Balancing radiators with heatpumps
I think I need to balance my radiators, since there doesn't seem to be proper flow getting through some of them.
Various guides out there suggest to aim for a 12 degC difference between the flow and return temperatures. But heatpumps are supposed to have lower flow temperatures, which is why we oversize radiators. Does this 12C rule (which seems fairly commonplace) still apply, or should another differential be used?
Â
Posted by: @prunusI think I need to balance my radiators, since there doesn't seem to be proper flow getting through some of them.
Various guides out there suggest to aim for a 12 degC difference between the flow and return temperatures. But heatpumps are supposed to have lower flow temperatures, which is why we oversize radiators. Does this 12C rule (which seems fairly commonplace) still apply, or should another differential be used?
Â
Hi Prunus,
I know that Daikin recommend a delta T of 8C for radiators according to their manuals. Other manufacturers specify a 5C or 6C delta T.
I think that with heat pumps it is very much a balancing act, a reasonable delta T is required otherwise the heat energy is not going to be transferred from the heat pump to the heat emitters, but of course, the higher the delta T, then the higher the water flow temperature and the lower the efficiency.
@derek-m Thanks. For the purposes of balancing, does it matter if the value is 12, or 8 or 5, as long as they're all the same? In other words, when balancing I aim to get as much deltaT out of the radiators as possible, and then step it back so that they're all doing the same (with the windows open so the rooms don't fight back by getting warm)?
Posted by: @prunus@derek-m Thanks. For the purposes of balancing, does it matter if the value is 12, or 8 or 5, as long as they're all the same? In other words, when balancing I aim to get as much deltaT out of the radiators as possible, and then step it back so that they're all doing the same (with the windows open so the rooms don't fight back by getting warm)?
Sorry Prunus, I should have made it clear, when the various manufacturers were referring to delta T. it was in relation to the water flow and return temperatures at the heat pump.
The purpose of balancing radiators, is not so much a matter of achieving a specified difference between the water entering, as against the water leaving, but to balance the heat energy supply to the heat loss, so that the room remains at the desired temperature. In an ideal world the radiators would be perfectly sized to match the room heat loss and balancing would not be necessary.
In the real world the practice is to calculate the heat loss, and then install the next size up radiator. The heat output from the radiator can then be adjusted down using the valves.
For the most efficient operation of a heat pump system, the heat emitters should be as large as possible so that they can still dissipate the required amount of heat energy, but at lower water flow temperatures. So the major limitation is set by the coldest room, the one with the smallest radiator output to heat loss, and hence requiring the highest water flow temperature. Once this room has been identified, its radiator valves should always be fully open, and then the valves on the radiators in the other rooms adjusted to achieve the desired room temperatures.
If there are large differences between rooms, then improvements in overall efficiency can be made by additional insulation and/or installing large output radiators.
It is not a quick and simple process balancing your heating system, but I think that you will find it to be beneficial in the long term.
I found this helpful:
https://www.heatgeek.com/balancing-heating-systems-the-ultimate-guide
Makes the point that what we really want is to balance the room temperatures, rather than the radiator temperatures, so this deltaT rule of thumb is a bit arbitrary in that context.
Meanwhile I have this radiator:
so things are very much not right (other radiators were more evenly about 32C, highest was 34C)
heres me just using the Mk. 1 hand to balance my rads
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 313 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
I fully understand your reasoning, same steady inputs s...
By cathodeRay , 9 minutes ago
-
RE: Electricity price predictions
@skd I think your guess might well be right - unfortuna...
By Toodles , 19 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@majordennisbloodnok I’m glad I posted this. There see...
By AndrewJ , 30 minutes ago
-
RE: What determines the SOC of a battery?
@batpred I didn't write the Seplos BMS software, I a...
By Bash , 2 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@tasos and @cathoderay thanks. I have some history grap...
By benson , 2 hours ago
-
I am having my existing heat pump changed to a Vaillant...
By trebor12345 , 3 hours ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 3 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 6 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 6 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 8 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 11 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 22 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 24 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago