Balancing radiators with heatpumps
I think I need to balance my radiators, since there doesn't seem to be proper flow getting through some of them.
Various guides out there suggest to aim for a 12 degC difference between the flow and return temperatures. But heatpumps are supposed to have lower flow temperatures, which is why we oversize radiators. Does this 12C rule (which seems fairly commonplace) still apply, or should another differential be used?
Â
Posted by: @prunusI think I need to balance my radiators, since there doesn't seem to be proper flow getting through some of them.
Various guides out there suggest to aim for a 12 degC difference between the flow and return temperatures. But heatpumps are supposed to have lower flow temperatures, which is why we oversize radiators. Does this 12C rule (which seems fairly commonplace) still apply, or should another differential be used?
Â
Hi Prunus,
I know that Daikin recommend a delta T of 8C for radiators according to their manuals. Other manufacturers specify a 5C or 6C delta T.
I think that with heat pumps it is very much a balancing act, a reasonable delta T is required otherwise the heat energy is not going to be transferred from the heat pump to the heat emitters, but of course, the higher the delta T, then the higher the water flow temperature and the lower the efficiency.
@derek-m Thanks. For the purposes of balancing, does it matter if the value is 12, or 8 or 5, as long as they're all the same? In other words, when balancing I aim to get as much deltaT out of the radiators as possible, and then step it back so that they're all doing the same (with the windows open so the rooms don't fight back by getting warm)?
Posted by: @prunus@derek-m Thanks. For the purposes of balancing, does it matter if the value is 12, or 8 or 5, as long as they're all the same? In other words, when balancing I aim to get as much deltaT out of the radiators as possible, and then step it back so that they're all doing the same (with the windows open so the rooms don't fight back by getting warm)?
Sorry Prunus, I should have made it clear, when the various manufacturers were referring to delta T. it was in relation to the water flow and return temperatures at the heat pump.
The purpose of balancing radiators, is not so much a matter of achieving a specified difference between the water entering, as against the water leaving, but to balance the heat energy supply to the heat loss, so that the room remains at the desired temperature. In an ideal world the radiators would be perfectly sized to match the room heat loss and balancing would not be necessary.
In the real world the practice is to calculate the heat loss, and then install the next size up radiator. The heat output from the radiator can then be adjusted down using the valves.
For the most efficient operation of a heat pump system, the heat emitters should be as large as possible so that they can still dissipate the required amount of heat energy, but at lower water flow temperatures. So the major limitation is set by the coldest room, the one with the smallest radiator output to heat loss, and hence requiring the highest water flow temperature. Once this room has been identified, its radiator valves should always be fully open, and then the valves on the radiators in the other rooms adjusted to achieve the desired room temperatures.
If there are large differences between rooms, then improvements in overall efficiency can be made by additional insulation and/or installing large output radiators.
It is not a quick and simple process balancing your heating system, but I think that you will find it to be beneficial in the long term.
I found this helpful:
https://www.heatgeek.com/balancing-heating-systems-the-ultimate-guide
Makes the point that what we really want is to balance the room temperatures, rather than the radiator temperatures, so this deltaT rule of thumb is a bit arbitrary in that context.
Meanwhile I have this radiator:
so things are very much not right (other radiators were more evenly about 32C, highest was 34C)
heres me just using the Mk. 1 hand to balance my rads
@derek-m it has 5 settings I can work off
- Really cold
- Cold
- warm
- really warm
- HOT HOT HOT
- 22 Forums
- 2,029 Topics
- 44.2 K Posts
- 47 Online
- 3,235 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Many thanks JamesPa - that's great advice which is well...
By Tomdad , 49 minutes ago
-
RE: Bathroom Radiator replacement
@rob-nezard can you please offer your professional advi...
By Mars , 1 hour ago
-
The radiator output at any given ft will increase if th...
By JamesPa , 2 hours ago
-
RE: Performance of Heat Pumps in Mild Weather
@heatgeek The switches to the flow rate were manua...
By RobS , 4 hours ago
-
-
RE: Questions on my Hitachi Yutaki SCombi Heat Pump
OK, thats good and low. With low flow temperatures lik...
By JamesPa , 20 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa “They are all equal but, some are more equal t...
By Toodles , 21 hours ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@cliffhanger Mine has a 'space heating off' setting! O...
By JamesPa , 1 day ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
Thank you, that helped in my understanding. I believe ...
By trebor12345 , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@old_scientist As another example of errors / differenc...
By Toodles , 1 day ago
-
RE: Replacing Worcester oil boiler with an ASHP
Is this something you are thinking of doing? Or has thi...
By Cliff-Arnold , 2 days ago
-
RE: Say hello and introduce yourself
Hi Mars Thanks for inviting me to join the forum, I h...
By Cliff-Arnold , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@agentgeorge Not with Eon Next. The only reson I left O...
By Andris , 2 days ago
-
RE: How hard and expensive would it be to change panel and add battery?
The difficulty with this discussion is that it's referr...
By Transparent , 2 days ago
-
Is this normal? Click of the DHW returning to space heating
This has been bugging me for a while and I just wanted ...
By Grantmethestrength , 3 days ago
-
@sandman1600 you need to measure whats going on real...
By davidnolan22 , 4 days ago
-
@brandon-r is this a project that you could assist with...
By Mars , 4 days ago
-
Has anyone installed these on their ASHP fed radiator s...
By Grantmethestrength , 5 days ago
-
Just an update on the responses received by Smart Heati...
By Eliuccio , 5 days ago
-
RE: Is your gut better than Math
By SUNandAIR , 5 days ago