Freeze Stat/Defrost...
 
Notifications
Clear all

Freeze Stat/Defrost setting….Ecodan in freezing conditions

30 Posts
8 Users
13 Reactions
9,682 Views
SUNandAIR
(@sunandair)
Noble Member Member
3387 kWhs
Joined: 2 years ago
Posts: 462
 

@walkers-heatpump agree. From a practical point of view your comments make sense…. I guess the key is to check the outside pipes are fully insulated right up to the body or the HP and around the isolator levers. 
I believe the ambient thermostat is exposed to the air so will get cold more readily.

The anti freeze valves are not supposed to be  insulated but they can be sheltered from wind and rain. This should mean the more exposed thermostat will reach 3C well before the valve does. 
Is that your post on the Facebook page?


   
👍
1
ReplyQuote
 Linz
(@linz)
Active Member Member
50 kWhs
Joined: 1 year ago
Posts: 6
 

@amanda1 thank you, great help 😀


   
ReplyQuote
 Linz
(@linz)
Active Member Member
50 kWhs
Joined: 1 year ago
Posts: 6
 

@sunandair thank you. Yes it was me on fb. I hadn't discovered this forum then and they took a while to approve my post. My next dilemma is how to adjust the setting, so I will trawl the manuals. Thanks again 😀


   
ReplyQuote
(@walkers-heatpump)
Trusted Member Member
237 kWhs
Joined: 2 years ago
Posts: 23
 

@sunandair Cheers. Yes I'd posted on the Ecodan group. I'll see what the installers say. They seem to have done a good job with the pipe insulation. Just dropping it by a degree or two I reckon could reduce freezestat runtime considerably over a winter


   
ReplyQuote
SUNandAIR
(@sunandair)
Noble Member Member
3387 kWhs
Joined: 2 years ago
Posts: 462
 

Posted by: @kev-m

Posted by: @walkers-heatpump

 

-- Attachment is not available --

No pretty sure it's the ambient outdoor temp, states in the manual - see attached screenshot

 

 

 

 

If you set it to 3 degrees....

When outside air temperature gets to 3 degrees, it starts the circulation pumps and monitors the flow (I assume it uses the RWT sensor) temperature . If the flow drops to 15 deg, the ASHP heats it to 20 deg. And repeats ... The 15 and 20 are not adjustable.

This won't use a lot of energy but may be annoying if you want a silent overnight setback.

That's what mine does anyway. 😀 

 

Surprise on Variable Freeze Stat function. As we know from this thread there are 2 parts to the freeze stat function -

1. To circulate the water so as to displace the colder water in the outside unit and pipework.

2. To reheat the circulating water if it drops below a certain temperature. (Factory set at 20degC.)

And as stated above we had ours starting to reheat at 15c flow temperature and reheating to just above 20c.

However it was -3c last night and I’m monitoring night time reheats at the moment and saw this reheat. So the Freeze Stat Function started a reheat of the circulation water at 20c which is 5c earlier/warmer than expected and took the unit into a defrost 22 minutes later, followed by a reheat up to 40c.

 

A75D2EFA AB91 4EE6 A228 70ACC069F7F9
D9EB0BCB C27D 45E4 B06E B1A764FEF432

As far as I am aware this was entirely due to the Freeze Stat Function changing its operating parameters based on the protection needs of the system.

the function finished with another defrost then stopped leaving the flow and return temperatures at 30c.

9465CB17 07E6 4820 8FDE B5705931AEF4

Interesting to note how quickly the temp then drops while the circulation pump continues to operate and it’s -3c outside. 

Incidentally I only have MELCloud and I don’t have specialist data collection on our HP but I’ve worked out a way of approximating the HP OUTPUT just from the MELCloud graphs but it requires an accurate flow rate to calculate it. Here is a graph showing some output values..

F88C60A0 5FB2 44B6 B31D 21FC19481FB4

Obvs. if someone knows these calcs don’t add up or any thoughts let me know.

The full 24 hours outside and inside temperatures can be seen on this graph.

7E3D5DF4 35B9 4B57 835A D659963E8E5D

 


   
ReplyQuote
(@glpinxit)
Trusted Member Member
451 kWhs
Joined: 2 years ago
Posts: 29
 

Our Ecodan was installed 18 months ago and glycol was included in the system. Since then I've been meaning to buy a refractometer so I can check the concentration of the glycol and the temperature that it reduces the freezing point to- see eBay item 354895847827 for example. I haven't got round to buying one  so far but would use it by releasing a little water from a radiator drain point (I used to use these instruments many years ago when I worked in a laboratory and they are very easy to use.) Although the glycol in our system should protect it down to about -12C I've still got the freeze protection set at about +5C as it isn't very bothersome.

Supplementary point: reading this thread sent me to look at my Melcloud results in the 'Hourly Temperature' report to find that it had been regularly cycling through the night because even here in rural Somerset it has been cold enough at night (-5C) here to cool the bedroom with the thermostat to the point where it calls for heat. I've relocated that thermostat to our (much warmer) bedroom and need to keep an eye on the temperature downstairs.


   
ReplyQuote



Page 3 / 3
Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security