I found my Daikin unit coped well with the recent cold spell, even when we had freezing fog the defrost cycles seemed very quick and didn't cause much interruption to the operation. I didn't manage to observe for long enough to time how frequent they were - not sure if there is any way to look back and see energy data. The screen only shows energy use in bar graph format with a 2 hour resolution.
Posted by: @bataltoonce you get below -5 there is no moisture in the air so you get substantially less defrosting - nothing to freeze. I used to live in Finland for a bit and -10 feels better than -2.
Correct, I was going to include that but it complicated the post more than I wanted, and furthermore at -5 and below the main problem is the heat pump's output dropping through the floor.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayPosted by: @bataltoonce you get below -5 there is no moisture in the air so you get substantially less defrosting - nothing to freeze. I used to live in Finland for a bit and -10 feels better than -2.
Correct, I was going to include that but it complicated the post more than I wanted, and furthermore at -5 and below the main problem is the heat pump's output dropping through the floor.
Not if you have a GSHP, which I believe is often the case in the Scandinavian countries.
Hi
We don’t have adjustable flow temperatures. Either not available to the user or because it’s air to air I don’t know. It seems if the room is more than about 10 degrees off the requested temperature the refrigerant flow (copper of the pipework qt least) is about 45-55C through the 50m of pipework all mounted outside and emitting at 20C through insulation. Over the really cold spat the temps in some rooms settled eventually at 14C so we had a maxed out inverter the whole time, when heating. It would run hot for about an hour. Defrost for 15 min. Take another 15min to 45min warming up the inverter before running for another hour. The defrost on air to air literally runs as an air conditioner blowing cold air so nowhere warm in the house although no one at risk in the house during this experimentation. The more I look at this setup, it’s location/humidity, it’s underpowered, it’s always high flow temp, it’s outside heat loss etc the more I think I would have done differently if I was the qualified one installing but at the moment I’m still waiting on resolution some 6 months later.
Thanks
Fujitsu AOYG45LBLA6 feeding 4x ASYG09LMCE and 2x ASYG12LMCE but all being a big paperweight and powered down since summer as it can’t generate enough heat in the 20+kW heat loss early 1800s home.
Posted by: @derek-mNot if you have a GSHP, which I believe is often the case in the Scandinavian countries.
Good point about GSHPs. It would still be interesting to know how other countries deal with ASHP frosting. Maybe they adopt @batalto's solution, choose to live where it is -10! But even in Finland and other cold places, there must be times in the year when they are in frosting temps.
The Midea seems fairly quick in it's defrost cycles, and when I've seen one happen, there isn't much of a dip in the secondary circuit temperature. I wonder if that may be a hidden benefit of the plate heat exchanger? If the direction of flow in the primary circuit reverses - not sure whether it does or not, but I think it must do, because the LWT goes below the RWT - then the PHE is the wrong way round, parallel flow rather than contraflow, and so it will be less efficient, and the secondary circuit will lose less heat back to the primary circuit. The heat pump then only has to heat the primary circuit during recovery.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayPosted by: @derek-mNot if you have a GSHP, which I believe is often the case in the Scandinavian countries.
Good point about GSHPs. It would still be interesting to know how other countries deal with ASHP frosting. Maybe they adopt @batalto's solution, choose to live where it is -10! But even in Finland and other cold places, there must be times in the year when they are in frosting temps.
The Midea seems fairly quick in it's defrost cycles, and when I've seen one happen, there isn't much of a dip in the secondary circuit temperature. I wonder if that may be a hidden benefit of the plate heat exchanger? If the direction of flow in the primary circuit reverses - not sure whether it does or not, but I think it must do, because the LWT goes below the RWT - then the PHE is the wrong way round, parallel flow rather than contraflow, and so it will be less efficient, and the secondary circuit will lose less heat back to the primary circuit. The heat pump then only has to heat the primary circuit during recovery.
The primary water flow does not change direction, it is the refrigerant gas flow inside the heat pump which changes direction.
Posted by: @derek-mThe primary water flow does not change direction, it is the refrigerant gas flow inside the heat pump which changes direction.
That's what I thought, it's the heat pump that 'inverts' to become a fridge, and uses the warm exhaust gas from the fridge to do the defrosting (put like this, it does shows it is a somewhat bizarre thing to be doing in cold weather...). But I needed to get my head round what the primary circuit does, and yes, now I have got it: the 'fridge' takes the heat from the returning water which is still going round the circuit the same normal way, and as a result, the leaving water has a lower temp than the returning water.
But that still leaves the question of whether the PHE somehow provides some protection against heat being lost from the secondary circuit. Based on only a few observations, I could see the LWT falling and then rising over a period of a few minutes, but a nearby and not particularly large rad didn't appear to change temp to the same extent, if at all. The reason for asking this rather obscure question is if it does provide any meaningful protection, then it becomes a possible argument in favour of PHEs.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayPosted by: @derek-mThe primary water flow does not change direction, it is the refrigerant gas flow inside the heat pump which changes direction.
