Ecodan Melcloud temperature control with compensation curve
I’ve installed MAC-587IF-E on my Ecodan. When I open the Melcloud app, it shows my Room Temperature -39C. Can anyone suggest where this data comes from? I guess I’m missing a room sensor? As I live in an area where it’s often subzero temperatures outside, I was hoping I could monitor my house temperature via Melcloud when I’m away for extended period.
Another disappointment is that Melcloud app seems to only support underfloor heating adjustments when not using “Curve” (weather compensation). When Curve is activated, I still see the slider set at 20C and no matter where I slide it, it doesn’t trigger change to Ecodan. When I change it to Room, the slider works fine and sends the data through.
My system is installed with one zone which heats both floors and rooms are manually adjusted by thermostats. Everything works fine and I’m happy with the efficiency. It’s just the lack of control via app.
Any advice is much appreciated.
Firstly, Melcloud isn't great at controlling the Ecodan.
I don't know where the -39 comes from but you can set where the room temperature is monitored from the initial settings menu on the main FTC control panel.The source of the temperature is the main wired control, a remote thermistor wired into the FTC or the Mitsubishi wireless controller. It will not show the temperature from a third party thermostat.
When curve is activated, you are right it won't respond to a change in room temp because you are not in room temp mode. The only way I've found to control the heating via the app is when you are in room temp mode.
Where is your main FTC controller? Is it in your living space?
As I said, the app isn't that good.
You can change the flow temp and target room temp via the app, but not the WC curve or the offset. A bit frustrating for me as my installer put the FTC in the boiler cupboard, meaning it is useless as a thermostat/temp sensor for Room Temp targetting. My only option therefore if I want to control the indoor temp remotely is to not use WC and instead manually adjust the flow temperature.
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
Thanks for your valuable input regarding WC. That’s unfortunate.
Kev M, thanks for the tip regarding initial settings. I changed sensor to Main RC and now it’s +29C. It’s probably what it is inside the controller panel. Let’s see how useful of a reference number that will be. I guess there’s no way to move that sensor outside?
On another note, I’ve noticed once before and just saw again that the black flash icon was on, meaning the electric heater is activated. I wonder why it does that? It’s +2 outside and DHW is 50 degrees. House heating is on. It is quite windy outside but it looks a bit odd it would use electric heater now and did fine when it was -15 outside a few weeks ago.
Posted by: @marthThanks for your valuable input regarding WC. That’s unfortunate.
Kev M, thanks for the tip regarding initial settings. I changed sensor to Main RC and now it’s +29C. It’s probably what it is inside the controller panel. Let’s see how useful of a reference number that will be. I guess there’s no way to move that sensor outside?
On another note, I’ve noticed once before and just saw again that the black flash icon was on, meaning the electric heater is activated. I wonder why it does that? It’s +2 outside and DHW is 50 degrees. House heating is on. It is quite windy outside but it looks a bit odd it would use electric heater now and did fine when it was -15 outside a few weeks ago.
The temp sensor is inside the main FTC control panel (the one you use to change settings). You can move that panel depending on how long the cable is. Alternatively you can attach a remote thermistor pac-se41ts-e to the main FTC box. It comes with a very long cable. You can get them for about £20 on ebay. That's what I use and it works well. Once it's attached another option appears in the initial settings menus you've already used.
I don't know why the electric heater is on. Maybe a legionella purge?
@scrchngwsl I am on the weather compensation setting but I can’t understand why Melcloud does not give me any flow temperatures. Temperature reports include a flow temperature feature but this I’d greyed out
@dotty9943 tap on the greyed out flow temp. What happens?
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @dotty9943@scrchngwsl I am on the weather compensation setting but I can’t understand why Melcloud does not give me any flow temperatures. Temperature reports include a flow temperature feature but this I’d greyed out
I assume you have tried tapping on the greyed out options? If they are available, doing this un-greys them.
-39C means that the software running the FTC is a buggy version that needs to be updated. There is a firmware check in the MelCloud app, I presume this is the software that needs to be updated (mine was changed during an engineer visit), there's only one way to find out! When you switch to room mode the FTC will be using this incorrect temperature as a gauge of how much energy it needs to put in, this will be massively wrong, which is what might be triggering the back-up heaters to come on . You don't want to be in room mode until you have an accurate temperature showing.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Oh @kev-m you star you 😘🤣
@dotty9943 I’m glad you’re on the up 👍
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@kev-m Now that you have solved the problem of temperature readings, this has enabled me to move on to the next stage of my attempts to find out why my heat pump is achieving such poor COP scores (They are about 2.3 when the predicted score is 3.2 and better. We have done the following without much progress
a. On the basis of the Ecodan recommendations following a heat loss study, we have up graded all our radiators
b. We have replaced doors and windows so that all our doors and windows are now double glazed
c. We have put new thicker insulation in our loft
c. We have put throttles in our chimneys
d. Our radiators were rebalanced last week
e. We have set weather compensation so that flow temperature is at the recommended level
f. The heat loss study confirmed that our 14 kw is big enough to heat our. House and compensate for the heat loss
G. The system was serviced in December, when the filters were cleaned.
My web researches don’t suggest any other explanation for poor efficiency so can any one come up with new ideas? Failing that I don’t know what to do short of taking our heat pump out and starting again with an efficient combi boiler
- 22 Forums
- 2,058 Topics
- 44.9 K Posts
- 15 Online
- 3,312 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@damon thank you for posting. Would you care to tell ...
By JamesPa , 29 minutes ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
Braver person than me. No way I would go down that rout...
By Johnmo , 2 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Well my switch from eon is tomorrow/Monday so I’ll soon...
By Westkent , 7 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@arundalep yes I have no issue with this. The observati...
By benson , 10 hours ago
-
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@johnmo I have been looking at the daily Agile rates fo...
By Toodles , 13 hours ago
-
RE: Rate the quality of your heat pump design and installation
So your Halo lite should really do nothing, when connec...
By Johnmo , 14 hours ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
This is indeed welcome news. In addition the new legi...
By JamesPa , 23 hours ago
-
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK, so when the HP comes on it becomes obvious.It's on ...
By tdudgeon , 2 days ago
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 2 days ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 3 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 4 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 4 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 4 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 4 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 5 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 5 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 5 days ago