How is water flow controlled in a heat pump system?
Comming from a +20 years old heatpump installation where the flow of the water flow is fixed I am trying to understand how the water flow is controlled in modern modulation ASHP.
I am looking at the simple installation of floor heating, no thermostats in the house, floor heating always on, no water buffer....
When the heatpump modulates because heat demand drops because of higher outside temperature.
- do HP keep the water flow constant (and this changing the delta temperature over the inflow-return)
- do HP change the flow so delta temperature over the inflow-return stays constant..
Or what do heatpump (of the circulation pump) control and how?
And is there a best solution for efficiency?
Walter
The short answer as always is it depends, different models do it differently. Mitsubishi is constant flow rate so as the heat pump modulates down you will see changes in delta T. Other manufacturers modulate the circulation pump flow rate and try to target dT5.
Is there an inherently better way to do it for efficiency, I don't believe so as just different sides of the mass flow equation in my opinion unless you want get into the watts a circulation pump uses.
Thanks for the feedback!
How does Mitsubishi control the flow rate? Is that the pump that does measure the rate or the Heatpump that measures and controls the pump power? And how is the pump power controlled?
(Sorry for the questions; I have a hard time finding that info on the installation guides).
I indeed think my question goes back to how different manufacturers implement their controls and I guess it goes together how they manage the modulation of the heatpump.
Thinking about it: Lowest water side temperature is best... So that would mean high water flow, meaning there would be no need to modulate the circulation pump down...
Maybe only when there is no heat demand from the house.
Opening the question how manufacturers would organize the modulation of the heatpump...
Posted by: @wvtienen1How does Mitsubishi control the flow rate? Is that the pump that does measure the rate or the Heatpump that measures and controls the pump power? And how is the pump power controlled?
There is a flow meter that measures the flow rate and can be accessed on the heatpump controller, the pump speed/power can be set from the heat pump controller to an arbitrary value (1-5), you can then check the flow rate that each of these values achieves.
@gary and how does Mitsubishi control the pump? Is there stearing signal going to the pump (pwm?) or ...?
Sorry fore the detailed question. In think I need to read about circulation pump controls...
@wvtienen1 Yes its controlled by a signal to the pump, if I change the value on the heatpump controller I can hear the pump speed up or slow down and I can see an increased or decreased flow rate on the controller.
- 26 Forums
- 2,342 Topics
- 53 K Posts
- 209 Online
- 6,000 Members
Join Us!
Worth Watching
Latest Posts
-
@majordennisbloodnok yes, still dead. Shame becauase it...
By Morgan , 3 minutes ago
-
RE: Configuration issues with 10kW Midea R32 heat pump
There's no setting. The app just doesn't work properly....
By benson , 5 minutes ago
-
RE: Poll for Time of Use, tariffs, technology
@papahuhu lithium prices have turned higher last few mo...
By Tim441 , 15 minutes ago
-
-
RE: Heat Pump Performance Analysis Web App using Modbus Data
@redzer_irl ok. Thanks I will have a look when ive got ...
By bontwoody , 39 minutes ago
-
RE: Here is my heat pump installation with questionable COP in Italy
Well in Italy there is nothing controlling the quality ...
By materox345 , 2 hours ago
-
RE: 10kw heat pump run in 24*7 data?
The curve really depends on the emitters in relation to...
By JamesPa , 3 hours ago
-
RE: Has Anyone Else Noticed a Decline in Tradesmanship?
Sadly that is true. There are various reasons of cours...
By JamesPa , 3 hours ago
-
I have just had a new solar array and batteries install...
By TechnoGeek , 6 hours ago
-
RE: What a Bad Heat Pump Installation Looks Like
@editor The trick to an inside unit installation is to ...
By MikeFl , 16 hours ago
-
RE: Different dT on each radiator?
The way heating systems are designed will result in rou...
By JamesPa , 19 hours ago
-
RE: Setback savings - fact or fiction?
PS by visually merging the two tables as above, I ended...
By cathodeRay , 1 day ago
-
RE: Homely for Daikin Altherma 3 - Petersfield Area
@russ If you would care to pose your questions on one o...
By Toodles , 1 day ago
-
RE: The good, the bad and the not that great – my heat pump installation
@cathoderay the guy I spoke to on the phone seemed very...
By Burtis , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
I get the impression that that comment "they don't comm...
By JamesPa , 2 days ago
-
@majordennisbloodnok Just in case there are variations ...
By Toodles , 2 days ago
-
RE: Latest NIBE model has known defect and no solution
@kings I’m glad I could help. NIBE are taking this very...
By Mars , 2 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@jamespa yes, I'm under no illusions but in some respec...
By AndrewJ , 2 days ago
-
RE: Electricity price predictions
It seems the end of cfd payments is in sight, even if a...
By Batpred , 2 days ago