Is it KISS or constant – weather compensation vs. set flow temperature?
Away at present. Hence the delay. Will get back asap.
Cliff
Okay. I have setup the system using just weather compensation. There is something called 'thermal blockade' on my smart controller which turns off the stat rather than turn it to maximum.
I'm going to video the heat curve but at the moment it starts at 18(20c) and runs to 45(-30). -5c = 33c. The OAT is 10c and the system is stable at 19.5c. I tried a lower curve but the pump cycled as expected, 25c is the lowest it will go.
What's struck me is how cool the rads are. They don't feel they could warm anything! But they do of course. Now we are at the end of March the system's not going to be tested at lower temperatures which to me is the breaker.
To be continued
Cliff
Posted by: @cliffhangerWhat's struck me is how cool the rads are. They don't feel they could warm anything! But they do of course. Now we are at the end of March the system's not going to be tested at lower temperatures which to me is the breaker.
Indeed. Its weird at first but you get used to it and actually it is more comfortable because the temperature gradients are less.
There is a school of thought pursued by some installers that having cool radiators leads to call outs (which is probably true). Thus some installers force a minimum FT of 37, which is roughly the point at which radiators feel warm. This of course increases the cost to the householder.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
We ran our radiations at anywhere between 30-35C over winter. At 30C I struggle to tell they are on. If I place my face over the top of the radiator, I can just about feel warm air convecting on my face. At 32C I can feel they are warm to the touch, and at 35C they are (relatively) positively hot!
I still walk around touching the radiators to see if they are on - I just need to trust the room thermostat, which doesn't lie.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
I had to laugh at this as I do exactly the same thing, I read on here someone explain it well, the body is running at 36c so anything less will feel cold. As I explain to friends it is actually magic that heats my house!
Kind Regards
Si
——————————————————————————
Grant Aerona3 13kW
13 x 435w + 13x 480w Solar Panels
Sigenergy 10kW Inverter
16kW Sigenstor battery
Hi
Just as an aside. My system is heating only.
What is the best way of turning a weather compensation setup off in the summer? I thought of turning the stat back on to its lowest temp, in this case 10c. Won't go any lower.
Or setting the heating curve to its lowest?
Cliff
@cliffhanger Mine has a 'space heating off' setting! Otherwise turn down thermostat if you have one and it's set up to call for heat
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 41 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
That's a valid point, of course nobody wants the inconv...
By downfield , 22 minutes ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
For best results with induction hobs use stainless stee...
By Scalextrix , 35 minutes ago
-
RE: Who’s Caved and Switched the Heating On Already?
Central heating still switched off and will be until Oc...
By AllyFish , 3 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Please read to the very end of this post, I shift my po...
By JamesPa , 3 hours ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 3 hours ago
-
RE: Midea ASHP – how to set weather compensation
I think it is a bug in the code, it comes on even when ...
By cathodeRay , 17 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 19 hours ago
-
RE: Buffers, hot water and cooling
@jamespa Your reasonably close! Especially with warmer ...
By dgclimatecontrol , 21 hours ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 1 day ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 2 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 2 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 2 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 2 days ago
-
RE: Solar Thermal DHW and ASHP
I was originally contemplating a solar thermal installa...
By jamespetts , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
My system installed in July 2024 has produced 6.4mWh in...
By jamespetts , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@judith thanks for your suggestions. Starting from col...
By GrahamF , 3 days ago
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 3 days ago
-
RE: DESNZ doing a survey which asks the right questions!
Without a survey their only source of data is probably ...
By JamesPa , 3 days ago