@batalto, your latest weather comp settings sound about the same as ours now and I'm thinking of knocking it down a bit. I agree about the water; I'm all for saving a few quid but not at the expense of comfort. We have electric showers for now so not an issue for us.
Hopefully you'll stay warm with the latest adjustments.
@kev-m we'll see. I'll note that last night we used 11kw and delivered 42 in heat - COP 3.88. and the night is the coldest time...
Yesterday as a whole we used 36kw and delivered 110kw in heat - COP 3.05
@batalto, my corresponding numbers are 30.6 and 4.6. I turn the room temps down during the day and through the night (something I'm going to experiment with). My delivered energy has stopped recording so I don't know COP.
Some feedback for everyone in two charts. As a note, I've created my own measure of efficiency beyond COP. At the moment its called COP-A (or COP per degree ambient). I'll explain my reasoning below.
This graph shows the impact of radiator balancing and weather compensation adjustment down. I started looking at the balance on the 2nd of November, which you can see coincides with a big drop in COP as we had a cold night. On the 3rd I adjusted them further and reduced my weather comp to 55 degrees at -2 and 33 at 16 degrees. You can see the COP easing upwards. However I find the graph very clunky to draw any conclusions.
The solution (in my view) is to link ambient temperature and COP; as these are the two most critical to performance. What I've done is take the COP and divide it by the ambient temperature. This gives me COP per degree ambient. The lower the number, the worse the performance of your system.
As you can see, there is a much clearer outcome from this. Even with a falling ambient (or rising) you can see how efficient your system really is. If you maintain your COP but your ambient drops your COP-A has risen. I have no idea how this metric might perform over time, but at least it delivers an insight beyond COP.
@batalto Nice indication of the implacations of flow temperature, try to drop your curve even further and disable all you other levels of control by turning them up fill (except your bedrooms). Control your internal temperature by adjusting the curve. You will find a huge differance and when you find the sweetspot for your house you wil need no furter control.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@kev-m that's an issue to cross when I get there lol. But it's more about trying to take cop out of the theoretical and ground it in reality so you can compare day to day. If today is warmer you can easily compare using this factor
Another day, another filter clean. Barely anything in there today
Curve adjusted down again last night - we are now at;
Max: 50 @ -4 degrees
Min: 25 @ 15 degrees
I might leave these alone now and track for the next week. I've made quite a few changes recently and I need to see the impacts
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 12 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Humming sound on new install.
One other thing, I haven’t balanced the rads yet so cur...
By AdamK , 4 hours ago
-
Funny story Graham, when I started looking to ...
By DREI , 5 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Possibly not the answer you might want, but if it were ...
By Temperature_Gradient , 7 hours ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 9 hours ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 10 hours ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 11 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Yes Octopus only have the £9 a month service plan for t...
By NJT , 13 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
@allyfish Dogs have owners - Cats keep staff. You are o...
By Toodles , 13 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 13 hours ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 19 hours ago
-
RE: Midea ASHP – how to set weather compensation
I think it is a bug in the code, it comes on even when ...
By cathodeRay , 1 day ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 1 day ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 2 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 2 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 2 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 3 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 3 days ago
-
RE: Solar Thermal DHW and ASHP
I was originally contemplating a solar thermal installa...
By jamespetts , 3 days ago
Members Online
No online members at the moment