System pressure dropping on my Ecodan ASHP system
I have an Ecodan ASHP, due to some building works the hot water cylinder was relocated and some legs have been run for 3 more radiators which have yet to be fitted.
Hot water has been fine since the relocation of the cylinder around 4 weeks ago. This weeknd I put the heating on, all was fine but next morning when the hot water cycle ran before the heating comes on there was a U1 fault which I believe is a low pressure fault.
So I filled the system to about 1.7bar when heating was on and bled the radiators. I manually put water cycle on and cylinder had hot water.
Next morning after heating had been on before same problem. It seems that when I fill the system within about 30 mins pressure drops to 1 bar or less, however all rads are nice and hot.
Any ideas? Thanks.
@spacebiscuit - this is an interesting question, why does an ASHP circuit need to be pressurised in the first place? I can't be, as it is with a traditional car radiator system, so the water can get to a higher temperature without boiling, since ASHPs don't get anywhere near those temps. I have a very very small leak, at least I assume it is, in my primary circuit, that causes the pressure to drop very slowly (over days if not weeks) and yet the system seems to run the same whatever the pressure, as long as the circuit has fluid in it, which it does. Maybe the pressure is there to stop negative pressure that would perhaps allow air to enter? Does anyone know the answer?
Midea 14kW (for now...) ASHP heating both building and DHW
Hello i am an ASHP Engineer and new to this group. Ecodan U1 code is said to be high pressure fault,which is cause by abnormal water flow on the primary circuit. I recommend get ASHP engineer to come have a look.
- 26 Forums
- 2,289 Topics
- 51.4 K Posts
- 238 Online
- 5,949 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: DHW heat loss through pumps.
Morning, and thanks for all the replies. I suppose it'...
By ngillam , 1 hour ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
It makes sense the gov will need to shift taxes from el...
By Batpred , 7 hours ago
-
RE: Do Heat Pumps need to start up at Full Power?
@toodles That certainly doesn't look optimal, does it? ...
By Steelbadger , 8 hours ago
-
RE: Electricity price predictions
Would 'foreign investment funds' always translate to fo...
By Batpred , 8 hours ago
-
RE: Renewables & Heat Pumps in the News
I cannot stop thinking... what sort of Air con unit cos...
By Batpred , 10 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
And the saga continues… So today a Senior Grant Engin...
By Crimson , 14 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
The problem comes only if you can't turn the ft down su...
By JamesPa , 15 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@jamespa Yes, the OAT sensor is situated on the back pa...
By Toodles , 16 hours ago
-
RE: Ecodan ASHP Low COP and Unstable Compressor Frequency
Just to clarify, returning water from UFH is colder tha...
By lukewarmbath , 16 hours ago
-
RE: 10kw heat pump run in 24*7 data?
A different heat pump (Midea 14kW) but a stark reminder...
By cathodeRay , 17 hours ago
-
From what I see, the work to upgrade the cable, etc all...
By Batpred , 17 hours ago
-
RE: Confusion over Octopus Tariffs
That's sounds great. I have no ASHP, but 15kwh storage....
By Batpred , 18 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Locked environments are difficult to manage, it also me...
By Batpred , 18 hours ago
-
RE: Has anyone seen this problem before? Huge anticycling times
Hi all, I had a 15kw installed 3 weeks ago. The past we...
By jamesh , 22 hours ago
-
Adia Therma - 'autopilot for heat pumps'
Thought I'd pop this one in here as the Adia proposal a...
By seatonian , 2 days ago
-
RE: Mitsubishi Ecodan R290 10kW performance
Don't know answer to final question. Your contract p...
By JamesPa , 2 days ago
-
RE: New Fogstar 15.5kWh upright solution
Ah, it seems PACE BMS are easy to source on AliExpress,...
By Batpred , 2 days ago
-
RE: Vaillant water pressure gauge vs Analogue gauge
@jamespa Agreed I don't feel concerned about this, espe...
By jeegnesh , 2 days ago
-
RE: Gov wants to alter our FIT contracts from rpi to cpi
The consultation is just part of the normal process for...
By Jeff , 2 days ago