Hi, I am planning to get a ASHP if I can satisfy myself that it won't disturb our household or the neighbours. I have seen some conversations about noise levels, and most of the replies seem to be objective, rather than subjective. The area I am interested in is measured noise after installation vs published specifications. I have a friend who got a heat pump and the noise was well above the specification. His heatpump isn't similar to size of the one I am getting, so can't infer much from his experience, but it does disrupt his sleep and disturbs his neighbours. It is also well above the published spec.

The measurements of heat pump noise are supposed to be standardised, but I don't have access to a copy of the standards, and also I am not sure the standards are representative of real world operation. For example, the Valliant 12kW VWL 125 / 6 states:

Sound power, EN 12102, EN 14511 LWA, A7/W55, sound power of 60

Firstly, the A7/W55 suggests that the ambient temperature of 7 degrees, which is clearly not the coldest it will be. An air temperature of 0c and water of 65 is more likely to be closer to max during the weekly Legionnaires cycle. The Vailant can do closer to 75c delta, but the measured noise is only a delta of 48c, so one would imagine that the noise levels have the potential to be much higher. I don't know if the fan noise is linearly proportionate to the temperature delta either.

Secondly, some people have said that the defrost cycle is also noiser that normal operation, and a different sound.

Ideally I would like an indication of _maximum_ sound pressure and something like A0/W55. The measurements of sound levels, rather than sound power, seem to be more of a marketing gimmic. This is because the Q factor (distribution/directionality) on these measurements is often based on a freestanding unit with 360 degrees emissions (a hemisphere). In most setups, the heatpump is up against a wall, so immediately it is louder that the suggested spec.

I also saw that the Valiant is rated by Quietmark, so I contacted them to see what methodolody they used to measure. I assumed they would have a more advanced measurement that included maximum sound level. I was disappointed to get the response:

"Due to the scale of the market, the variable siting of heat pump installations, and therefore the cost and time to acoustically test all these variables, Quiet Mark does not carry out physical acoustic tests of the air source heat pump category."

I understand why they do this as the cost of setting up each heatpump and testing in real conditions would be expensive. However, I think they would make it clear that they are just taking the standard N 12102, EN 14511 measurements and the limitations that that infers.

I wonder what can be done about this. It almost seems like a Dieselgate situation that the measurement can be not reflecting real life usage. It has the potential to slow down the uptake of ASHPs, which would be a shame. I would pay for real high quality information about this. Probably there is a wider market for this also.

Also, if anyone as actual measurements of 12KW units at maximum fan speed, I would be super grateful. Especially the Valliant ArcoTherm or Ecodan R32 Ultra Quiet PUZ. A video + sound measurement at 1 metre on a phone app would be a start, but is not a solution for the wider market.

Any other thoughts on the matter would be welcome.

Thanks,

Olly

 


This topic was modified 10 months ago by Mars

   
👍
2
Quote
Topic Tags
(@batalto)
Famed Member Member
Joined: 4 years ago
Posts: 1091
 

I wouldn't worry to be honest. When the pump would be at it loudest (when it's cold) people will not have their windows open. We actually find the water pump is louder than the heat pump and we do get a low hum when it's silent in the house. We never hear the pump.


12kW Midea ASHP - 8.4kw solar - 29kWh batteries
262m2 house in Hampshire
Current weather compensation: 47@-2 and 31@17
My current performance can be found - HERE
Heat pump calculator spreadsheet - HERE


   
ReplyQuote
 olly
(@olly)
Trusted Member Member
Joined: 4 years ago
Posts: 18
Topic starter  

@batalto thanks for the response. I realise in my original post I got a sentence the wrong way round. I meant "most of the replies seem to be subjective, rather than objective". I have spoken to some people who are not bothered by the sound with their setup, and some who are very disturbed. As I said in the original post, I have a friend who is disturbed by his, and his sleep is measurably affected, as are his neighbours. He is thinking of having it removed if he can't somehow reduce the sound. He is in a urban environment, and also has a larger pump, so is more likely to have issues than someone with a small pump in a house in the middle of a field. I visited another couple with two Nibes and they never hear them, but have very thick stone walls, great glazing and no neighbours, and not near any bedrooms and are happy.

I also visited someone else with a Nibe F2040 16KW and was suprised how loud it was. I measured 65db at one metre and 55db at 5 metres. That was on a iphone, so is not calibrated, however the background noise outside my house about 48db and I can hear that through some of my shut windows, so that gives me some indication.

One issue with anecdotes is that the same make/range varies considerably with output. For example the Nibe F2040 6KW is 50db, and the 16KW is 61db, and if I understand the db scale (which is unlikely!), that means one is 8 times louder than the other at source. In this way, it is easy to see that one person could say that they love the Nibe F2040, and the other says they hate it, depending on what model.

Regarding your comment about people having their windows closed at the coldest time, I agree. However, the people with the Nibe 16KW suggest they can hear it through the wall/ double glazed window when no window is open. Theirs is on the side of a house pointing out onto a field. It doesn't bother them much, but if this were in the side return of a terrace house, this would seem much louder.

My point is really that I have lots of anecdotal evidence either way, and I know that the rated noise of the heat pump only at some parts of its operational range. Overall the picture is still a bit merky. I hope to find a way to resolve this. Knowing the maximum sound power of the heat pumps would really help. A graph of noise vs temperature delta would be fantastic, if only they would publish this.



   
ReplyQuote



(@batalto)
Famed Member Member
Joined: 4 years ago
Posts: 1091
 

@olly they do have these, the issue you'll come across is that sound volume very much depends on context settings e.g. where the pump is. Ours is next to a hedge on one side, which absorbs the sound. If it was surrounded by all hard surfaces it would probably be louder.

