Route of primary heat circuit through block and beam floor
This is a bit of an odd question, but please bear with me if you can 😀 I am having an extension to my house built. It will have block and beam concrete floors with UFW. The primary circuit or "heat main" needs to run from the "boiler" room in the house about 10 metres to the external wall where the ASHP outdoor unit will be. The question is really whether this should be:
1) somehow buried inside the insulation + screed in the floor. I think the pipes are 28mm, but will need some form of insulation. Any heat loss would be into the house. Also the pipes would have to be placed in such a way to not impact UFW pipes
2) pre-insulated pipes should drop underneath the void in the floor and out. Any heat loss would disappear into the air that flows through the underfloor and out the vents
I have two heating engineers I am talking to, and they come up with different answers. The architect says that the ASHP manufacturer would have an opinion, but that seems fairly unlikely as their installation manual says nothing. It seems that there are so many possible types of buildings that trying to provide this advice for all countries would be a Sisyphean task. The builder seems to think the architect or heating engineer should know.
Has anybody had an installation with block and beam floor? If so, what did they end up doing?
Posted by: @ollysomehow buried inside the insulation + screed in the floor.
You need to check the building regs on that.
Posted by: @ollyHas anybody had an installation with block and beam floor? If so, what did they end up doing?
Not block and beam, but we did have 100mm concrete 150mm celotex and 100mm concrete, this for a polished concreted floor with UFH.Ā I expect with block and beam, you should have a void under the floor and could do something similar.
We have about 5m of pipe under this floor to the boiler room and another 17m to the heat pump.Ā For this we used "Microflex UNO" 32 for the flow and return, mostly because it had the smallest bend radius of anything I was able to find and reasonably priced.Ā We put this 90mm pipe (diameter of the casing) inside two even larger twin wall pipe that was pretty robust.Ā It is in theory, possible to take the microflex pipe out and replace it with limited damage to the boiler room floor.Ā You will also notice I put some 25mm water pipe in as well as conduit for the control cables to the heatpump.Ā It has only been running for 1 month now, but seems to be working well.Ā The picture below is inside.Ā Outside I did put some 100% waterproof connectors on that are pretty expensive, they stop water getting into the insulation.Ā In hindsight, I am not sure thatĀ I should have used PTFE on the connectors, so don't follow me on that one, I should have probably used hemp and sealer.Ā PTFE seems to work though, no pressure loss in 30 days so far.
Note: I did not fully appreciated the heat loss associated with pipes in the ground, even well insulated ones, so do your research on that front.
Not B&B, but my builders are doing a class Q conversion at the moment and they laid a couple of lengths of 32mm pex-al-pex in between the layers of 75mm celotex that they used for their floor insulation.
If I was doing B&B (which I would never do, hateful system) then Iād just use microflex uno or duo and route it in the floor void and use a lintel to bridge over the missing block in the footings where It comes outside.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wifeās house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Thanks for the replies @hughf and @william1066. You have given me food for thought. If I get a definitive answer on the way it should be done from building control, I'll report back.
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 34 Online
- 5,662 Members
Podcast Picks
Latest Posts
-
@ashp-bobba interesting insights. We also chatted after...
By Mars , 11 minutes ago
-
RE: Why so many sigenergi installer recommendations?
Iāve not come across this brand, but then again I donāt...
By Mars , 16 minutes ago
-
Sanity check please. Battery storage and inverter sizing.
I had one installer essentially wanting to install a ti...
By AdamK , 10 hours ago
-
RE: Rodents! A word of warning for heat pump owners
The gaps and holes have reduced on heat pumps over the ...
By dgclimatecontrol , 15 hours ago
-
RE: Ecodan & MelCloud scheduling
I couldn't agree more. I might go so far as to change t...
By Majordennisbloodnok , 16 hours ago
-
RE: Air source heat pump roll call ā what heat pump brand and model do you have?
Forum Handle: EGP01 Manufacturer: Samsung Model: 8K...
By EGP01 , 18 hours ago
-
Thanks for the heat geek info. I've fitted my own heat ...
By bontwoody , 20 hours ago
-
RE: Does anyone have experience of a smart water meter?
Just to give a sense of scale, I've used the CCW water ...
By Majordennisbloodnok , 21 hours ago
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 2 days ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 3 days ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 3 days ago
-
RE: Heat Pump Servicing & Maintenance ā Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 4 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 4 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 4 days ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 5 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 6 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 7 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 7 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 1 week ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 1 week ago