2 X Midea 16kw setup
Hi guys, just wanted some input from you on my system now that the installation is all but complete so I can now describe how its been setup.
We have 2 Midea 16kw ASHP connected as shown below.
There are 2 manifolds as shown below and radiators upstairs.
The ASHP (1) that does DHW and the upstairs radiators is set to use the temperature compensation curve as set out in the Freedom setup guide.
The ASHP (2) that does the UFH is set to have a fixed flow temp of 35 degrees.
ASHP 1 therefore can vary its water temp between 37 and 55 degrees depending on outside temp.
However ASHP 2 is fixed at 35 degrees.
As the 2 ASHP’s share the buffer tank this means there could be conflicts in temperature.
For example if ASHP 1 is outputting water at 50 degrees to the radiators and then ASHP 2 gets a call for heat it will see that the water in the buffer is already above its fixed temp and therefore contribute no heat, but also allow 50 degree water to go through the UFH which exceeds most flooring max temps as there is no mixer/blender at the manifolds.
The above is only one example of where there could be issues and conflicts between the 2 ASHP’s I’m sure there are others and its likely that the hours in operation are not likely to be spread evenly over the 2 units..
As the ASHP’s aren’t connected (master/slave) there is no way for them to communicate and work together.
In my mind the best solution is to have them both connected together (Master /Slave, I believe this is possible) running temperature compensation or fixed temp and have a mixer on each manifold limiting the UFH water temp to around 30 degrees.
I assume FreedomHP had input only about the ASHP's and probably didnt specify anything about the manifolds.
I'm about to send the above to my installer, I did raise my concern about no mixers and the possibilty of different temps in the buffer and at the manifolds but they didnt see it as a problem when I brought it up some time ago and until the setup was complete I couldnt be sure if they were right or wrong.
I'd be interested if anyone else has a dual ASHP Midea system especially if its been setup as master and slave.
Who was your system designer, just so I know who to avoid 🙂
That ufh manifold needs a mixer, I genuinely don’t get why these installers think otherwise. Or better yet mixed pump group with a esbe mixer for weather comp’d ufh.
What size of property needs that much heat input? I’d be interested to see your heat loss calcs. Although to be fair, a 16kW midea is more like a 12 in normal winter conditions.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
To be fair I think its a steep learning curve for the installer and probably themselves and Freedom probably havent given each other the full picture of the install, and every one seems to have its difficulties, especially in our case being a retro fit to a house that was previously storage heaters. Anyway the installer is has been in conversation with them and its agreed they will fit mixers on the manifolds. As to cascading the heat pumps (master/slave) they feel there is little to gain as they dont think they are as intelligent as we might think in terms of sharing out the work load, but I could try this later on if I feel there might be something to gain.
As for the calcs, not really looked too closely into them other than it was felt one 16kw (probably nearer 12kw as you say) was borderline and therefore the installer didnt want cut it fine and I simply want to heat the house properly (unlike what the storage heaters were doing). The belief is the ASHP doing upstairs and DHW is likely to spend most of its running time doing the DHW and on the odd occasion some heating.
Take the buffer out, split the two systems into upstairs and downstairs. Set the weather comp curves for the upstairs rads to suit, and the same for the downstairs.
They’ll never work well driving into a common buffer.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 26 Forums
 - 2,265 Topics
 - 50.6 K Posts
 - 516 Online
 - 5,924 Members
 
Join Us!
Podcast Picks
Latest Posts
- 
                        
                                RE: My DIY Heat Pump installation
That is kind, this site and your blogs were my main sou...
By Polar bear , 3 minutes ago
 - 
                        
                                RE: Midea ASHP – how to set weather compensation
@pash44pump - I stopped using the Mide app ages ago, so...
By cathodeRay , 8 minutes ago
 - 
                        
RE: UFH downstairs and radiators upstairs balancing question
@ashp-bobba Can I pick you brain about mine ...
By davidnolan22 , 1 hour ago
 - 
                        
RE: Help me keep the faith with my air source heat pump installation
@adamk I run the downstairs UFH as an open loop, the ki...
By AgentGeorge , 2 hours ago
 - 
                        
RE: Oil Boiler & Heat Pump Hybrid System
thanks for your reply, tried to explain that tenants fo...
By paultheheating , 4 hours ago
 - 
                        
RE: Who has a V2G EV installation
They certainly look stylish! But it seems that Ander...
By Batpred , 10 hours ago
 - 
                        
                                RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
And if MCS don’t have one on record that’s an issue bec...
By Mars , 10 hours ago
 - 
                        
                                RE: Electricity price predictions
One persons view In sync with the Nesta figures s...
By Jeff , 13 hours ago
 - 
                        
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
Ok so that seems to be the key point namely only mcs ca...
By JamesPa , 15 hours ago
 - 
                        
RE: One flow valve appears to be duff
You might want to consider the following common faults:...
By IaAck , 22 hours ago
 - 
                        
                                RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
We are on the Intelligent Octopus Go tariff. We instal...
By GrahamF , 1 day ago
 - 
                        
RE: New build installation query
@paullacey While the others wait for more info do you m...
By ASHP-BOBBA , 1 day ago
 - 
                        
                                RE: British Gas Heat Pump Installation Complaint
@bgno, the other consideration for legionella cycles ar...
By Mars , 2 days ago
 - 
                        
                                @old_scientist I dont monitor the tank temperature but ...
By bontwoody , 2 days ago
 - 
                        
                                RE: Say hello and introduce yourself
Hello @paultheheating - I'm a rural Moderator! What's...
By Transparent , 2 days ago
 - 
                        
RE: What valves to replace radbots?
Yes. Radbots just replace TRV heads. TRV heads push t...
By JamesPa , 2 days ago
 - 
                        
RE: When will fusion be producing energy?
I am thinking of the case where AI was able to distingu...
By Batpred , 2 days ago
 - 
                        
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
Very definitely. I think the market has changed a bit...
By JamesPa , 3 days ago
 