Grant Aerona circulation/system pump staying on
@mikefl Parameter 41 22 is 30 so presume that's 30 mins which the pump seems to be ignoring.
The other oddity is the outdoor temperature at which the system pump switches off which varies from 5.5C to 7.5C, so it doesn't seem to be following parameters 43 11 & 12 (we've altered those as a test but it makes no difference).
And the sensor still reckons outdoor temp can increase 1.5C in seven minutes which maybe points to it being the issue.
Busy time for installers and engineers so we'll have to wait patiently until someone comes 😐
Hopes it’s ok to jump onto to this conversation, I have found it really useful but have a further question.
The circulation pump in my system have been on for the past few days due to colder weather…. The issue I have is that it is rather noisy.
Could it be a case of air in the DHW system? The noise stops when the heating kicks in.
If so… any ideas on how to bleed the DHW system?
Thanks in advance.
Posted by: @richwThe circulation pump in my system have been on for the past few days due to colder weather…. The issue I have is that it is rather noisy
Hi @richw, there should be manual bleed valves on your piping or Low Loss Header/Volumiser if fitted. (Items 10 and 11 on diagram) If you don't have a low loss header (item 8) then check what circulation path is open to the pump inside the Grant Aerona when it is running in frost protection. Check it's not pumping against closed 2 or 3 port valves when CH and DHW are and causing the bypass valve to lift & open, Grant pre-plumb cylinders have an automatic bypass valve (Item 6) across the primary flow and return pipe connections, designed to prevent primary flow becoming excessively low, it's noisy when it lifts and operates. It shouldn't normally operate. It's these subtle details such as the internal pump switching on for frost protection that seem to go overlooked by Grant system installers.
@richw Is the frost protection symbol on (on the control panel) when you hear the noise?
We get the noise but not the frost protection symbol.
And more bizarre with the control panel as it increased outdoor temp by 5C before our eyes.
Mystery solved. Grant says it can happen where the system pump sticks on and it's not to do with frost protection. Doing reset on the pump stops the issue.
My pump stays on 24/7, as it's the only pump in the system and I don't ever turn my heating off.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@sentinam hi, did resetting really solve the issue. It hasn't for me...The exact same thing is happening to my grant heat pump for the last 2 weeks. The water circulation pump is running for long periods (i.e. no frost protection symbol) when the frost protection turns off and again starts up in the evening several hours prior to the frost protection kicking in?
Really would be interested to know I you got this issue sorted.
Cheers.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 48 Online
- 5,736 Members
Podcast Picks
Latest Posts
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@downfield I tend to agree. We have 2 heat pumps (my ...
By Tim441 , 11 minutes ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
For best results with induction hobs use stainless stee...
By Scalextrix , 11 minutes ago
-
RE: Who’s Caved and Switched the Heating On Already?
Central heating still switched off and will be until Oc...
By AllyFish , 2 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Please read to the very end of this post, I shift my po...
By JamesPa , 3 hours ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 3 hours ago
-
RE: Midea ASHP – how to set weather compensation
I think it is a bug in the code, it comes on even when ...
By cathodeRay , 17 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 19 hours ago
-
RE: Buffers, hot water and cooling
@jamespa Your reasonably close! Especially with warmer ...
By dgclimatecontrol , 20 hours ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 1 day ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 2 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 2 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 2 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 2 days ago
-
RE: Solar Thermal DHW and ASHP
I was originally contemplating a solar thermal installa...
By jamespetts , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
My system installed in July 2024 has produced 6.4mWh in...
By jamespetts , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@judith thanks for your suggestions. Starting from col...
By GrahamF , 3 days ago
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 3 days ago
-
RE: DESNZ doing a survey which asks the right questions!
Without a survey their only source of data is probably ...
By JamesPa , 3 days ago