Mitsubishi Ecodan-Zubadan in Hybrid /backup configuration with gas boiler
Hello!
I own a Mitsubishi Ecodan / Zubadan ASHP 14kW with a gas boiler attached as backup heat source. It can help in colder periods but it should also switch based on energy price.
Mitsubishi also released this document
Which states that it can be achieved but it is not technical.
The HP has an Intelligent operation mode where it can select Cost based between electricity and gas based on the price/kW of each energy.
I expect as example that at a certain outside temperature,
COP=3 and 3kW of heat are produced from 1kW electricity
1kWh electricity costs 0.6. But it produces 3kWh heat with a cost of 0.2 /kWh heat
1kWh produced with gas costs 0.2 => it produces 1kWh heat with a cost of 0.2
=> it should stay as it is for now. As soon as the outside temperature drops and COP drops => it should switch to gas boiler which becomes cheaper /kWh produced.
Settings:
Service menu / Operation settings / Boiler Operation / Hybrid settings/Priority Mode: Cost
Service menu / Operation settings / Boiler Operation / Intelligent settings/Energy Price / Electricity: 0.6 */kWh
Service menu / Operation settings / Boiler Operation / Intelligent settings/Energy Price / Boiler : 0.2 */kWh
I can force a boiler operation when accessing
Service menu / Heat source setting (Standard/Heater/Boiler/Hybrid *7) : Boiler.
But when i select Hybrid, it only runs on HP, although it should switch based on the Cost setting.
To test, I used a ridiculosly increase price for electricity (1000x) and it does not switch to gas.
I can also force only boiler operation using the settings:
Service menu / Operation settings / Boiler Operation / Hybrid settings /Outdoor ambient temperature: HP-Boiler when under -15 and Boiler to HP when over 1 (deg C). But it does not account the cost variable and it never switches.
The manuals say very little about this topic. They say it should work.
if anyone has this setup and can advice or is an installer that did this before. thank you in advance for helping me out.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 309 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Electricity price predictions
i only know about Intelligent Octopus Go ToU, where acc...
By SKD , 41 minutes ago
-
RE: What determines the SOC of a battery?
@batpred I didn't write the Seplos BMS software, I a...
By Bash , 1 hour ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
Without knowing it, @andrewj, you've laid down the gaun...
By Majordennisbloodnok , 2 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@tasos and @cathoderay thanks. I have some history grap...
By benson , 2 hours ago
-
I am having my existing heat pump changed to a Vaillant...
By trebor12345 , 2 hours ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 3 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 3 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 5 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 6 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 7 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 11 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 21 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 23 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago