@gary So following your instructions I'll have 99 seconds to run through and pair (if required)? I was hoping I could remove faceplate and switch to correct rooms if they were paired incorrectly. Hopefully all will become clear over the weekend, I don't remember my actuators moving freely, lets see.
Cheers,
Neil.
@gary The heating bill often looks like we live in a mansion with multiple wings.......but that's just because it gets to warm. Next time you're in North Oxfordshire let me know....owe you multiple pints.
Neil.
Thanks to @gary my heatmisers and UFH manifolds are paired and talking to each other, although the far bedroom seems to have switch off on manifold every now and then despite heatmiser demanding heat?!
This is the latest set of numbers for the last week/24hrs.
Any thoughts or observations?
Thanks,
Neil.
@ngillam If the far bedroom is turning on for 12 mins then off for 48mins then the wiring centre isn't getting a signal this is a fail safe that allows the circuit to operate whilst it has no connection to the thermostat.
In the melcloud app below the internal temperature section there is hourly temps and you can look at what is going on every hour for the previous 24 hours it will show you what your heat pump is doing hour by hour its useful to see how often it cycling on and off.
Below the estimated energy use plot there are bar charts for estimated consumed and delivered energy dividing delivered by consumed will give the efficiency or COP, mine when its cold like yesterday is about 3
Does your system have glycol in it, if so you can turn off the freeze stat function that operates the pumps when the HP is off, this is for 100% water systems to prevent them freezing
@gary Hi, Unsure what else I can do about signal to far bedroom, aerials are in but assume the timber heavy nature of the structure might hinder it?
Cycling doesn't look too bad over the last number of hours
My cop based on 12.5 consumed and 60 delivered for yesterday is 4.8
Glycol.....not sure, surely there must be a label/tag somewhere to indicate?
The house is still a bit too warm for us, but the flow temp is about 28, I fear cycling if I go any lower, can I adjust flow rates to somehow cool the rooms?
Thanks,
Neil.
All you can really do is try lower flow rate as long as it’s only cycling once an hour that’s ok.
Only other way to reduce cycling is to ensure the max water volume is available that means removing all the actuators so all areas are heated then you may be able to run the flow temp lower
For the bathroom that’s losing connection I would remove the actuator so it’s always open then as long as one of the circuits on that manifold calls for heat then heat will always flow to the bedroom
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 15 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Say hello and introduce yourself
@transparent - as a matter of interest whats 52V for? ...
By JamesPa , 8 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@heat-pump-newbie Yes you need F Gas engineers like us ...
By dgclimatecontrol , 13 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 17 hours ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 19 hours ago
-
RE: Anyone still weathering it out with Agile?
Yes, but now try finding a working phone box….
By Majordennisbloodnok , 1 day ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 2 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 2 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 3 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 4 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 4 days ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 4 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 5 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 5 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 6 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 6 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 7 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 7 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 1 week ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago
Members Online
No online members at the moment