Balancing radiators with heatpumps
I think I need to balance my radiators, since there doesn't seem to be proper flow getting through some of them.
Various guides out there suggest to aim for a 12 degC difference between the flow and return temperatures. But heatpumps are supposed to have lower flow temperatures, which is why we oversize radiators. Does this 12C rule (which seems fairly commonplace) still apply, or should another differential be used?
Â
Posted by: @prunusI think I need to balance my radiators, since there doesn't seem to be proper flow getting through some of them.
Various guides out there suggest to aim for a 12 degC difference between the flow and return temperatures. But heatpumps are supposed to have lower flow temperatures, which is why we oversize radiators. Does this 12C rule (which seems fairly commonplace) still apply, or should another differential be used?
Â
Hi Prunus,
I know that Daikin recommend a delta T of 8C for radiators according to their manuals. Other manufacturers specify a 5C or 6C delta T.
I think that with heat pumps it is very much a balancing act, a reasonable delta T is required otherwise the heat energy is not going to be transferred from the heat pump to the heat emitters, but of course, the higher the delta T, then the higher the water flow temperature and the lower the efficiency.
@derek-m Thanks. For the purposes of balancing, does it matter if the value is 12, or 8 or 5, as long as they're all the same? In other words, when balancing I aim to get as much deltaT out of the radiators as possible, and then step it back so that they're all doing the same (with the windows open so the rooms don't fight back by getting warm)?
Posted by: @prunus@derek-m Thanks. For the purposes of balancing, does it matter if the value is 12, or 8 or 5, as long as they're all the same? In other words, when balancing I aim to get as much deltaT out of the radiators as possible, and then step it back so that they're all doing the same (with the windows open so the rooms don't fight back by getting warm)?
Sorry Prunus, I should have made it clear, when the various manufacturers were referring to delta T. it was in relation to the water flow and return temperatures at the heat pump.
The purpose of balancing radiators, is not so much a matter of achieving a specified difference between the water entering, as against the water leaving, but to balance the heat energy supply to the heat loss, so that the room remains at the desired temperature. In an ideal world the radiators would be perfectly sized to match the room heat loss and balancing would not be necessary.
In the real world the practice is to calculate the heat loss, and then install the next size up radiator. The heat output from the radiator can then be adjusted down using the valves.
For the most efficient operation of a heat pump system, the heat emitters should be as large as possible so that they can still dissipate the required amount of heat energy, but at lower water flow temperatures. So the major limitation is set by the coldest room, the one with the smallest radiator output to heat loss, and hence requiring the highest water flow temperature. Once this room has been identified, its radiator valves should always be fully open, and then the valves on the radiators in the other rooms adjusted to achieve the desired room temperatures.
If there are large differences between rooms, then improvements in overall efficiency can be made by additional insulation and/or installing large output radiators.
It is not a quick and simple process balancing your heating system, but I think that you will find it to be beneficial in the long term.
I found this helpful:
https://www.heatgeek.com/balancing-heating-systems-the-ultimate-guide
Makes the point that what we really want is to balance the room temperatures, rather than the radiator temperatures, so this deltaT rule of thumb is a bit arbitrary in that context.
Meanwhile I have this radiator:
so things are very much not right (other radiators were more evenly about 32C, highest was 34C)
heres me just using the Mk. 1 hand to balance my rads
@derek-m it has 5 settings I can work off
- Really cold
- Cold
- warm
- really warm
- HOT HOT HOT
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 93 Online
- 3,393 Members
Join Us!
Latest Posts
-
RE: Ecodan consuming 100kwh per day in new build!!!
It does indeed look like that, @skyefarmer. There is ...
By Majordennisbloodnok , 57 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist I found the switching between tariff jus...
By Toodles , 16 hours ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 19 hours ago
-
@editor @bart Hi, I can see a few problems with your in...
By Brendon Uys , 22 hours ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 1 day ago
-
RE: Location of hot water isolation valve on cylinder
@rossowheels if you isolate the water supply in it will...
By ASHP-BOBBA , 2 days ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 2 days ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 2 days ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 3 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 3 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 3 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 3 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 4 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 4 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 4 days ago