The sheet in my signature has a sound approval calculator. Maybe that might be a good place for you to start?


12kW Midea ASHP - 8.4kw solar - 29kWh batteries
262m2 house in Hampshire
Current weather compensation: 47@-2 and 31@17
My current performance can be found - HERE
Heat pump calculator spreadsheet - HERE


   
ReplyQuote
(@prunus)
Estimable Member Member
Joined: 4 years ago
Posts: 64
 

To add, another thing is the sensitivity of the occupants.  I specifically chose a larger double-fan heat pump because it was quieter (60dB) than a smaller one with single fans (63dB). The only place next to the house for it to go was beside the kitchen. This means you're about 1m away from it when making a cup of tea.  That was a risk we took since there was not really anywhere else to put it.  The heat pump isn't so bad when you are several metres away, but the noise is still noticeable and it makes the kitchen pretty unpleasant when it's buzzing away.

Also the 'you don't run it when the windows are open' is a fallacy, because we need ventilation - if your windows have trickle vents then you have some part of the window open where sound can get through. Most people don't have a MVHR system to prevent this.

One other knob I tried is 'night mode', which can drop the fan speed to (at most) 50% when you push a button (or timer or relay contact). This doesn't make the slightest bit of difference. I'm exploring if this is due to other issues with the installation. (It was also super noisy to begin with due to air in the pipes, which has gone away as I keep topping up the water)

A family member is autistic and can't abide the noise even at what I'd call barely audible volume, despite their room being two rooms away from the heat pump. We have to turn the whole thing off at night. So we're looking at moving it down the bottom of the garden, which will put it 15m away from the house. It'll make our efficiency worse and require substantial construction works, but you gotta do what you gotta do...


This post was modified 4 years ago by Prunus

   
ReplyQuote
 olly
(@olly)
Trusted Member Member
Joined: 4 years ago
Posts: 18
Topic starter  
Posted by: @batalto

@olly they do have these

I am having trouble finding any kind of graphs related to noise. The installer manuals have some more information. For example for the aroTherm installation manual quotes some figures on page 94.

If you look at the figures a couple of things are clear:

1) Input air is 7c for all figures. No lower temperatues are quoted, so clearly this is not maximum sound pressure

2) Noise reduction mode figures aren't quoted for for water temperatures above 35c. Does this mean that noise reduction mode can't produce enough heat with flow temperatures with a delta greater than 28c? If so, this is a big limitation. For hot water supplies and radiator systems this might mean this feature is useless.

 

I found even less information for the Mitsubishu Ecodan. Do you have examples of other manufacters that give the full dataset of sound information?

Regarding the spreadsheet for commissioning that you had in your footer, it was indeed interesting. Thanks for that. The issue remains that if the published sound pressure levels are not the maximum sound pressure levels, then it doesn't really answer the question of whether it will produce acceptable sound levels. It would no doubt help with planning permission/permitted development, as I am sure that they take the sound pressure on the appliance label, not maximum sound pressure.

 

 



   
ReplyQuote
 olly
(@olly)
Trusted Member Member
Joined: 4 years ago
Posts: 18
Topic starter  

@prunus you have a point about trickle vents. Yours is another case where I feel full sound pressure information would help, rather than just an appliance rating at A7/W55. Have you ever measured your unit to see if it is in line with the calculations done during the planning phase?

I am also sorry it has caused so much inconvience to you. Whilst I think there is lots to say about sound sensitivity of different people, the accoustic environment that the unit is installed in, etc, the point I really want to pickup on this thread is that I feel the rated sound pressure levels are not representative of the units for the full range of operation. If anyone has empirical measurements which could confirm that on at least one unit, that would help.



   
👍
2
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 5 years ago
Posts: 4427
 

@olly 

Hi,

You can find more detailed noise data in the attached documents. The access code for the Midea document is midea2020.

 



   
👍
2
ReplyQuote
 olly
(@olly)
Trusted Member Member
Joined: 4 years ago
Posts: 18
Topic starter  

Wow @derek-m, I see graphs. Thanks! The frequency curves are interesting. However, even with the extra info, the same problem remains for the Midea as all measurements are at air 7c, but the unit is measured for heating performance down to Air -20c to water 55c, which gives a delta of 75c across the compressor, rather than the sound measurement taken with only a 48c delta. Now, I appreciate that at -20c it is ok to have excessive noise, as it is pretty rare, but many winter nights are just below zero in the UK, so the measurement is not really a clear indicator of noise. From the PDF:

dB is the maximum value tested under the conditions below:
1) Outdoor air temperature 7C DB, 85% R.H.; EWT 30C, LWT 35C. Free compressor frequency.

2) Outdoor air temperature 7C DB, 85% R.H.; EWT 47C, LWT 55C. Free compressor frequency

The Ecodan gives even less for us to understand what air/water temperatures it is running at. From the PDF:

Sound data is taken when the system is running stably.

Relatively large noise could be heard transiently in the case 4-way valve, or LEV operates

The best case would be that the system is measured at maximum load, but unfortunately I can't tell. If it is, then I am impressed. However, I think it more likely it is measured at A7/W55c, as I am guessing that is what is in the ISO spec. Perhaps somewhere else there is this data. If anyone has a copy of the ISO spec, that would be great also.


This post was modified 4 years ago 2 times by olly

   
👍
2
ReplyQuote



(@derek-m)
Illustrious Member Member
Joined: 5 years ago
Posts: 4427
 

@olly 

Hi,

I think the only data that you will find on the internet will be no more detailed that that provided.

I suggest that you contact the technical help departments of the various manufacturers to see if they can provide any further data, or at least that they can confirm the power level at which the readings were taken.



   