System pressure dropping on my Ecodan ASHP system
I have an Ecodan ASHP, due to some building works the hot water cylinder was relocated and some legs have been run for 3 more radiators which have yet to be fitted.
Hot water has been fine since the relocation of the cylinder around 4 weeks ago. This weeknd I put the heating on, all was fine but next morning when the hot water cycle ran before the heating comes on there was a U1 fault which I believe is a low pressure fault.
So I filled the system to about 1.7bar when heating was on and bled the radiators. I manually put water cycle on and cylinder had hot water.
Next morning after heating had been on before same problem. It seems that when I fill the system within about 30 mins pressure drops to 1 bar or less, however all rads are nice and hot.
Any ideas? Thanks.
@spacebiscuit - this is an interesting question, why does an ASHP circuit need to be pressurised in the first place? I can't be, as it is with a traditional car radiator system, so the water can get to a higher temperature without boiling, since ASHPs don't get anywhere near those temps. I have a very very small leak, at least I assume it is, in my primary circuit, that causes the pressure to drop very slowly (over days if not weeks) and yet the system seems to run the same whatever the pressure, as long as the circuit has fluid in it, which it does. Maybe the pressure is there to stop negative pressure that would perhaps allow air to enter? Does anyone know the answer?
Midea 14kW (for now...) ASHP heating both building and DHW
Hello i am an ASHP Engineer and new to this group. Ecodan U1 code is said to be high pressure fault,which is cause by abnormal water flow on the primary circuit. I recommend get ASHP engineer to come have a look.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 49 Online
- 5,736 Members
Podcast Picks
Latest Posts
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 41 minutes ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 2 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 3 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
@old_scientist, our system was royally bodged six years...
By Mars , 3 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
@scalextrix You're assuming that the source of the comm...
By Transparent , 3 hours ago
-
@jamespa thanks, I appreciate the offer. For n...
By DREI , 17 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
I have 3 women in the house, 2 little ones, so my heati...
By DREI , 22 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 22 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 2 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 3 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 3 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 3 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 3 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 3 days ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 4 days ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 4 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 5 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 5 days ago