Determining correct flow rate for a heat pump
Following on from the flow sensor topic, I was hoping for some more guidance around what flow rate(s) should my primaries be set to, given the Ecodan databook (v6) information and how it differs with ambient temperature.
The 6kw outdoor unit flow rate range in the databook is stated as 8.6 to 17.2 l/min, with a 'recommended' of 10.8 (the databook noting this recommended flow rate is "to ensure optimal heating operation (condition: inlet/outlet temperature difference dT = 8K)."
The first point to note is the deltaT of 8K(/8C), not 5C as is widely acknowledged/understood on this forum!
However it also states two sets of 'capacity' values, one at OAT of 7C and one at 2C - with the capacity/COP/flow of 5.00kW/5.10/14.3lpm at 7C and 6.00/3.75/17.2 at 2C OAT respectively.
The second point to raise would be, what about at an OAT of say 12 or 24C, and conversely below zero - such as -3C?
Thirdly, it would not be surprising if the flow rate needed to be different for just DHW compared with demand of two heating zone pumps, though it could be said that the heating pumps should have been chosen/configured to work optimally at the same flow rate and therefore it isn't a consideration.
Finally, is the simple answer, as has generally been stated elsewhere on the forum, still just to set it such that the dT (of 8C? 5C?) is maintained, and adjust the flow settings on the pump if the OAT affects the delta between seasons?
Mitsubishi Ecodan - FTC6, PUZ-WM60VAA 6kW outdoor unit; third-party cylinder and pump
Have a look at John Cantor's excellent online calculators here (specifically the flow rate calculator):
https://heatpumps.co.uk/calculators/
Heat (kW) = Flowrate (Litres/sec.) x 4.2 (Specific heat of water) x temperature rise (dt)
So for a given heat output from your ASHP, flow rate is directly proportional to dT (between flow and return). As the flow rate drops, the dT will increase, and vice versa.
Some systems use fixed flow pumps, so your flow rate will be static (some are adjustable with maybe 3 settings). Others will use PWM pumps which are able to adjust their flow rates, and the heat pump will attempt to control the flow to meet a target dT.
so conversly, flowrate = heat / 4.18 / deltaTHeat (kW) = Flowrate (Litres/sec.) x 4.2 (Specific heat of water) x temperature rise (dt)Posted by: @old_scientistSo for a given heat output from your ASHP, flow rate is directly proportional to dT (between flow and return). As the flow rate drops, the dT will increase, and vice versa.
Using 6kW as power ('heat'), 6 / 4.18 / 8 * 60 (to get lpm) = 10.77lpm, or the 10.8 I quoted - nice. (The same equation gives the 17.2lpm if I use deltaT of 5)
Yes - do you know if using a Grundfos (with three modes + three speeds in each mode) capable of / using PWM would be continuously-variable, or just step through the three speeds the pump mode would be set in at the time? Can you share any info as to how the FTC controls pump speeds (settable separately for DHW + heating between 1 and 5) on its cylinders?Some systems use fixed flow pumps, so your flow rate will be static (some are adjustable with maybe 3 settings). Others will use PWM pumps which are able to adjust their flow rates, and the heat pump will attempt to control the flow to meet a target dT.
Mitsubishi Ecodan - FTC6, PUZ-WM60VAA 6kW outdoor unit; third-party cylinder and pump
Nothing is straight forward, delta T will change depends on which way you heat, for example radiators will take a wider dT than UFH.
Example
Target room temperature
Well insulated house UFH. Return temp from floor does not go below room target temp. So no lower than 21. If you set dT at 8 your min flow temperature becomes 29. Plus your compressor restart hysterisis is dT plus a further temp delta. So now your Min flow temp is about 29.5. if you operate with dT 4 your min flow temp becomes 25.5 which is better for CoP and not over heating the house.
So dT is horses for courses. You get a better CoP with the widest dT you can operate. But you can easily short cycles at lower loads.
My 6kW heat pump ramps from 14 l/s to 18l/s doing UFH over a 10 min period.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Yes - do you know if using a Grundfos (with three modes + three speeds in each mode) capable of / using PWM would be continuously-variable, or just step through the three speeds the pump mode would be set in at the time? Can you share any info as to how the FTC controls pump speeds (settable separately for DHW + heating between 1 and 5) on its cylinders?
I don't I'm afraid - you could try looking up the specs of the Grundfos pumps online.
My own system uses fixed flow rate Wilo pumps, with 3 different curves or modes, and 3 different speeds. I've just left them in the standard fixed mode, and have tried the 3 different speeds to see the effect on flow rates, and hence dT. These are not PWM pumps.
I think systems that do use PWM pumps, will attempt to vary the pump speed to keep dT constant at whatever it has been set to - so if you've set the system with a desired dT of 5C, and the heat pump is producing 5kW of heat, the system will attempt to adjust the flow rate to be 14.3L/min. If the heat pump output should rise to 6 kW, the system would attempt to increase the flow rate to 17.1L/min to keep the dT at 5C.
