Why is my heat pump cooling my DHW?
Just wondered -can you lower the temperature when your hot water reheat starts?
You seem to only have a 5 deg drop. That also means the start of the reheat is at 43 degC which might be a bit high.
I’ve got an 8.5kw HP and have the temp set to 48degC with reheat kicking in at 38degC. That means it’s got a 10 deg drop and so, not switching continually to DHW. And perhaps equally importantly the reheat temp starts when pipe temps roughly match the radiator temps if they’ve been heating the radiators.
I hope this is of interest
Posted by: @sunandair“The cylinder seems to hold the temperature quite well. The problem happens when the system is totally idle, no demand for space heating, no use of hot water. When the temperature drops to 43 (due to normal loss) and the HP starts up to reheat the DHW back to 48, that's when it does the sharp drop.”
I think I’ve encountered something similar. Your paragraph above seems to describe my thoughts.
If HP was idle then the primary pipes are probably cold. HP is slow to build temp up so while water is circulating it’s re absorbing heat from your DHW cyl. This could be confusing for the system (for a while) since the return will be warmer than the flow.perhaps try to coincide DHW reheat while the space heating has been running then the primaries will already have some heat in them. Just a thought from a newbie.
My DHW has always been like this, it drops about 7 or 8 degrees if I recall correctly when it starts heating, I attributed it to what SUNandAIR describes. Since summer I have it set to only heat at midday for an hour and do a manual start if more is required, so its not as noticeable because the tank is mostly cold anyway and I don't watch it like I did when it was first installed.
Mitsubishi Ecodan 8.5kWh
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
- 22 Forums
- 2,097 Topics
- 46.2 K Posts
- 43 Online
- 3,385 Members
Join Us!
Latest Posts
-
RE: Weather compensated secondary circuits with Biomass
@sune thanks for the LK link, looks like a possible opt...
By AndyCoo , 9 hours ago
-
RE: Heat pump solutions and/or installer recommendations for France
No idea, but Google-Fu leads me to Bon chan...
By Scalextrix , 11 hours ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 23 hours ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 1 day ago
-
RE: Mitsubishi cycling while on chilled water output
I absolutely wouldn't remove the buffer altogether, I'd...
By JamesPa , 2 days ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 2 days ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 3 days ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 4 days ago
-
RE: Say hello and introduce yourself
Yes please do Suggesting a loss in the region...
By JamesPa , 4 days ago
-
As I have reported elsewhere we turned on the cooling o...
By downfield , 5 days ago
-
-
@el3b Hi, sorry to hear that, it is advisable to instal...
By ASHP-BOBBA , 5 days ago