That's what I thought, it's the heat pump that 'inverts' to become a fridge, and uses the warm exhaust gas from the fridge to do the defrosting (put like this, it does shows it is a somewhat bizarre thing to be doing in cold weather...). But I needed to get my head round what the primary circuit does, and yes, now I have got it: the 'fridge' takes the heat from the returning water which is still going round the circuit the same normal way, and as a result, the leaving water has a lower temp than the returning water.
But that still leaves the question of whether the PHE somehow provides some protection against heat being lost from the secondary circuit. Based on only a few observations, I could see the LWT falling and then rising over a period of a few minutes, but a nearby and not particularly large rad didn't appear to change temp to the same extent, if at all. The reason for asking this rather obscure question is if it does provide any meaningful protection, then it becomes a possible argument in favour of PHEs.
I doubt that having a PHE will make much if any difference to the defrost cycle.
The temperature change at the flow and return temperature sensors will be much more noticeable, because all the water flow is going through the same pipes at that point. This water flow is shared over the number of radiators within the system, so the temperature change at the radiators will be much smaller.
The same process will take place whether a PHE is installed or not.
Hi
So on a air to air a defrost cycle actively blows cold 10-15C air into the room (for at least 7 minutes typically 10-20min) but are you saying an air to water during defrost the radiators in the home hardly change in temperature at all?
Thanks
Fujitsu AOYG45LBLA6 feeding 4x ASYG09LMCE and 2x ASYG12LMCE but all being a big paperweight and powered down since summer as it can’t generate enough heat in the 20+kW heat loss early 1800s home.
On my system, defrosts definitely lower the flow temp, both on the monitoring and the rads getting noticeably cooler. Does it make the house cooler? Almost certainly because the average flow temp shown in the graph below is about 3 deg lower that the WC target. Interestingly, defrosting neither increases power used nor decreases the COP. It would have done both had I maintained the WC flow temp by bumping up the curve.
Hi
Thank you for this. I see the flow temp drop and the radiators must get colder but the room temps don’t seem to drop. Does it reduce the flow or anything to compensate?
Thanks
Fujitsu AOYG45LBLA6 feeding 4x ASYG09LMCE and 2x ASYG12LMCE but all being a big paperweight and powered down since summer as it can’t generate enough heat in the 20+kW heat loss early 1800s home.
Posted by: @huwsyHi
Thank you for this. I see the flow temp drop and the radiators must get colder but the room temps don’t seem to drop. Does it reduce the flow or anything to compensate?
Thanks
It is all to do with the amount of stored heat energy and its location. A litre of water contains approximately 3500 times more energy than a litre of air. When an ASHP carries out a defrost cycle, it uses electrical energy to drive the compressor and heat the refrigerant gas, along with heat energy from the water, or in your case air, to provide the heat necessary to melt the ice on the evaporator.
- 22 Forums
- 2,073 Topics
- 45.5 K Posts
- 68 Online
- 3,353 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Solar Power Output – Let’s Compare Generation Figures
Well we finished this month with an all time record! Ev...
By Andris , 6 hours ago
-
RE: 5 Star Service from Havenwise
Oh good! I was wondering when/if you might pick them ...
By Transparent , 8 hours ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
update - my old installer insisted on a heat loss of 11...
By MatWin , 10 hours ago
-
I agree it's not very helpful. Generally, the max heat ...
By Old_Scientist , 11 hours ago
-
RE: Commencing on an ASHP Installation Process
I think therein lies the problem. Ratio of quotes to i...
By JamesPa , 1 day ago
-
RE: Why Your MCS-Certified Installer Might Not Be As Competent As You Think
Hive and most other smart thermostats don't play well w...
By JamesPa , 1 day ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
Thanks for the input. I've been running various experim...
By Grahamh-uk , 1 day ago
-
RE: Radiators downstairs are cooler at the bottom after ASHP install
@melonbuffet Hi, this sounds great is you are getting 5...
By ASHP-BOBBA , 2 days ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
I believe there's another reason that network upgrades ...
By Transparent , 2 days ago
-
RE: What’s the modern take on advised types of insulation?
@jeff I am sorry @jeff if I have misunderstood what you...
By Toodles , 2 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@editor Cobbler’s Mantra that!
By Toodles , 3 days ago
-
RE: Renewables & Heat Pumps in the News
Australia Blue, the first wind farm in Western Victoria...
By Morgan , 3 days ago
-
RE: Flow rate discrepancy between ASHP and manifold
That's useful thanks, I hadn't seen that table before. ...
By AshRolls , 4 days ago
-
In principle I agree, @johnmo, but with provisos. The...
By Majordennisbloodnok , 4 days ago
-
RE: Heat pump installation and BUS Grant timings
@jamespa Thats how I understood it too. 🙂
By ASHP-BOBBA , 4 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@sallyl That sounds about right if they are re-filling ...
By Brendon Uys , 4 days ago
-
I wouldn't be so sure about that. Heat pump designers ...
By JamesPa , 5 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@toodles they're a rowdy bunch!
By Mars , 6 days ago
-
RE: Home energy storage & battery register
@jamespa To a certain extent, by exporting to the grid ...
By Toodles , 6 days ago