Optimising ecodan ASHP
Hi,
I am trying to optimise my installation and have learnt a lot in the past few days but still have some significant gaps in my knowledge!
I have an 11.2kw ecodan hearing all rads to a 4 bed detached home. I had been controlling by third party thermostat with overnight set back, but a few days ago switched to weather compensation (and turned off the overnight setback last night as it was so cold…but that was expensive! So will leave it on in normal times).
it’s set to 42/-4, 32/15. No science behind this I took a guess but it seems right at maintaining the thermostat downstairs at 20 so far. Upstairs a bit cold in this cold weather, otherwise ok.
I finally set up the WiFi unit yesterday (a year later…) so finally have some data! There doesn’t seem to be much difference between flow and return temps. See pic below.
my questions are: (sorry there’s a few, I will take as many or as few answers as I can get!)
1. should I be trying to increase this delta and if so how do I do that?
2. WC seems to increase comfort but doesn’t decrease energy consumption - does that sound right? At the moment tends to be drawing about 2kw at any given time usually. Sometimes this falls and I don’t know why…
3. Is the fall in flow temp likely a defrost cycle? This seems to have happened hourly today, it is cold so seems right?
4. How do I know if my heat pump is cycling?
5. I can’t get data on consumption/delivery as the app says no consumption meter fitted. There is an sd card in there which I thought was saving that data. Any idea on how I can get this or is it a lost cause?
6. I understand moving the curve at the -4 end, but not at the 15c end - any tips? Or do I just wait and see as it gets warmer?
thank you!
Your delta T is bigger than 2 probably 4 or 5. If you press the legends on the plot it will remove the tank temp and rescale so you may able to see the delta T. Or you can look on your unit under settings thermistor readings and it will show you the current flow and return temps.Posted by: @hotheat
-- Attachment is not available --
WC will save energy by using a lower flow temp when it warms up but isn’t going to do anything at current freezing temps.
Drop in power and flow temp is defrosting
If it was cycling the flow temp would be increasing and decreasing every 10 mins you will get cycling when it’s warmer and the heat pump can’t reduce its power any further to maintain the flow temp so it has to turn off for a few mins then back on to heat it back up hence cycling on and off.
Under the reports tab in the app are energy reports these can show estimated consumption and generation.
The lower end looks good at 32C that is the lowest temp I can use without the unit cycling you may be able to lower it further it’s just trial and error.
I can't answer all of your questions but here goes for some of them:
(1) I am not sure which delta you are referring to - rad to room or LWT/RWT. The latter in the mage you posted looks OK, about 5 degrees.
(2) there is a lot of debate about this, see other threads. The general principle is that WC is the best way to run heat pumps, with Auto-Adaption if you have it (Ecodans do, I believe) which tweaks the WCC Set LWT, taking into account indoor temperature. But not everyone runs them this way.
(3) The fall in the LWT in the image you posted is a defrost cycle. The giveaway clue is the LWT goes below the RWT. Over-shoot (modulating) cycling looks similar, but the LWT stays above the RWT. Examples of both can be seen in my recent posts in this thread.
(4) Visual inspection of the LWT/RWT trace, for the characteristic rise and fall in LWT, and distinguish between defrost and modulating cycles as above.
(5) Can't answer this one, as I have a Midea unit rather than an Ecodan.
(6) The principles are the same at both ends of the WCC, in practice you are more likely to tweak the left hand end in cold weather, and the right hand end in warmer weather. The end points just describe a (mostly/usually) linear relationship between the outside air temp and the Set LWT.
Midea 14kW (for now...) ASHP heating both building and DHW
Ref 5 - you need the electric and heat meters to get the full data , usually about a £700 add on
Posted by: @walkers-heatpumpRef 5 - you need the electric and heat meters to get the full data , usually about a £700 add on
For sure, that is the gold standard, but you can get some Ecodan data, see posts by @kev-m, though obviously it comes, like my data from a Midea unit, with the caveat that it comes from manufacturer supplied raw data, and as a result dieselgate/compressorgate precautions apply.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay the data I've seen without the metering set up hasn't looked great, especially during summer season where it overestimates standby power 3-4x greater
have you been able to get the consumed/delivered data from the main controller? It's accessed using the far right of the four buttons. The every hour drop in consumption in this weather is a defrost. The ASHP stops for a few minutes to do this then starts up again. Overall you're using more energy though because the refrigerant and the flow temperatures drop and need to recover.
Posted by: @walkers-heatpumpthe data I've seen without the metering set up hasn't looked great, especially during summer season where it overestimates standby power 3-4x greater
There certainly are discrepancies, but I am fortunate that for the energy in I can measure them, as I have an external heat pump dedicated kWh meter. Having done comparisons over time, I have found on average (there are minor apparently random variations) the true (meter) reading is about 1.18 times more than the values derived from the Midea data (reported amps and volts in, collected at minute intervals over modbus, and then used to calculate the kWh in values). I have now incorporated this correction factor into my current reported data, but not they historical data (before 29 Nov).
The energy out data I am less sure about, because as you correctly say I would need a lot of expensive and invasive equipment to verify it. The flow rate (I use modbus minute by minute flow rate x LWT/RWT delta t x specific heat of circulating fluid, which in my case does have glycol, to calculate it) I am fairly sure about, my Midea runs with a pretty steady flow rate, and the value agrees so far as i can make out with that obtained from an analogue flow meter in the circuit. The specific heat value I use is 4.05, for a 10% glycol mix, again that shouldn't be too far out. The values that are uncertain are the LWT/RWT - where and how exactly are they measured? - but as it is the delta not absolute values I am interested in for the calculations, I might not be that far out for the delta t, even if the absolute values are both out (the same way) by a few degrees. But the bottom line remains, I can't prove the modbus collected Midea data is correct.
I'm mostly interested in the heating side of things, that is when energy use goes up greatly. Even if the errors are greater in the summer, it doesn't matter, insofar as I am not looking at that data, though of course it might well affect things if I looked at very long time frames eg annual (S)COP.
Midea 14kW (for now...) ASHP heating both building and DHW
To optimise, you really need real time energy consumption from the ASHP. My pump runs off an exclusive breaker in the consumer unit, and I use a shelly EM with a clamp round the live exiting the breaker ( https://shellystore.co.uk/product/shelly-em-50a/) for about £50. I collect the data using Home Assistant on a Raspberry pi with the very easy-to-use shelly and melcloud integrations, I keep a log/graph of flow, return and outside temps, Power usage and H/W tank temp. Takes a little while to set up but once it's there you can home in on getting it super-efficient. The image shows quite low power and a lower flow than return temp as it's just starting a defrost, but you get the idea of where it's been from the graph.
@cathoderay thank you - appreciate you taking the time to respond to all of these qs and useful to understand defrost vs cycling. Yes I think I will end up with WC with a night time setback once cold snap ends
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 65 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@jamespa cannot find loss calculation. When they get i...
By BAMi , 5 minutes ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 46 minutes ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 3 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
Something else... that works for some people... LG ha...
By Tim441 , 3 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 4 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 5 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 5 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 6 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 17 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 20 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 21 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 24 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 5 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 6 hours ago
-
SolarPV tables / online calculator
By MichelleC 13 hours ago
-
By Toodles 2 days ago