Balancing radiators with heatpumps
I think I need to balance my radiators, since there doesn't seem to be proper flow getting through some of them.
Various guides out there suggest to aim for a 12 degC difference between the flow and return temperatures. But heatpumps are supposed to have lower flow temperatures, which is why we oversize radiators. Does this 12C rule (which seems fairly commonplace) still apply, or should another differential be used?
Â
Posted by: @prunusI think I need to balance my radiators, since there doesn't seem to be proper flow getting through some of them.
Various guides out there suggest to aim for a 12 degC difference between the flow and return temperatures. But heatpumps are supposed to have lower flow temperatures, which is why we oversize radiators. Does this 12C rule (which seems fairly commonplace) still apply, or should another differential be used?
Â
Hi Prunus,
I know that Daikin recommend a delta T of 8C for radiators according to their manuals. Other manufacturers specify a 5C or 6C delta T.
I think that with heat pumps it is very much a balancing act, a reasonable delta T is required otherwise the heat energy is not going to be transferred from the heat pump to the heat emitters, but of course, the higher the delta T, then the higher the water flow temperature and the lower the efficiency.
@derek-m Thanks. For the purposes of balancing, does it matter if the value is 12, or 8 or 5, as long as they're all the same? In other words, when balancing I aim to get as much deltaT out of the radiators as possible, and then step it back so that they're all doing the same (with the windows open so the rooms don't fight back by getting warm)?
Posted by: @prunus@derek-m Thanks. For the purposes of balancing, does it matter if the value is 12, or 8 or 5, as long as they're all the same? In other words, when balancing I aim to get as much deltaT out of the radiators as possible, and then step it back so that they're all doing the same (with the windows open so the rooms don't fight back by getting warm)?
Sorry Prunus, I should have made it clear, when the various manufacturers were referring to delta T. it was in relation to the water flow and return temperatures at the heat pump.
The purpose of balancing radiators, is not so much a matter of achieving a specified difference between the water entering, as against the water leaving, but to balance the heat energy supply to the heat loss, so that the room remains at the desired temperature. In an ideal world the radiators would be perfectly sized to match the room heat loss and balancing would not be necessary.
In the real world the practice is to calculate the heat loss, and then install the next size up radiator. The heat output from the radiator can then be adjusted down using the valves.
For the most efficient operation of a heat pump system, the heat emitters should be as large as possible so that they can still dissipate the required amount of heat energy, but at lower water flow temperatures. So the major limitation is set by the coldest room, the one with the smallest radiator output to heat loss, and hence requiring the highest water flow temperature. Once this room has been identified, its radiator valves should always be fully open, and then the valves on the radiators in the other rooms adjusted to achieve the desired room temperatures.
If there are large differences between rooms, then improvements in overall efficiency can be made by additional insulation and/or installing large output radiators.
It is not a quick and simple process balancing your heating system, but I think that you will find it to be beneficial in the long term.
I found this helpful:
https://www.heatgeek.com/balancing-heating-systems-the-ultimate-guide
Makes the point that what we really want is to balance the room temperatures, rather than the radiator temperatures, so this deltaT rule of thumb is a bit arbitrary in that context.
Meanwhile I have this radiator:
so things are very much not right (other radiators were more evenly about 32C, highest was 34C)
heres me just using the Mk. 1 hand to balance my rads
@derek-m it has 5 settings I can work off
- Really cold
- Cold
- warm
- really warm
- HOT HOT HOT
- 22 Forums
- 2,052 Topics
- 44.7 K Posts
- 23 Online
- 3,283 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
I’m an Aira customer with a 6kW Outdoor Unit in a small...
By KevinPotts , 6 hours ago
-
RE: Tariff and charging strategy advice please
We pay 30p 0830 - 0130, then 13p 0130 - 0830. A smart...
By Johnmo , 6 hours ago
-
RE: Is your heat pump insured?
@richard24738 good to hear. I’ll also review them this ...
By Mars , 6 hours ago
-
RE: Hydronic plinth heaters and ASHPs
@benson will you be proceeding with the plinth heaters ...
By Mars , 6 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
You’re on an insane FiT rate 😂 I don’t think we...
By Mars , 7 hours ago
-
RE: Warm weather and heat pumps.
Just looked at my WC setting, it is programmed for 25 D...
By Johnmo , 9 hours ago
-
RE: How to disable radiator heating in LG HM161MR
Just to add to above,when adjusting WC heat pump should...
By JamesPa , 15 hours ago
-
@johnmo yes I can believe that. It seems to be human na...
By SUNandAIR , 19 hours ago
-
RE: Help optimising my system!
I would be doing things a little more simply. Your heat...
By Johnmo , 19 hours ago
-
RE: Yes, the "zoning with ASHP" topic again...
@johnmo Thanks, Johnmo — fair points as always. I ...
By HarryRea , 19 hours ago
-
RE: Renewables & Heat Pumps in the News
If you want to read a huge amount of speculation, fabri...
By Judith , 1 day ago
-
-
IVT Greenline high pressure switch and electrical cassette errors
I have an IVT Greenline HT Plus C heat pump that is con...
By tdudgeon , 2 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
Not sure if you have the defrost cycle and what happens...
By Johnmo , 2 days ago
-
RE: Additional Battery v Wind Turbine v Ripple
There was a call today for Ripple investors and amongst...
By Judith , 3 days ago
-
-
RE: Commencing on an ASHP Installation Process
I think you may very well be right and of course A2A ca...
By JamesPa , 3 days ago
-
-
RE: Agile: average import cost vs other tariffs?
@old_scientist We are with SSEN and our G99 application...
By Toodles , 4 days ago
Members Online
No online members at the moment