Ecodan Melcloud temperature control with compensation curve
I’ve installed MAC-587IF-E on my Ecodan. When I open the Melcloud app, it shows my Room Temperature -39C. Can anyone suggest where this data comes from? I guess I’m missing a room sensor? As I live in an area where it’s often subzero temperatures outside, I was hoping I could monitor my house temperature via Melcloud when I’m away for extended period.
Another disappointment is that Melcloud app seems to only support underfloor heating adjustments when not using “Curve” (weather compensation). When Curve is activated, I still see the slider set at 20C and no matter where I slide it, it doesn’t trigger change to Ecodan. When I change it to Room, the slider works fine and sends the data through.
My system is installed with one zone which heats both floors and rooms are manually adjusted by thermostats. Everything works fine and I’m happy with the efficiency. It’s just the lack of control via app.
Any advice is much appreciated.
Firstly, Melcloud isn't great at controlling the Ecodan.
I don't know where the -39 comes from but you can set where the room temperature is monitored from the initial settings menu on the main FTC control panel.The source of the temperature is the main wired control, a remote thermistor wired into the FTC or the Mitsubishi wireless controller. It will not show the temperature from a third party thermostat.
When curve is activated, you are right it won't respond to a change in room temp because you are not in room temp mode. The only way I've found to control the heating via the app is when you are in room temp mode.
Where is your main FTC controller? Is it in your living space?
As I said, the app isn't that good.
You can change the flow temp and target room temp via the app, but not the WC curve or the offset. A bit frustrating for me as my installer put the FTC in the boiler cupboard, meaning it is useless as a thermostat/temp sensor for Room Temp targetting. My only option therefore if I want to control the indoor temp remotely is to not use WC and instead manually adjust the flow temperature.
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
Thanks for your valuable input regarding WC. That’s unfortunate.
Kev M, thanks for the tip regarding initial settings. I changed sensor to Main RC and now it’s +29C. It’s probably what it is inside the controller panel. Let’s see how useful of a reference number that will be. I guess there’s no way to move that sensor outside?
On another note, I’ve noticed once before and just saw again that the black flash icon was on, meaning the electric heater is activated. I wonder why it does that? It’s +2 outside and DHW is 50 degrees. House heating is on. It is quite windy outside but it looks a bit odd it would use electric heater now and did fine when it was -15 outside a few weeks ago.
Posted by: @marthThanks for your valuable input regarding WC. That’s unfortunate.
Kev M, thanks for the tip regarding initial settings. I changed sensor to Main RC and now it’s +29C. It’s probably what it is inside the controller panel. Let’s see how useful of a reference number that will be. I guess there’s no way to move that sensor outside?
On another note, I’ve noticed once before and just saw again that the black flash icon was on, meaning the electric heater is activated. I wonder why it does that? It’s +2 outside and DHW is 50 degrees. House heating is on. It is quite windy outside but it looks a bit odd it would use electric heater now and did fine when it was -15 outside a few weeks ago.
The temp sensor is inside the main FTC control panel (the one you use to change settings). You can move that panel depending on how long the cable is. Alternatively you can attach a remote thermistor pac-se41ts-e to the main FTC box. It comes with a very long cable. You can get them for about £20 on ebay. That's what I use and it works well. Once it's attached another option appears in the initial settings menus you've already used.
I don't know why the electric heater is on. Maybe a legionella purge?
@scrchngwsl I am on the weather compensation setting but I can’t understand why Melcloud does not give me any flow temperatures. Temperature reports include a flow temperature feature but this I’d greyed out
@dotty9943 tap on the greyed out flow temp. What happens?
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @dotty9943@scrchngwsl I am on the weather compensation setting but I can’t understand why Melcloud does not give me any flow temperatures. Temperature reports include a flow temperature feature but this I’d greyed out
I assume you have tried tapping on the greyed out options? If they are available, doing this un-greys them.
-39C means that the software running the FTC is a buggy version that needs to be updated. There is a firmware check in the MelCloud app, I presume this is the software that needs to be updated (mine was changed during an engineer visit), there's only one way to find out! When you switch to room mode the FTC will be using this incorrect temperature as a gauge of how much energy it needs to put in, this will be massively wrong, which is what might be triggering the back-up heaters to come on . You don't want to be in room mode until you have an accurate temperature showing.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Oh @kev-m you star you 😘🤣
@dotty9943 I’m glad you’re on the up 👍
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@kev-m Now that you have solved the problem of temperature readings, this has enabled me to move on to the next stage of my attempts to find out why my heat pump is achieving such poor COP scores (They are about 2.3 when the predicted score is 3.2 and better. We have done the following without much progress
a. On the basis of the Ecodan recommendations following a heat loss study, we have up graded all our radiators
b. We have replaced doors and windows so that all our doors and windows are now double glazed
c. We have put new thicker insulation in our loft
c. We have put throttles in our chimneys
d. Our radiators were rebalanced last week
e. We have set weather compensation so that flow temperature is at the recommended level
f. The heat loss study confirmed that our 14 kw is big enough to heat our. House and compensate for the heat loss
G. The system was serviced in December, when the filters were cleaned.
My web researches don’t suggest any other explanation for poor efficiency so can any one come up with new ideas? Failing that I don’t know what to do short of taking our heat pump out and starting again with an efficient combi boiler
- 22 Forums
- 2,038 Topics
- 44.4 K Posts
- 29 Online
- 3,252 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
@editor guess the reason im asking is cause ive looked ...
By AdamK , 7 hours ago
-
RE: Help with understanding my Mitsubishi Ecodan air source heat pump
It is taken from the website MEL Pump App
By Patch , 11 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
Not the first time I've heard this... it sounds like th...
By Mars , 11 hours ago
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
This is where the cold water storage tank was situated;...
By Dwynwen , 20 hours ago
-
RE: Air Source Heat Pump - Side Alley Suitability
Thats probably fair enough. The degree-days calculatio...
By JamesPa , 21 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
That’s interesting, but obviously concerning also…. Do ...
By SUNandAIR , 2 days ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thank you @robs - that very useful data. The issue wa...
By Transparent , 2 days ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 3 days ago
-
RE: The Great British Heat Pump Quiz
@allyfish thanks for the feedback and glad it was fun! ...
By Mars , 3 days ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 3 days ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 3 days ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 3 days ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 3 days ago
-
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 4 days ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 4 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 5 days ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 5 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 5 days ago