I wouldn't become too fixated on it - as long as you have sufficient flow rate to transfer the required heat around your system, dT will be what it is. My dT is low at ~2.5C with a fixed flow rate of ~25-26L/min when the heat pump is just idling putting out around 4.5kW but rises to 4C as the heat output rises to 7K and again to 5C at 9kW output. I could turn my pumps down slightly (to around 21L/min), and dT would increase a whole half degree to 3C at low (4.5kW) output, but I wouldn't want to run a flow rate much below that.
Edit: I need slightly higher flow rates for the same dT due to use of glycol in my system.
Posted by: @rhh2348Thirdly, it would not be surprising if the flow rate needed to be different for just DHW compared with demand of two heating zone pumps, though it could be said that the heating pumps should have been chosen/configured to work optimally at the same flow rate and therefore it isn't a consideration.
Optimising flow rate for DHW heating is something I'd been thinking about over the summer, as we are only heating DHW at that time.
My simplistic thinking is that you'd want to try to keep dT quite narrow/small so would favour a higher flow rate. My reasoning, equally simplistic, is that if I want to heat my DHW to 50C, and I have a dT of 5C, to achieve that I may need a final flow temp (LWT) of 55C and return of 50C. If dT were 10C, I'd need a flow temp of 60C and return temp of 50C, so I'd have to heat the LWT higher to deliver that same final DHW tank temp?
I tried running some tests but there were too many other variables (OAT, DHW tank starting temp etc) making it difficult to compare truly like for like runs.
Happy to hear other's views and to have my thinking corrected / adjusted as appropriate.
Posted by: @rhh2348Can you share any info as to how the FTC controls pump speeds (settable separately for DHW + heating between 1 and 5) on its cylinders?
Hi I assume you have found the settings for pump speeds in the settings menu as you mention settings 1-5. if you have a newer FTC 6 then you can set the pump speed separately for heating and dhw.
When the heatpump is running you can go into the running information menu and type in code 540 this gives you the current flow rate. You can then see how changing the settings 1-5 affects that flow rate. It is fixed and the heatpump can’t change it dynamically you just have to set it at an appropriate speed for your system
Posted by: @old_scientistOptimising flow rate for DHW heating is something I'd been thinking about over the summer, as we are only heating DHW at that time.
There is a video from heat geek about optimal settings for DHW. To get best CoP it more about the cylinder coil being able to strip away as much energy as possible so return temp stays low, for best CoP. Worth finding and watching.
Mine setting are preset and not adjustable, so pump runs at full speed for DHW, so about 1.5m³/h, heat pump adds heat and keeps dT at about 3.5. Seem to get a CoP of about 2.5 to 3.5.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
This may seem like a daft question but can I please check - one should always aim for their systems to have a return temp of <target temp> + dT + hysterisis delta?[snip]ExamplePosted by: @johnmoTarget room temperature
Well insulated house UFH. Return temp from floor does not go below room target temp. So no lower than 21. If you set dT at 8 your min flow temperature becomes 29. Plus your compressor restart hysterisis is dT plus a further temp delta. So now your Min flow temp is about 29.5. if you operate with dT 4 your min flow temp becomes 25.5 which is better for CoP and not over heating the house.
So dT is horses for courses. You get a better CoP with the widest dT you can operate. But you can easily short cycles at lower loads.
In the example above, if my flow was 30.5 rather than 25.5, would the floor get the room to target temp quicker, or would it get there at the same time but overshoot and make the room too warm?
If I want my flow at 25.5, I assume I then adjust the w/c 'curve' so that the flow remains at 25.5 depending on the OAT?
Mitsubishi Ecodan - FTC6, PUZ-WM60VAA 6kW outdoor unit; third-party cylinder and pump
I lowered my flow rate to c. 11L/m for the Ecodan and the heat/power output went down to c. 3.8kW :-/ The deltaT remained around 5 so I assume Ecodan's algo tries to achieve 5 regardless, countering their own documentation referring to 8C/K.Using 6kW as power ('heat'), 6 / 4.18 / 8 * 60 (to get lpm) = 10.77lpm, or the 10.8 I quoted - nice. (The same equation gives the 17.2lpm if I use deltaT of 5)
Mitsubishi Ecodan - FTC6, PUZ-WM60VAA 6kW outdoor unit; third-party cylinder and pump
Posted by: @rhh2348In the example above, if my flow was 30.5 rather than 25.5, would the floor get the room to target temp quicker,
Yes, but that is thinking like gas boiler logic, not heat pump logic, you need as low a flow temperature as possible. Also the further you are away from ideal flow temperature the more likely to overshoot, then depending on your thermostat, screed thickness, insulation levels outside temp you could also undershoot as the system can't keep up.
