Balancing a low loss header/buffer tank on a Grant Aerona 2 13kw r32 system
We can ignore the house heating load. Yes it's low on the ch side, it only needs 23° - 25° in the ufh to get to 19° in the room.
Grant ashp lowest setting is 23°, so for the time being we can ignore the wc curve and just set it to a temp. In our case we are having to set it to 28° - 30° to get ch side to the correct setting.
We have run through all the settings from setting the grant to its lowest, mid and highest flows and then taking the pumps though the 6/7 settings they have. Allow it to settle and check temp and nothing seems to make any difference.
I am now running the system on grants highest setting and two of the pumps are turned off. HP set tp 30°. This is what we get ORDER ABCD
Not sure exactly what the picture shows as there appear to be 8 readings. If its the bottom temp readings that are of interest, the they seem to be 29.2, 28.3, 27.5, 19.2 so A-> C now a bit less than 2. Isn’t this an improvement? D seems to indicate deltaT across UFH now 8C, which at current OAT seems quite high, so may be a problem when OAT drops but equally might not matter. However thats perhaps because the flow rate is low as you have only 1 pump running.
TBH I think you have run through all the simple options and Im not sure I can add much more. I have the impression you understand the principles, so its a bit of a case of play and see what happens, or wait until someone comes along with a magic solution, if indeed there is one without spending any significant money.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa sorry my bad. Yes it's the middle readings that have a temp probe. The are ordered as ABCD
I've just turned on all the pumps and set them to high load and noticed that B went down and D came up. So the CH is taking from the tank.
Once it stopped changing so much I lowered the speed of the CH pumps to 1 and will check again.
(I'm sure I had the HP set at its highest speed, but I didn't turn off any pumps last time I tried.)
If the above goes back to major differences then I'll just run the one pump tomorrow and if if things settle down.
Currently viewing this topic 1 guest.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 44 Online
- 5,736 Members
Podcast Picks
Latest Posts
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 19 minutes ago
-
RE: Who’s Caved and Switched the Heating On Already?
Mine went on today. IAT has dropped two degrees over t...
By JamesPa , 56 minutes ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 1 hour ago
-
RE: Big Changes Coming to Our Heat Pump System
@editor No pressure then 🤣 🤣
By Brendon Uys , 1 hour ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 3 hours ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 4 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 5 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 6 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 1 day ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 2 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 3 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 3 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 3 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 3 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 3 days ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 4 days ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 4 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 5 days ago