I think that you will find that the 'soft' start for an electric induction motor is only over a period of seconds, to limit the current inrush. The ...
Just a note of caution. Correctly optimising the WC curve can literally take weeks to achieve dependent upon variations in weather conditions. Only ...
It is interesting to see how the compressor appears to go up to maximum speed when the actually LWT is quite low when compared to the target value, wh...
If I am understanding correctly, your WC curve is set to LWT of 35C @ OAT of -4C and LWT of 30C @ OAT of 20C. So at an OAT of 0C, the LWT should be in...
@cathoderay So on your particular system, when in setback mode, the whole system appears to be disabled, including the water pump or pumps. When cyc...
It may have been adequate a few days ago, when the OAT was higher, but now 35.5C could be inadequate. Your system cannot be operating in WC mode if ...
@cathoderay The data that you are providing is extremely useful, because it not only provides a better insight into how heat pump controllers appear...
If you run your heat pump on a fixed LWT, the IAT will likely vary with changes in OAT. Applying a 1C setback may have just made matters worse. If y...
That would be the case if the water pump keeps running for the whole compressor off period. I believe that some heat pump controllers can be set to ru...
I would suggest that you check the location of the temperature sensor on your hot water cylinder, since if it is fitted too high up the cylinder you m...
@jamespa Hi James, I would welcome your thoughts on the following. Calculating the thermal energy output from heat emitters is fairly straightfo...
@guthrie I know that some controllers can be removed from their main housing and relocated using a suitable extension cable, but I'm not certain if ...
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 41 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@abernyte Mitsubishi warranty is 3 years if installed b...
By dgclimatecontrol , 8 minutes ago
-
The amount paid even if it worked is mindblowing, I'm a...
By dgclimatecontrol , 14 minutes ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
I think so but I don't know for certain. A cascade as ...
By JamesPa , 1 hour ago
-
RE: Humming sound on new install.
Sorry, I should also add these checks The ASHP must ...
By ASHP-BOBBA , 2 hours ago
-
RE: Midea ASHP – how to set weather compensation
Mostly, I think, but with some caveats. I set the TI...
By cathodeRay , 2 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I have been working on network resilience for a while. ...
By Scalextrix , 4 hours ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 20 hours ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 22 hours ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 23 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
@allyfish Dogs have owners - Cats keep staff. You are o...
By Toodles , 1 day ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 1 day ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 1 day ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 2 days ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 2 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 3 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 3 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 3 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 3 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 3 days ago