Kev-M's ASHP Performance
The next round is to try and use weather compensation and thermostats together. Here’s what happened.
The theory is that setting a compensation curve that would normally make the house a few degrees too warm and limiting it by on/off thermostats will reduce cycling while keeping the house at a steady temperature. The aim is to get something like the below 45 deg set flow but with lower flow temps. Although even this didn't prevent all cycling.
But what actually happens is the weather compensation and thermostats just end up getting in each other's way. The thermostat causes ons and offs but in between there is a lot of cycling. This is because the ASHP will stop heating when either the thermostat temp (21 deg in my case) or the weather comp flow temp is reached and won’t start until the thermostat calls for heat and the weather comp flow temp is low. So the thermostat calls for heat and the ASHP starts heating. But the target flow temp is reached before the thermostat set temp, so the ASHP stops, even though the thermostat is still calling for heat. The flow (and the house) cool down a bit then the ASHP kicks in again. And repeats this until the thermostat set temp is eventually reached, at which time the ASHP stops, whether or not its flow temp is reached. The house then cools from 21.5 deg or so to 20.5 deg or so, the thermostat calls for heat and does it all again.
The below graph illustrates the above. You can see the 5am start up, the steady state running, the gaps when the thermostats switch the ASHP off and the 3pm DHW peak. There are only four periods of ASHP heating but these all include as much cycling as letting the ASHP run constantly.
The obvious way to stop the cycling is to increase the flow temp so that it requires a high enough output/flow, a bit like the fixed flow above. To get this to work the compensation curve is going to have to be very flat, not a million miles from the fixed flow.
But does it matter? Cycling for me is about twice an hour or so and in these conditions my COP is good. This was a warmish day using weather compensation only. I’d rather get the cold weather performance right...
But I like tinkering so I have now bumped up the warm end of the curve so that it’s 42 @ -2 and 33 at 20 and the thermostats are controlling the room temp. I'll report back.
This is what happened. There is almost no cycling. The outside temp was 0-12C. Is it better/cheaper? The house temperature varies more, which isn't as good. I don't know if it's cheaper but I suspect there won't be much in it. Although there are periods when the ASHP is off, the flow temp is several degrees higher than it needs to be. It's interesting to see the COP is low at very low ASHP consumption. This is because the ASHP itself is slightly less efficient at very low outputs and also because with the way COP is measured in my set up, the consumed energy is everything; the pumps, FTC controller the immersion (if it's used) and these are running all the time the ASHP is.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 56 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat Pump Damage on install - useable or dealbreaker?
I wouldn't personally say it's an excessive demand. It ...
By benson , 5 minutes ago
-
-
RE: Electricity price predictions
@diverted-energy sounds like good tariff for you. Octop...
By JulianC , 30 minutes ago
-
RE: Who’s Caved and Switched the Heating On Already?
In the last week, the external temperature in south Man...
By GrahamF , 2 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 3 hours ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 3 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 5 hours ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 7 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 7 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 8 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 1 day ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 2 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 3 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 3 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 3 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 3 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 3 days ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 4 days ago