Creating a second zone on Mitsubishi Ecodan ASHP
Gary -in the installation manual I'm looking at, on p26, 5.3. Functions Settings, under SW2-6. (mixing tank) it states that when SW2-6 is off 2 Zone temp control is not available! And under SW 4-1 multiple units (which I don't have) it states that when SW4-1 is off 2 zone temp control is not available. I'm getting very confused!
Derek - thanks for that. Zone 1 was set to Room RC1 (I assume that's because I have the wireless thermostat ). I've changed it to main RC to see if it makes any difference but I can't leave Zone 2 unselected. It has to be TH1, MainRC or Time/Zone. I've tried all of them.
@bryanb There are known to be mistakes in the manual, so don't treat it as gospel, afaik SW2-6 is if you have a mixing valve to have different temperatures in the 2 zones so hotter rads and cooler UFH, if you dont have that it should be set to off. SW4-1 is definitely if you have more than one outdoor unit this is nothing to do with 2 zone control so again I think is a mistake in the manual and both SW4-1 and SW4-2 should be set to off.
SW1-8 should be set to ON if you have a wireless controller, presumably that is the case and by wireless controller I mean this.
If the above controller is on zone 1 that should be set to RC1 and if zone 2 is using a 3rd party thermostat should be set to main RC.
This is the main RC.
I'm not sure any of these changes will impact the error you are seeing but its worth a shot.
Thanks for your time with this Gary. I have a wireless controller running Zone 1. Sounds like the manual is more of a hindrance than a help! Your comment re SW4 1& 2 make sense.
I think though if I didn’t have SW2-6 on it gave me an LL error which was to do with incorrect DIP switches. I’ll check all that again when I clear out the airing cupboard to get at the control box.
Had another go at this, the morning. With SW2-7 ON it gives me a flashing LL error at the top of the main controller, but it still appears to run normally. However it does not seem to set up a Zone 2. The bottom left button on the controller is still marked "I" and I cannot set up Zone 2 room sensors. If I turn on SW2-6 I don't get the LL error and can set up Zone 2 settings - left button on controller marked as "Z1 or Z2". But then after several minutes the L5 error comes up and everything shuts down.
I guess if I turn on SW2-6, it's looking for a mixing tank(which I don't have) but presumably would have a thermistor which it can't find, hence the L5 error. I have what I think is called a low loss header, but that's hardly a mixing tank, with no temp sensors.
Not sure where to go from here!
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 664 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
That’s my pleasure, @andrewj. The only challenge now is...
By Majordennisbloodnok , 4 hours ago
-
RE: Electricity price predictions
@toodles @skd Then there is not going to be much from t...
By ChandyKris , 5 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
@batpred I reckon Andy might know a thing or 2 about...
By Bash , 5 hours ago
-
RE: What determines the SOC of a battery?
@batpred Ironically you didn't have anything good to...
By Bash , 6 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Here’s a current graph showing a bit more info. The set...
By benson , 7 hours ago
-
RE: Setback savings - fact or fiction?
True there is a variation but importantly it's understa...
By RobS , 7 hours ago
-
Below is a better quality image. Does that contain all ...
By trebor12345 , 7 hours ago
-
Sorry to bounce your thread. To put to bed some concern...
By L8Again , 7 hours ago
-
@painter26 — they (the analogue gauges) are subtly diff...
By cathodeRay , 8 hours ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 11 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 14 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 16 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 1 day ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 1 day ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 2 days ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 2 days ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 2 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 2 days ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago