Air in the heating system
Our underfloor (ASHP powered) system has air in it. I can hear water trickling through the pipework at night and every day canbleed air out of the heated towel rails.
I know this makes it less efficient and have an engineer visiting next week, hopefully to rectify it. He has already been once and identified that the pressure gauge on the heating expansion vessel isn't working so always shows zero pressure instead of what I'm told should be about 1 to 2 bar.
With the current very cold weather our electricity consumption has of course gone through the roof and I'm hoping to see some improvement from fixing this.
But how does the air get into the system? How do you eliminate it? There is no sign of fluid leaking out but the plumber thinks it should be topped up via the fill tube (which the installers helpfully put downstairs while the pressure tank and other pipework are upstairs!).
Grant Aerona HPID10 10kWh ASHP
Few ways. Easiest is to isolate return manifold, close all zones (loops) but one and install hose to return drain point and open. Then open filling loop unit air clear. Repeat for each loop.
seemingly very few installers know yet alone do this
These guys have "deaerators" that can remove microbubbles that are left flowing around a system, might improve matters. They also sell exotic "vacuum degassers" I think those need electric mind, to directly remove dissolved gasses.
Never used any of them myself, we have conventional rads with bleed valves all over the place- every time I have ever had the system emptied and refilled it has taken weeks to settle down and stop gurgling. When I refill it I wish we had a clever pump that jerked on/off as some now do to help clear air locks. It's only done every 5 years/never, so no worries. I've trawled around the website looking for pressure versus flow on them, they just say "low pressure drop".
- 22 Forums
- 2,084 Topics
- 46 K Posts
- 21 Online
- 3,378 Members
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Vaillant AroTherm Plus 7kW
@judith we had a thermostat fitted for the kitchen as t...
By Scalextrix , 21 minutes ago
-
RE: Commencing on an ASHP Installation Process
There's one radiator not within the delivery, but this ...
By Sheriff Fatman , 1 hour ago
-
There are heat recovery heat pumps that are designed to...
By Scalextrix , 7 hours ago
-
RE: Mitsubishi Ecodan Fails to Heat Water despite temperature drop
Hi @m1kegibson Maybe a long shot but is the controll...
By RobS , 17 hours ago
-
RE: Renewables & Heat Pumps in the News
Yes I realise I'm picking this up a week late...... but...
By Transparent , 1 day ago
-
@editor Mars if you have any recommendations for down s...
By abam48 , 2 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness HI, The rules is a best practise, the ...
By ASHP-BOBBA , 2 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@cathoderay how did you get a script to run for that- d...
By benson , 2 days ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@ashp-bobba thank you, and equally so, thank you for ta...
By Mars , 3 days ago
-
@judith good to know… I’ll continue to feed Wattson, an...
By Mars , 4 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 5 days ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 5 days ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 5 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 6 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 1 week ago