Posted by: @cathoderay@majordennisbloodnok - cripes, it sounds complicated!
...
Not really. In effect I've just used my home network to extend the wire. If I had a network cable coming out of the back of my PC into the WaveShare unit and another cable from the WaveShare unit into the RS485 port of the inverter it would be logically speaking exactly the same setup. I know I can communicate with the WaveShare unit so everything that's seeming complicated is already proven working.
...
Posted by: @cathoderay...
The key thing is something in software has to do what I have described in the last paragraph, something has to initiate the connection and make the requests. I wonder if that is what is missing on your setup at the moment?
...
I know what you mean, but I don't believe that's the case although self-evidently I'm not in a position to be definite. The Solax integration has to be configured software-wise and that means giving it the IP address of the WaveShare unit, telling it what kind of modbus to use (TCP, RTU over TCP or ASCII over TCP) and what TCP port to use. As a result of that it then does exactly what you're describing and attempting to read the device on the other side. When I do that my logs show several error messages most of which are talking about a failure to read the firmware from addres 0x9. To me this suggests that either the RS485 port on the inverter is not configured correctly, that I've told Solax to use the wrong device address (default is 1 but I've also tried 4) or that I've got the wrong wires connected to the RS485B and -A terminals of the WaveShare unit. The last of these seems to me the most likely, but without a definitive document I'm rather floundering in the dark. Some documents for other Growatt units have suggested wires 1 and 2, some 1 and 5 and some 4 and 5, all with the caveat that if that suggestion doesn't work then switch them round the other way. Ho, hum.
And this is where my investigative process of elimination stalls. I can't test the inverter's port is configured correctly if I don't know I've got it wired up right and I can't test the wiring combinations if I don't know the inverter's port is configured correctly. A little bit of Growatt documentation would go a long way around about now.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@majordennisbloodnok - my hunch is that it is the device address. This can be a gotcha - you can't ask it what it's device address is without knowing its device address! Maybe see if somewhere that (default) address is given? Another scenario: I think I had a situation where two devices both had the same default address, say 1, and to get both to work I had to turn off one (its device ID would remain 1), and then set the device ID on the other device to 2 ('set device 1 ID to 2'), then turn on device 1 again...
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderay@majordennisbloodnok - my hunch is that it is the device address. This can be a gotcha - you can't ask it what it's device address is without knowing its device address! Maybe see if somewhere that (default) address is given? Another scenario: I think I had a situation where two devices both had the same default address, say 1, and to get both to work I had to turn off one (its device ID would remain 1), and then set the device ID on the other device to 2 ('set device 1 ID to 2'), then turn on device 1 again...
Well worth a try; after all, I only have one device the WaveShare box can talk to so it's not a multi-device setup per se. I'll try and see what I find.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Have you actually got a copy of the Growatt Modbus RTU documentation @majordennisbloodnok ?
If not, then there are several online, such as this one on Github.
Growatt doesn't obey the internationally accepted Modbus standard, but it's a close approximation derived from it.
Note that if you've only got one device connected to an RS485 port on your WaveShare converter, then you can send out a command with the ID as 0, which is 'broadcast'.
What you receive as a reply might not make sense at first, but it does at least confirm you've established communication.
Save energy... recycle electrons!
Nope, still no joy. I'll try everything again with the other two pinouts I'm aware have met with success for some others but after that I think I'm going to need some help confirming which wires Growatt are using for RS485 on this particular inverter.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Save energy... recycle electrons!
Posted by: @transparentHave you actually got a copy of the Growatt Modbus RTU documentation @majordennisbloodnok ?
If not, then there are several online, such as this one on Github.
Growatt doesn't obey the internationally accepted Modbus standard, but it's a close approximation derived from it.
Note that if you've only got one device connected to an RS485 port on your WaveShare converter, then you can send out a command with the ID as 0, which is 'broadcast'.
What you receive as a reply might not make sense at first, but it does at least confirm you've established communication.
That could be very useful to know; thanks. Yes, I've got the documentation you mentioned but to be frank I haven't looked too closely at it so far given I expected it to be irrelevant until I had a successful physical connection. More fool me.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @majordennisbloodnokPosted by: @transparentHave you actually got a copy of the Growatt Modbus RTU documentation @majordennisbloodnok ?
If not, then there are several online, such as this one on Github.
Growatt doesn't obey the internationally accepted Modbus standard, but it's a close approximation derived from it.
Note that if you've only got one device connected to an RS485 port on your WaveShare converter, then you can send out a command with the ID as 0, which is 'broadcast'.
What you receive as a reply might not make sense at first, but it does at least confirm you've established communication.That could be very useful to know; thanks. Yes, I've got the documentation you mentioned but to be frank I haven't looked too closely at it so far given I expected it to be irrelevant until I had a successful physical connection. More fool me.
As I have often told young Engineers, "If all else fails, read the instructions".
Posted by: @derek-mPosted by: @majordennisbloodnokPosted by: @transparentHave you actually got a copy of the Growatt Modbus RTU documentation @majordennisbloodnok ?
If not, then there are several online, such as this one on Github.
Growatt doesn't obey the internationally accepted Modbus standard, but it's a close approximation derived from it.
Note that if you've only got one device connected to an RS485 port on your WaveShare converter, then you can send out a command with the ID as 0, which is 'broadcast'.
What you receive as a reply might not make sense at first, but it does at least confirm you've established communication.That could be very useful to know; thanks. Yes, I've got the documentation you mentioned but to be frank I haven't looked too closely at it so far given I expected it to be irrelevant until I had a successful physical connection. More fool me.
As I have often told young Engineers, "If all else fails, read the instructions".
I wish I could claim to be young. Or, for that matter, an engineer. Failed on both counts.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
And finally!
Houston, we have lift-off; thanks to everyone who gave of their time to help. For reference, the pinout was wires 4 and 5 with 4 being wired into RS485B and 5 into RS485A. Nonetheless, I've decided to start a new thread shortly detailing my wider setup (and related decisions to get to that point) as something of a parallel to @cathoderay's "beginner's guide" thread but with a slightly different emphasis.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Posted by: @majordennisbloodnokHouston, we have lift-off
Great, you must be very pleased! I'm also sure others will welcome a separate thread with details of your wider setup, and a slightly different emphasis can only improve the totality of information available here on the forum.
Midea 14kW (for now...) ASHP heating both building and DHW
As promised, here's the separate thread. Beware it's more of a blog article than a thread but if it helps anyone then great.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 48 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Big Changes Coming to Our Heat Pump System
You are too young, 50s-60s expression (or earlier?) whi...
By JamesPa , 16 minutes ago
-
RE: Heat Pump Damage on install - useable or dealbreaker?
Definitely that one, more important than the fins proba...
By JamesPa , 21 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson - looks like good work, and thanks for posting ...
By cathodeRay , 41 minutes ago
-
RE: Electricity price predictions
@diverted-energy sounds like good tariff for you. Octop...
By JulianC , 12 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
In the last week, the external temperature in south Man...
By GrahamF , 14 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 14 hours ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 15 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 17 hours ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 18 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 19 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 20 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 3 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 4 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 4 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 4 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 4 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 4 days ago