Midea M-thermal Mono ASHP - setting Schedule / Timer
Good morning. New member. Recently installed 16kW Midea M-thermal Mono ATW Heat Pump - - providing DHW and supply to both UFH & rads.Â
Seeking advice from more experienced members here.Â
My grid electricity is around 40% cheaper from 2330 - 0630 than daytime. We very rarely need 'hot' DHW after 2100. So ....  obviously I can use my heating (UFH & Rads) controller to switch off demand in the evenings when the house is warmed up & grid electricity is 'expensive' - - but how do I do the same for my DHW ??
I have tried to use the 'Schedule / Timer ' options on the Midea wired controller - - but it is not clear to me how to achieve this Â
When I go into the controller Schedule panel it offers START and END times (clear enough!) but also requires MODE (HEAT / COOL / DHW) and TEMP. Â
My questions ->
* what is the best way to 'switch' off any DHW heating demand on my ASHP in the evenings ... delaying that demand until I have cheaper grid electricity at night ?
* is it to use the SCHEDULE functionality in the Midea controller ?
* if so, do I just need the TIMER screens ? ignore WEEKLY SCHEDULE ?
* what MODE should I set ? and what TEMP ?Â
* what happens to my system outside of times programmed into the SCHEDULE screens ? is it ' business as usual' ?
I look forward to your thoughts.Â
Â
@dealstriker - welcome to the forum, and to the crazy world of the Midea controller.
I have my controller set up to have the DHW heating on between 1300 and 1400 every day (no time of use tariff, so use the usually warmer part of the day), and use just the Schedule > Timer screen, just one (first) row ticked, start 1300 end 1400 mode DHW temp 50 (same as on front page/main screen).
This does seem to work, but when I tried a while back to do something to time the heating to be off overnight, it didn't work. But, as I say, the single row DHW timer does work. Â
I think the Timer screen is just a global every day screen, the second Weekly Schedule screen is there to set different timings for different days of the week. Â
Midea 14kW (for now...) ASHP heating both building and DHW
- 22 Forums
- 2,097 Topics
- 46.2 K Posts
- 56 Online
- 3,385 Members
Join Us!
Latest Posts
-
RE: Ecodan consuming 100kwh per day in new build!!!
Hmm Before doing that I would want to be certain that...
By JamesPa , 14 minutes ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 20 minutes ago
-
RE: Heat pump solutions and/or installer recommendations for France
Sorry Bravo. I have no installer contacts outside the U...
By Mars , 11 hours ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 11 hours ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 19 hours ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 22 hours ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 2 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 3 days ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 3 days ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 4 days ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 5 days ago
-
RE: Say hello and introduce yourself
Yes please do Suggesting a loss in the region...
By JamesPa , 5 days ago