345 I would say if it a new build it’s no mo...
By Aventus Eco , 4 days ago