Watching the discussion on dT. An observation.
As you add heat to the floor the return temperature will rise, the heat pump should let this occur and add more heat to the flow, keeping your dT stable. Once dT and target temp are at point where your settings say is correct, the heat pump should modulate down to keep target and dT stable. If your heat required is below min modulation, the dT will get smaller, and the flow temperature increase, until flow hits your upper limit. Mine can come down to about 3 dT.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
I asked the question to gain more understanding in the context of the flow/return temps rather than that being what I wanted to/was planning to achieve!Posted by: @johnmoPosted by: @rhh2348In the example above, if my flow was 30.5 rather than 25.5, would the floor get the room to target temp quicker,
Yes, but that is thinking like gas boiler logic
On the basis when OAT gets lower, more heat is lost from the room, would the floor flow temp need to go up (perhaps even to 30.5C) to keep up with losses or if it's kicking out 21C heat all the time the room should broadly stay at 21C? Would the flow temp need to increase just to maintain the floor's own temperature at 21 C, or does it need more to then maintain the room's temp?
Mitsubishi Ecodan - FTC6, PUZ-WM60VAA 6kW outdoor unit; third-party cylinder and pump
- 21 Forums
- 1,865 Topics
- 40.7 K Posts
- 128 Online
- 2,184 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump? Or already have one but it’s not performing as it should? Rob is here to help!
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
Latest Posts
-
RE: Not a good January? My heat pump used 840 KWh of electricity
@tim441 East Midlands Uk. Yes to weather compensation. ...
By Carpenterstation , 6 minutes ago
-
RE: Controversial opinions - pure weather compensation, buffer tank, heat loss, oversized heat pumps
Hi @stuartornum, would you be willing to share your WC ...
By Grantmethestrength , 2 hours ago
-
Octopus intelligent Go, IOG. maximising slots
Agile user for most of last year but now moved to IOG. ...
By Tim441 , 2 hours ago
-
RE: Agile: average import cost vs other tariffs?
@toodles Partial answer to my own question!EV is 100% f...
By Tim441 , 3 hours ago
-
RE: New Mitsubishi system, several concerns but just a newbie…..
Got home from work today. Same scenario. Nothing callin...
By Carpenterstation , 5 hours ago
-
RE: Grant Aerona3 with Octopus Cosy tariff
We have a Grant Aerona3 as well. We are not on Octopus ...
By davidm06 , 5 hours ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
@jamespa Perfectly possible re the pipes from the Buffe...
By Alfapat , 5 hours ago
-
RE: New Project! ASHP, Solar PV + Battery, MVHR!
@nickmorgan We have a Sunamp Thermino eP210; this may b...
By Toodles , 5 hours ago
-
RE: Air source heat pump roll call
User name: ASHP-AeronaASHP model: Grant Aerona3 13kW HP...
By ASHP-Aerona , 6 hours ago
-
RE: ASHP & Radiator Sizing - Measuring Heat Loss
That's correct. You probably will need to measure flow...
By JamesPa , 6 hours ago
-
RE: Tesla Powerwall charge level.
@gary that’s what I am hoping - whatever he said he is ...
By andy_e , 7 hours ago
-
RE: Do thick walls make for warm houses?
@transparent understood, thanks very much. I'll create ...
By nickmorgan , 8 hours ago
-
-
You can only get 4kw out of the inverter, regardless of...
By Uk_pete_2000 , 10 hours ago
-
RE: Looking for some advice – no viable installer/system – I'm stuck
Wow, thats a lot of gas - you said 120 sq m is that the...
By JamesPa , 11 hours ago
-
RE: 4 port buffer tank connections
In the coming weeks, I’ll be scheduling another session...
By Mars , 13 hours ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@grantmethestrength, thanks so much for the feedback. I...
By Mars , 14 hours ago
-
RE: Is there a problem with SolarEdge monitoring?
@johnr thanks. After not being able to login for at lea...
By Mars , 14 hours ago
-
RE: Is the Grant controller a thermostat?
@davidm06 no doubt you're right, the house is newish an...
By damonc , 1 day ago
Latest Topics
-
Octopus intelligent Go, IOG. maximising slots
By Tim441 2 hours ago
-
Grant Aerona3 with Octopus Cosy tariff
By ASHP-Aerona 6 hours ago
-
New Project! ASHP, Solar PV + Battery, MVHR!
By nickmorgan 7 hours ago
-
By Curlykatie 10 hours ago
-
ASHP & Radiator Sizing - Measuring Heat Loss
By IanMK13 1 day ago
-
By DavidAlgarve 2 days ago
-
Octopus design temperatures confusion
By AndrewJ 2 days ago
-
Is there a problem with SolarEdge monitoring?
By Mars 2 days ago