Ecodan Melcloud temperature control with compensation curve
I’ve installed MAC-587IF-E on my Ecodan. When I open the Melcloud app, it shows my Room Temperature -39C. Can anyone suggest where this data comes from? I guess I’m missing a room sensor? As I live in an area where it’s often subzero temperatures outside, I was hoping I could monitor my house temperature via Melcloud when I’m away for extended period.
Another disappointment is that Melcloud app seems to only support underfloor heating adjustments when not using “Curve” (weather compensation). When Curve is activated, I still see the slider set at 20C and no matter where I slide it, it doesn’t trigger change to Ecodan. When I change it to Room, the slider works fine and sends the data through.
My system is installed with one zone which heats both floors and rooms are manually adjusted by thermostats. Everything works fine and I’m happy with the efficiency. It’s just the lack of control via app.
Any advice is much appreciated.
Firstly, Melcloud isn't great at controlling the Ecodan.
I don't know where the -39 comes from but you can set where the room temperature is monitored from the initial settings menu on the main FTC control panel.The source of the temperature is the main wired control, a remote thermistor wired into the FTC or the Mitsubishi wireless controller. It will not show the temperature from a third party thermostat.
When curve is activated, you are right it won't respond to a change in room temp because you are not in room temp mode. The only way I've found to control the heating via the app is when you are in room temp mode.
Where is your main FTC controller? Is it in your living space?
As I said, the app isn't that good.
You can change the flow temp and target room temp via the app, but not the WC curve or the offset. A bit frustrating for me as my installer put the FTC in the boiler cupboard, meaning it is useless as a thermostat/temp sensor for Room Temp targetting. My only option therefore if I want to control the indoor temp remotely is to not use WC and instead manually adjust the flow temperature.
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
Thanks for your valuable input regarding WC. That’s unfortunate.
Kev M, thanks for the tip regarding initial settings. I changed sensor to Main RC and now it’s +29C. It’s probably what it is inside the controller panel. Let’s see how useful of a reference number that will be. I guess there’s no way to move that sensor outside?
On another note, I’ve noticed once before and just saw again that the black flash icon was on, meaning the electric heater is activated. I wonder why it does that? It’s +2 outside and DHW is 50 degrees. House heating is on. It is quite windy outside but it looks a bit odd it would use electric heater now and did fine when it was -15 outside a few weeks ago.
Posted by: @marthThanks for your valuable input regarding WC. That’s unfortunate.
Kev M, thanks for the tip regarding initial settings. I changed sensor to Main RC and now it’s +29C. It’s probably what it is inside the controller panel. Let’s see how useful of a reference number that will be. I guess there’s no way to move that sensor outside?
On another note, I’ve noticed once before and just saw again that the black flash icon was on, meaning the electric heater is activated. I wonder why it does that? It’s +2 outside and DHW is 50 degrees. House heating is on. It is quite windy outside but it looks a bit odd it would use electric heater now and did fine when it was -15 outside a few weeks ago.
The temp sensor is inside the main FTC control panel (the one you use to change settings). You can move that panel depending on how long the cable is. Alternatively you can attach a remote thermistor pac-se41ts-e to the main FTC box. It comes with a very long cable. You can get them for about £20 on ebay. That's what I use and it works well. Once it's attached another option appears in the initial settings menus you've already used.
I don't know why the electric heater is on. Maybe a legionella purge?
@scrchngwsl I am on the weather compensation setting but I can’t understand why Melcloud does not give me any flow temperatures. Temperature reports include a flow temperature feature but this I’d greyed out
@dotty9943 tap on the greyed out flow temp. What happens?
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @dotty9943@scrchngwsl I am on the weather compensation setting but I can’t understand why Melcloud does not give me any flow temperatures. Temperature reports include a flow temperature feature but this I’d greyed out
I assume you have tried tapping on the greyed out options? If they are available, doing this un-greys them.
-39C means that the software running the FTC is a buggy version that needs to be updated. There is a firmware check in the MelCloud app, I presume this is the software that needs to be updated (mine was changed during an engineer visit), there's only one way to find out! When you switch to room mode the FTC will be using this incorrect temperature as a gauge of how much energy it needs to put in, this will be massively wrong, which is what might be triggering the back-up heaters to come on . You don't want to be in room mode until you have an accurate temperature showing.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Oh @kev-m you star you 😘🤣
@dotty9943 I’m glad you’re on the up 👍
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@kev-m Now that you have solved the problem of temperature readings, this has enabled me to move on to the next stage of my attempts to find out why my heat pump is achieving such poor COP scores (They are about 2.3 when the predicted score is 3.2 and better. We have done the following without much progress
a. On the basis of the Ecodan recommendations following a heat loss study, we have up graded all our radiators
b. We have replaced doors and windows so that all our doors and windows are now double glazed
c. We have put new thicker insulation in our loft
c. We have put throttles in our chimneys
d. Our radiators were rebalanced last week
e. We have set weather compensation so that flow temperature is at the recommended level
f. The heat loss study confirmed that our 14 kw is big enough to heat our. House and compensate for the heat loss
G. The system was serviced in December, when the filters were cleaned.
My web researches don’t suggest any other explanation for poor efficiency so can any one come up with new ideas? Failing that I don’t know what to do short of taking our heat pump out and starting again with an efficient combi boiler
- 22 Forums
- 2,073 Topics
- 45.5 K Posts
- 75 Online
- 3,353 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Solar Power Output – Let’s Compare Generation Figures
Well we finished this month with an all time record! Ev...
By Andris , 7 hours ago
-
RE: 5 Star Service from Havenwise
Oh good! I was wondering when/if you might pick them ...
By Transparent , 9 hours ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
update - my old installer insisted on a heat loss of 11...
By MatWin , 11 hours ago
-
I agree it's not very helpful. Generally, the max heat ...
By Old_Scientist , 13 hours ago
-
RE: Commencing on an ASHP Installation Process
I think therein lies the problem. Ratio of quotes to i...
By JamesPa , 1 day ago
-
RE: Why Your MCS-Certified Installer Might Not Be As Competent As You Think
Hive and most other smart thermostats don't play well w...
By JamesPa , 1 day ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
Thanks for the input. I've been running various experim...
By Grahamh-uk , 1 day ago
-
RE: Radiators downstairs are cooler at the bottom after ASHP install
@melonbuffet Hi, this sounds great is you are getting 5...
By ASHP-BOBBA , 2 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
I believe there's another reason that network upgrades ...
By Transparent , 2 days ago
-
RE: What’s the modern take on advised types of insulation?
@jeff I am sorry @jeff if I have misunderstood what you...
By Toodles , 2 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@editor Cobbler’s Mantra that!
By Toodles , 3 days ago
-
RE: Renewables & Heat Pumps in the News
Australia Blue, the first wind farm in Western Victoria...
By Morgan , 3 days ago
-
RE: Flow rate discrepancy between ASHP and manifold
That's useful thanks, I hadn't seen that table before. ...
By AshRolls , 4 days ago
-
In principle I agree, @johnmo, but with provisos. The...
By Majordennisbloodnok , 4 days ago
-
RE: Heat pump installation and BUS Grant timings
@jamespa Thats how I understood it too. 🙂
By ASHP-BOBBA , 4 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@sallyl That sounds about right if they are re-filling ...
By Brendon Uys , 5 days ago
-
I wouldn't be so sure about that. Heat pump designers ...
By JamesPa , 5 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@toodles they're a rowdy bunch!
By Mars , 6 days ago
-
RE: Home energy storage & battery register
@jamespa To a certain extent, by exporting to the grid ...
By Toodles , 6 days ago