Getting it right (Hopefully) – ECO4 Grant Aerona 13kW
I have an ECO4 installation. Grant Aerona 13kW output ASHP driving 14 brand new radiators and all new pipework plus new DHW tank and 10 total (3.6Kwh) solar panels. The installation and removal of 37 year old oil boiler was completed in 3 days the standard of work was good although much making good of old radiator fixing points required by me. Handover was perfunctory at best and initially we were running it using the digital wireless room stat which was calling and not calling frequently. We set it at 20°C. System has worked fine since install but when temps dropped to around zero living room would not rise above 18°C. The radiator for the sitting room on initial delivery was too big (sat above window ledge) so a smaller one had been fitted. Called installer and they sent a surveyor, turns out the original survey had reported the size of the window as smaller than it was. He recalculated and said we needed a bigger radiator which was fitted after about 2 week, since when temps have been fine. On discovering this forum realised we were probably running it incorrectly as the constant on off from room stat never gave the heat pump chance to settle. Have now opened all the TRV's (except conservatory that would be like heating Norfolk county!) and set thermostat to 30°C so constantly calling. Took my courage in my hand having read the manual and stuff on here had a look at settings as installed which were as follows: Max outgoing water temp in Heating Mode (Tm1) 50°C: Min Outgoings Water Temp in Heating Mode (Tm2) 30°C: Minimum outdoor air temp corresponding to Max outgoing water temp(Te1) -2°C: Maximum outgoings Air temperature corresponding to maximum (surely that SHOULD be a 'minimum?) outgoings water temp (Te2) 25°C. This was giving us an indoor temp of 23° plus.
Adjusted as follows (28/01/2025) Tm1 40: Tm2 28; Te1 -2: Te2 20. Still slightly too hot. Adjusted (30/01/2025) Tm1 38; Tm2 27; Te 1&2 as before. Slightly cold now so adjusted (01/02/2025) Tm1 39 everything else as 30/01/25. This is giving 19.5/20°C all over house comfortable for us. We run the system 24/7 ISH although around 2130 I do set the system back to 18°C using ECO setting on thermostat until the economy 7 kicks in at 0030. As this is 0.06p per unit compared with 0.37p per unit day rate I am quite happy for it to consume a few units heating the property again. By the time we come down it is back to 19.5° so quite happy. Bedroom is always comfortable.
I have not had sight of the heat loss calculation for the property but it seems to be working ok. We have an electric AGA which without fail consumes 30 units per night. So taking that out of the equation and background use of approx 6 units per day (I have kept usage records for many years on a spreadsheet so these are accurate figures) the ASHP is consuming around 25 - 40 units per day depending on OAT. This equates to approx £8 to £15 per day averaging about £10 so January electricity bill will be £300. Do these figures KWh not costs seem about right. The high figures were when OAT was around -7 overnight.
The PV panels are doing very little as they are facing East/West (5 each way) and shaded in winter by a higher east /west ridge immediately to the south (where the very low sun is!!!). Come late Feb March they will get a much better sight of the sun. Currently they run the house when ASHP is idle i.e. light, Tele, fridge etc. if the light is good..
Well that enough from me feel free to comment for my consideration, thank you in advance. Every day is a learning day. Mark B
- 26 Forums
- 2,275 Topics
- 50.9 K Posts
- 138 Online
- 5,936 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
@treewizard Very interesting, thanks - although I hav...
By GrahamF , 5 hours ago
-
RE: My DIY Heat Pump installation
…and I’m assuming the “more” option on the right of the...
By Majordennisbloodnok , 5 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Yup, totally understand, @gmuzz. However, fitting Ope...
By Majordennisbloodnok , 5 hours ago
-
RE: Who's your electricity provider and what's your tariff?
So I’m still with E.ON Next, and I received a pretty sn...
By Mars , 6 hours ago
-
RE: Heat Loss v Outside Air Temperature
I think this can be dealt with without the need for OAT...
By JamesPa , 6 hours ago
-
RE: First time wall mounting an ASHP
what you need to do is everything you can to remove the...
By ASHP-BOBBA , 7 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Aira 12kW - @gmuzz
By Gmuzz , 7 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
ASHP switched off per specialists guidance. Seems the b...
By Crimson , 8 hours ago
-
RE: Faulty Clivet heat pump out of the box
@steveimpey that is disappointing. I am inclined to agr...
By benson , 10 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj Bear with me, this is my first post on this fo...
By KevH , 11 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
Is the ZD is a bit of a marketing ploy? has the it bee...
By BWood , 15 hours ago
-
For anyone interested in levelling up their understandi...
By Mars , 16 hours ago
-
RE: Solar panels on side of house to heat water
Thankyou for the brain dump, all very worthy items. W...
By paultheheating , 16 hours ago
-
Ecodan HW temp setting set itself to 40C
This morning I noticed that the HW was lukewarm and MEL...
By downfield , 17 hours ago
-
RE: Is Your House Warmer Upstairs Than Downstairs?
I suspect its mainly that you get the views. Upstairs...
By JamesPa , 17 hours ago
-
RE: Mitsubishi Ecodan FTC7 Legionella date set
The next run date/time is determined by the settings co...
By F1p , 18 hours ago
-
@treewizard is this not the electrical pulse that keeps...
By ASHP-BOBBA , 1 day ago
-
RE: Samsung Gen6 and Havenwise ........
I am no expert on this but on your gen 6 controller onc...
By Alfapat , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk these are called roll top rads, they were still ...
By AgentGeorge , 2 days ago
-
If the Vaillant is a 7kw unit I’d avoid. Quiet outside ...
By AdamK , 2 days ago