Getting it right (Hopefully) – ECO4 Grant Aerona 13kW
I have an ECO4 installation. Grant Aerona 13kW output ASHP driving 14 brand new radiators and all new pipework plus new DHW tank and 10 total (3.6Kwh) solar panels. The installation and removal of 37 year old oil boiler was completed in 3 days the standard of work was good although much making good of old radiator fixing points required by me. Handover was perfunctory at best and initially we were running it using the digital wireless room stat which was calling and not calling frequently. We set it at 20°C. System has worked fine since install but when temps dropped to around zero living room would not rise above 18°C. The radiator for the sitting room on initial delivery was too big (sat above window ledge) so a smaller one had been fitted. Called installer and they sent a surveyor, turns out the original survey had reported the size of the window as smaller than it was. He recalculated and said we needed a bigger radiator which was fitted after about 2 week, since when temps have been fine. On discovering this forum realised we were probably running it incorrectly as the constant on off from room stat never gave the heat pump chance to settle. Have now opened all the TRV's (except conservatory that would be like heating Norfolk county!) and set thermostat to 30°C so constantly calling. Took my courage in my hand having read the manual and stuff on here had a look at settings as installed which were as follows: Max outgoing water temp in Heating Mode (Tm1) 50°C: Min Outgoings Water Temp in Heating Mode (Tm2) 30°C: Minimum outdoor air temp corresponding to Max outgoing water temp(Te1) -2°C: Maximum outgoings Air temperature corresponding to maximum (surely that SHOULD be a 'minimum?) outgoings water temp (Te2) 25°C. This was giving us an indoor temp of 23° plus.
Adjusted as follows (28/01/2025) Tm1 40: Tm2 28; Te1 -2: Te2 20. Still slightly too hot. Adjusted (30/01/2025) Tm1 38; Tm2 27; Te 1&2 as before. Slightly cold now so adjusted (01/02/2025) Tm1 39 everything else as 30/01/25. This is giving 19.5/20°C all over house comfortable for us. We run the system 24/7 ISH although around 2130 I do set the system back to 18°C using ECO setting on thermostat until the economy 7 kicks in at 0030. As this is 0.06p per unit compared with 0.37p per unit day rate I am quite happy for it to consume a few units heating the property again. By the time we come down it is back to 19.5° so quite happy. Bedroom is always comfortable.
I have not had sight of the heat loss calculation for the property but it seems to be working ok. We have an electric AGA which without fail consumes 30 units per night. So taking that out of the equation and background use of approx 6 units per day (I have kept usage records for many years on a spreadsheet so these are accurate figures) the ASHP is consuming around 25 - 40 units per day depending on OAT. This equates to approx £8 to £15 per day averaging about £10 so January electricity bill will be £300. Do these figures KWh not costs seem about right. The high figures were when OAT was around -7 overnight.
The PV panels are doing very little as they are facing East/West (5 each way) and shaded in winter by a higher east /west ridge immediately to the south (where the very low sun is!!!). Come late Feb March they will get a much better sight of the sun. Currently they run the house when ASHP is idle i.e. light, Tele, fridge etc. if the light is good..
Well that enough from me feel free to comment for my consideration, thank you in advance. Every day is a learning day. Mark B
- 26 Forums
- 2,233 Topics
- 49.7 K Posts
- 51 Online
- 5,898 Members
Join Us!
Podcast Picks
Latest Posts
-
As mentioned in other forums when 2 x 10kw grant aerona...
By bretix , 4 hours ago
-
RE: Effect of Mitsu PAR WT60 Wireless Controller
Hi David, If your Mitsi is still on weather compensa...
By RobS , 5 hours ago
-
In most cases I'd expect such liability would be tested...
By Transparent , 7 hours ago
-
RE: Say hello and introduce yourself
This discussion has gone quite deep for our Hello &...
By Transparent , 7 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - it sounds as though you are close to havi...
By cathodeRay , 8 hours ago
-
Let's see if we can tempt @glyn-h to give his insights....
By Mars , 9 hours ago
-
RE: New Fogstar 15.5kWh upright solution
I should've read further before posting the above. ...
By Transparent , 10 hours ago
-
RE: Question about Heating Pump Operation mode – Ecodan FTC6 v20.06
This isn't an exact reply to your question, as I don't ...
By rhh2348 , 10 hours ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
@radwhisperer It does seem to occur most loudly the mor...
By Jancold , 11 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
Let's first note what those parameters are. They are ...
By Transparent , 12 hours ago
-
I’ve met the Flexi-Orb team, and they come across as ge...
By Mars , 12 hours ago
-
Webinar on "Heat Pumps for Home Owners" Thursday 20...
By Mars , 14 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@grantmethestrength also i need to check the other stra...
By AdamK , 15 hours ago
-
@jamespa @old_scientist @iaack Hi, thanks for the inp...
By bontwoody , 15 hours ago
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
This is how Daikin run their heat pumps. Weather Comp...
By RadWhisperer , 18 hours ago
-
Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
I ended up with a Solis S6-EH1P8K-L-PLUS (8 kW) hybrid ...
By Batpred , 1 day ago
-
RE: Options on flushing my system
@grantmethestrength with your pragmatic approach and &#...
By SUNandAIR , 1 day ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
@batpred For the moment I'm sticking with what I have, ...
By bubuontheweb , 1 day ago
-
RE: Electricity price predictions
Nice to be back on track! If we all had the interest, s...
By Batpred , 1 day ago