Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan flow rate tweak
Dear all,
I currently have the setup below.
- Zubadan PUHZ-SHW140 YHA (-BS) outdoor
- Ecodan ERST20C-VM2DR1.UK indoor
My dT is 10 around freezing temperatures, and I want to lower that by increasing the flow rate.
I adjusted the pump speed to 5 (maximum), but it doesn't give me a lot of flow. My outdoor unit supports a flow between 18 and 37 liters per minute, according to the specs. The max flow of my indoor unit is 27 liter per minute, but I only reach 21 liters per minute (probably piping, height resistance, etc). There is no button to control pump speed on the pump itself. The water pump is a Grundfos UMP3K 15-75-130.
I see that there are other indoor units (E*PT 20X series for example) that have the exact same water pump, but according to the specs of those units they have a max flow of 35 liters per minute. Besides, when I look up the specs of the water pump on the website of Grundfos, the max flow of my pump is much higher than the 27 liters (or even the 35) per minute.
I think the pump speed is restricted by the indoor unit, even when it is on speed 5. Unplugging the CNPWM doesn’t set the water pump on max performance either.
Does anyone have ideas how to increase the flow by speeding up the pump (which should be possible according to the specs of the water pump)?
1. Are all your radiator valves (both any thermostatic valves and the lockshield valves) fully open?
2. What diameter is your pipework to the radiators?
3. What size house?
Thanks for your reply.
Yes all radiators and floor heating is fully open. Pipes are 28mm or bigger. It is a 15kW heatpump used for both a big farmhouse and an apartment.
I think the 21 liter (out of the max 27) corresponds with the height resistance etc. I don’t think I can improve much on the piping and radiator sitution itself.
Therefore I am looking for alternative solutions to increase the flow.
Thanks for your reply.
Where did you find that table? The information in my installation manual is totally different (different flow rates, doesn’t say dT of 8 etc).
It mentions an additional pump. But what do they mean with that? Putting two pumps in series doesn’t result in extra flow, only in extra kPa.
@jingle86 Thats in the Ecodan ATW Databook Volume 6.0 https://library.mitsubishielectric.co.uk/pdf/book/Ecodan_ATW_Databook_Vol.6_.0_.pdf#page-1.
No idea what they mean that's why I suggested calling the technical help line they are usually very helpful and its free.
- 26 Forums
- 2,717 Topics
- 63.6 K Posts
- 475 Online
- 7,119 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Vaillant Arotherm Pro vs new Plus
@judith @jamespa Our installer used screed drying mo...
By Batpred , 7 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
It’s here
By avenir , 7 hours ago
-
Hi everyone, I’m looking for real-world advice and co...
By asoksevil , 10 hours ago
-
I knew that Reactive Power support was required by the ...
By Transparent , 11 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Those are very good questions and indeed ones I was ask...
By JamesPa , 15 hours ago
-
For cooling a whole building, or even a big room with l...
By EtchedPixels , 15 hours ago
-
RE: Comms and power cabling to outside unit
@old_scientist 100%, the cover is for warrantied unit...
By Papahuhu , 15 hours ago
-
I don't remember the manufacturer name, but I saw simil...
By bobflux , 17 hours ago
-
RE: Weather compensated secondary circuits with Biomass
UFH is ideal to get max efficiency with a heat pump, bu...
By bobflux , 17 hours ago
-
RE: Rate the quality of your heat pump design and installation
I had a Heat Geek lead install by Green Heat Norfolk. T...
By Orlando , 2 days ago
-
RE: Mitsubishi Ecodan FTC6 settings
While @F1p's dongles are great, the FTC can do this its...
By RobS , 2 days ago
-
RE: Samsung heat pump - data cable issue
If it's a data cable, current will be minuscule, voltag...
By bobflux , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
I got hit with an RHI audit in 2022. It was far from c...
By Abernyte , 3 days ago
-
Hi,is there any Haier super aqua gt users on here,that ...
By Glenn Crawford , 3 days ago
-
RE: Electricity price predictions
@papahuhu Groucho Marx had something to say about no...
By Toodles , 3 days ago