Best control strategies for heat pumps that are way oversized
If I have read and copied the Midea data tables correctly, I am not sure I can see much 'efficiency' difference between a smaller heat pump running flat out and a large heat pump running at a lower output. The data here is from Midea's 8kW foot warmer (on the left) vs their 16kW roaster (on the right). Copying PDF tables is always a hit and miss affair, but these tables are just about readable, and what you want to do is, comparing across the same OAT and LWT, find matching outputs (the CAP or capacity column (in Watts), the other two are COP, and PI which is power input in Watts), and then look at the COP and PI values. Of course, none of the outputs match, making this very much a Mark I Eyeball exercise, but in general the 8kW COPs are perhaps slightly worse than the 16kW for similar outputs. For example, at an OAT of 10 and a LWT of 40, the 8kW unit can put out 7774W at a COP of 4.48 using 1735W (the 'norm' row) while the 16kW unit can put out 7441W at a COP of 4.59 using 1620W (the 'min' row) (relevant cells highlighted in attached image). The outputs are not identical, with the 16kW model output slightly lower, and the difference in COP is small, and furthermore these are 'lab' results, ie controlled conditions, not typical real world conditions.
I would much rather have observational data from real world installation...
Midea 14kW (for now...) ASHP heating both building and DHW
A few Mitsubishi figures from their data book for comparison...
5kW output at 12C OAT:
5kW unit is COP of 6.15
11.2kW unit is COP of 5.9
5kW output at -7C OAT:
5kW unit is COP of 3.0
11.2kW unit is COP of 2.9
The 11.2kW is the closest to double the 5kW in Mitsubishi's R32 range, the 6kW is a software limited 8.5kW so not a good comparison.
Comparing the Mitsubishi 8.5kW to the 14kW for an output of 8kW, at 12C and -7C, gives the same COP values.
So a larger unit running at approx. 50% vs smaller unit at approx. 100% doesn't seem to always result in greater efficiency.
I feel the best first question after establishing that a heat pump is over-sized (even massively so say 3x) is does that affect efficiency?
John Cantor covers this well in this YouTube session https://m.youtube.com/watch?v=0oszaqP0TI4
the critical aspect being is it at the limit of its turn down range and then short cycling (which is inefficient). If it isn’t inefficient then the being over-sized is fine, but often isn’t.
Then forcing the cycling to effectively a shorter time on period would be a good first tactic. This would work best with high thermal mass, eg. UFH or solid brick house with good insulation. Aligning the on time to cheap electric is an opportunity.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
Posted by: @judithThen forcing the cycling to effectively a shorter time on period would be a good first tactic. This would work best with high thermal mass, eg. UFH or solid brick house with good insulation. Aligning the on time to cheap electric is an opportunity.
Pretty much I'm coming to that conclusion, TBH it was my hunch when I started this thread but I wanted (and still want) to see if anyone comes up with anything different. So far not but it's still open to debate.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @judithThen forcing the cycling to effectively a shorter time on period would be a good first tactic. This would work best with high thermal mass, eg. UFH or solid brick house with good insulation. Aligning the on time to cheap electric is an opportunity.
Pretty much I'm coming to that conclusion, TBH it was my hunch when I started this thread but I wanted (and still want) to see if anyone comes up with anything different. So far not but it's still open to debate.
I agreed with your approach on the other thread and so pulling out the general case is a better way of capturing it.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
On LG ashp they have a "silent mode" that operates at reduced power (intended to reduce noise at night) and some users use successfully to reduce cycling etc in oversized pumps.
I dont know if other ashp have similar function?
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@tim441 Re the silent mode, It made me think have a missed something, but i have looked it up, on the Viessmann all the silent mode does is restrict the fan speed, this doesn't reduce the minimum capacity of the compressor therefore doesn't effect minimum output. When the pump is trying to go as low as it can, to reduce output, the fan is already at a reduced speed.
@mikef interesting!
As mentioned .. from info in LG user group it does reduce cycling and output. But I don't use it myself as my heat pump seems approx right size.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
On this forum with advanced monitoring available a Mitsubishi user whose pump was oversized recommended the cloud based auto-adaptation function to improve COP.
It tends to more technical discussions there
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 13 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Say hello and introduce yourself
@transparent - as a matter of interest whats 52V for? ...
By JamesPa , 3 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@heat-pump-newbie Yes you need F Gas engineers like us ...
By dgclimatecontrol , 8 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 12 hours ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 14 hours ago
-
RE: Anyone still weathering it out with Agile?
Yes, but now try finding a working phone box….
By Majordennisbloodnok , 1 day ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 1 day ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 2 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 3 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 3 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 3 days ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 3 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 5 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 5 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 6 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 6 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 6 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 7 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 1 week ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago