Ecodan 11.2 KW Flow Rate
Hi,
I recently had a Mitsubishi Ecodan 11.2 kW ASHP installed and I have a concern regarding the flow rate.
In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Most of the plumbing to the outdoor unit is 28 mm so I'm surprised it's low. I was wondering if someone who has one of these units can have a look at their flow rate and pump speed settings as a comparison?
Thanks.
Posted by: @elabHi,
I recently had a Mitsubishi Ecodan 11.2 kW ASHP installed and I have a concern regarding the flow rate.
In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Most of the plumbing to the outdoor unit is 28 mm so I'm surprised it's low. I was wondering if someone who has one of these units can have a look at their flow rate and pump speed settings as a comparison?
Thanks.
The FTC6 manual suggests 14-32 l/min as the acceptable range so 32 would be right at the upper end. My 14kW Ecodan is running at about 24l/min, also well within the acceptable range. The most I have seen it output is 12-13kW so I'm fairly happy and so was the engineer who serviced it. My delta T probably averages nearer 4 than 5.
I would guess your ASHP will never need to deliver 11.2kW constantly in a steady state. It'll do it in bursts when heating the house up, defrosting, heating DHW, etc.
How is the ASHP working otherwise?
Posted by: @elabIn the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Hi @elab
How are you getting on with getting your flow rate sorted? Do you still need help targeting a DeltaT of 5?
in your post I can’t see what your current temperature difference (DeltaT) is.
If you are trying to increase your DeltaT then the flow rate needs to be reduced to allow the heat to transfer to the circulating water. So it also follows that if you are trying to reduce your DeltaT then the flow rate needs to be increased, therefore spreading the heat transfer to a larger volume of water, at a slightly lower temperature.
As @kev-m states, each size heat pump has a different designed flow rate range. In your case the 11.2 kw ecodan has a stated flow range between 14 lpm and 32 lpm.
you can check your current flow rate on your main controller screen.
hope this helps.
Posted by: @sunandairPosted by: @elabIn the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Hi @elab
How are you getting on with getting your flow rate sorted? Do you still need help targeting a DeltaT of 5?
in your post I can’t see what your current temperature difference (DeltaT) is.
If you are trying to increase your DeltaT then the flow rate needs to be reduced to allow the heat to transfer to the circulating water. So it also follows that if you are trying to reduce your DeltaT then the flow rate needs to be increased, therefore spreading the heat transfer to a larger volume of water, at a slightly lower temperature.
As @kev-m states, each size heat pump has a different designed flow rate range. In your case the 11.2 kw ecodan has a stated flow range between 14 lpm and 32 lpm.
you can check your current flow rate on your main controller screen.
hope this helps.
@sunandair, @elab hasn't been seen on the forum since 1st May so I don't think s/he is worthy of any more attention!
- 22 Forums
- 2,097 Topics
- 46.2 K Posts
- 43 Online
- 3,385 Members
Join Us!
Latest Posts
-
RE: Weather compensated secondary circuits with Biomass
@sune thanks for the LK link, looks like a possible opt...
By AndyCoo , 6 hours ago
-
RE: Heat pump solutions and/or installer recommendations for France
No idea, but Google-Fu leads me to Bon chan...
By Scalextrix , 8 hours ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 19 hours ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 1 day ago
-
RE: Mitsubishi cycling while on chilled water output
I absolutely wouldn't remove the buffer altogether, I'd...
By JamesPa , 2 days ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 2 days ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 3 days ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 3 days ago
-
RE: Say hello and introduce yourself
Yes please do Suggesting a loss in the region...
By JamesPa , 3 days ago
-
As I have reported elsewhere we turned on the cooling o...
By downfield , 4 days ago
-
-
@el3b Hi, sorry to hear that, it is advisable to instal...
By ASHP-BOBBA , 5 days ago