Creating a second zone on Mitsubishi Ecodan ASHP
Gary -in the installation manual I'm looking at, on p26, 5.3. Functions Settings, under SW2-6. (mixing tank) it states that when SW2-6 is off 2 Zone temp control is not available! And under SW 4-1 multiple units (which I don't have) it states that when SW4-1 is off 2 zone temp control is not available. I'm getting very confused!
Derek - thanks for that. Zone 1 was set to Room RC1 (I assume that's because I have the wireless thermostat ). I've changed it to main RC to see if it makes any difference but I can't leave Zone 2 unselected. It has to be TH1, MainRC or Time/Zone. I've tried all of them.
@bryanb There are known to be mistakes in the manual, so don't treat it as gospel, afaik SW2-6 is if you have a mixing valve to have different temperatures in the 2 zones so hotter rads and cooler UFH, if you dont have that it should be set to off. SW4-1 is definitely if you have more than one outdoor unit this is nothing to do with 2 zone control so again I think is a mistake in the manual and both SW4-1 and SW4-2 should be set to off.
SW1-8 should be set to ON if you have a wireless controller, presumably that is the case and by wireless controller I mean this.
If the above controller is on zone 1 that should be set to RC1 and if zone 2 is using a 3rd party thermostat should be set to main RC.
This is the main RC.
I'm not sure any of these changes will impact the error you are seeing but its worth a shot.
Thanks for your time with this Gary. I have a wireless controller running Zone 1. Sounds like the manual is more of a hindrance than a help! Your comment re SW4 1& 2 make sense.
I think though if I didn’t have SW2-6 on it gave me an LL error which was to do with incorrect DIP switches. I’ll check all that again when I clear out the airing cupboard to get at the control box.
Had another go at this, the morning. With SW2-7 ON it gives me a flashing LL error at the top of the main controller, but it still appears to run normally. However it does not seem to set up a Zone 2. The bottom left button on the controller is still marked "I" and I cannot set up Zone 2 room sensors. If I turn on SW2-6 I don't get the LL error and can set up Zone 2 settings - left button on controller marked as "Z1 or Z2". But then after several minutes the L5 error comes up and everything shuts down.
I guess if I turn on SW2-6, it's looking for a mixing tank(which I don't have) but presumably would have a thermistor which it can't find, hence the L5 error. I have what I think is called a low loss header, but that's hardly a mixing tank, with no temp sensors.
Not sure where to go from here!
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 21 Online
- 5,662 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Octopus replacing the fixed 15p/kWh export rate with a market tracking one
@trbob I have just extracted the details for Agile Expo...
By Toodles , 58 minutes ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
The Ultimate Guide to Heat Pumps is less than a month a...
By Mars , 2 hours ago
-
RE: Rodents! A word of warning for heat pump owners
@tim441 Or as they didn’t quite say in the space travel...
By Toodles , 8 hours ago
-
RE: Mitsu Wireless Controller and MelCloud
Update: I have found that the contractor had changed on...
By DavidAlgarve , 19 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@editor Hi Mars, We have just installed a Grant Aerona...
By GrahamF , 20 hours ago
-
RE: Sanity check please. Battery storage and inverter sizing.
There are MCS guidelines about how close to the edge/ri...
By Old_Scientist , 23 hours ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I estimated our usage on the following basis. The mos...
By Old_Scientist , 1 day ago
-
RE: Why so many sigenergi installer recommendations?
It’s a really simple answer, GivEnergy. Installers ...
By SAEnergy , 1 day ago
-
@editor Something changed in this last 12 months, they ...
By ASHP-BOBBA , 2 days ago
-
RE: Ecodan & MelCloud scheduling
I put the above question to Mitsu UK at the sme time as...
By DavidAlgarve , 2 days ago
-
Thanks for the heat geek info. I've fitted my own heat ...
By bontwoody , 3 days ago
-
RE: Does anyone have experience of a smart water meter?
Just to give a sense of scale, I've used the CCW water ...
By Majordennisbloodnok , 3 days ago
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 4 days ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 5 days ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 6 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 6 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 7 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 1 week ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 1 week ago