HomeArticles
DIY Heat Pump Installations: Navigating Legal and Regulatory Hurdles
By
DIY heat pump installations
My interest in DIY heat pump installations began when I converted my old garage into a workshop. As a keen and experienced ‘DIYer,’ I wanted the satisfaction of doing the entire project myself—including heating this previously damp and dark space. I chose to install a mini-split air conditioner in heating mode because I could keep it completely separate from the house, it was relatively cheap, and I have previous experience with these systems.
The practical side of the installation was straightforward, especially compared to understanding the permitted development and planning application aspects! In this article, I’ll share what I learned about the legal and regulatory aspects of installing my own system. It should be applicable to both dedicated air source heat pumps (ASHPs) and split-system air conditioners being used to heat spaces such as workshops, home offices, etc.
Permitted Development
Many professional air-conditioning and heat pump contractors state that any installation can be done under ‘Permitted Development’ (PD). In many situations that may well be the case, but it should be noted that the PD route has many restrictions. The following is a summary of the legislation, which is slightly different for England, Northern Ireland, Scotland and Wales. You should check the full details depending on where you live – there are links are at the bottom of the page.
The restrictions are typically:
  • Compliance with MCS Planning Standards or equivalent standards.
  • Only one ASHP permitted per property. (A block of flats usually counts as one property.)
  • The ASHP unit must be more than 1m from property boundaries. It must be more than 1m from the edge of a flat roof and not on a pitched roof.
  • There mustn’t be a wind turbine at the property.
  • THE ASHP mustn’t face a highway if installed above ground storey.
  • The ASHP must not be on, or on the land of, a listed building.
  • The ASHP must not be in an Area of Natural Beauty (AONB), National Park, Conservation Area or World Heritage Site.
Apart from the first in the list, the requirements are clear. The first one, the MCS Planning Standards. is somewhat contentious, and has been discussed in several posts on the Renewable Heating Hub Forums. In summary:
Fortunately, the Permitted Development legislation specifies ‘MCS Planning Standards or equivalent standards’. Unfortunately, there isn’t guidance on what is considered an ‘equivalent standard’, but it could be argued that the following would be valid as an ‘equivalent standard’.
  1. Selecting an MCS approved heat pump
  2. Working within the recommendations of MIS 3005 except for the MCS certification requirement
  3. Meeting the noise calculation requirements of MCS 020 (see below)
In my opinion, this part of the legislation lacks clarity. That MCS wrote the standard that has been included in the legislation appears dubious, especially since it requires installers have MCS certification (a process from which MCS itself financially benefits). A more open approach would be to either detail the requirements in the legislation itself, or to have several organisations offering acceptable certification routes, which would create a competitive market.
The MCS 020 Noise Calculation
It is perfectly possible to do the equivalent of the MCS 020 noise assessment yourself. The guidelines look confusing, but have been made more user-friendly by Heat Geek in their video.
Can you DIY install under Permitted Development?
Given the above, yes, I believe it possible to do a DIY installation of an ASHP, working within the PD rules, and fulfilling ‘equivalent standards’ to the MCS Planning Standards requirement. Indeed, MCS themselves, say that ‘an MCS certificate is not a mandatory or legal requirement for system installation’. See https://mcscertified.com/consumers-communities/certificate-queries.
However, there are a couple of other things that should be considered:
The system must be for heating purposes only.
PD excludes systems that are capable of cooling – i.e. air-conditioners. However, many Local Planning Authority departments are happy to take a sensible approach as they realise that people are using air-conditioners as heat pumps. Also see the conclusion below.
Permitted Development may be restricted by the Local Planning Authority (LPA)
Some LPAs restrict the installation of ASHPs under PD by imposing an ‘Article 4 direction’. This is typically invoked by inner city LPAs where they think noise could an issue in densely populated areas, or it could detract from the unique architecture of an area. See https://commonslibrary.parliament.uk/when-is-planning-permission-not-needed-permitted-development-in-england/
Planning Permission
If your proposed installation doesn’t meet the PD requirements, it doesn’t necessarily mean you cannot have an ASHP. Instead you must obtain Planning Permission.
Even if you intend to go down the PD route, an email to check the position with your LPA is a good idea. In my experience, LPAs vary, ranging from unresponsive to disinterested to pragmatic to obstructive, but I think it is good to establish where you stand before committing time and money.
While LPAs are under pressure to permit renewable heat systems, they do have the power to make you remove a system if they consider it in breach of Planning Permission. It can be better in the long run to have some evidence showing you approached them prior to installation.
Other regulatory considerations
As well as Permitted Development and Planning Permission, you should also consider the following regulatory requirements prior to undertaking a DIY ASHP installation:
District Network Operators
Your electricity is supplied by the District Network Operator (DNO). They need to be notified prior to installing a heat pump (or electric vehicle charging point) so they can use the data for infrastructure planning. Note that
  1. the DNO is not necessarily the company you pay your bill to, and
  2. you are not seeking permission, it is simply a requirement to inform them.
In my experience, DNOs can be slow to respond and are only interested in dedicated heat pumps, rather than small air-conditioners acting as ASHPs. Nevertheless, they should be consulted as a matter of diligence. The process for notification them is currently changing, which will hopefully improve response times. See https://www.energynetworks.org/industry/connecting-to-the-networks/connecting-electric-vehicles-and-heat-pumps
F-gas
Heat pumps utilise refrigerant gases. If it’s an F-gas (fluorinated gas) you are required by law to use a F-gas qualified professional to do anything involving the refrigerant connections. This shouldn’t stop you doing the rest of the installation yourself, it’s just any F-gas connections or lines that must not be touched. When purchasing your system will need to inform the merchant which F-gas installer you will be using.
Note that some refrigerants such as R290 (propane) are not F-gases. This removes the requirement for an F-gas registered installer.  However, R290 propane is highly flammable which introduces a significant risk that some sellers and manufacturers are playing down. In reality it is blow-torch gas, without the added odour, being pumped at pressure around a system whose joints are continually stressed through thermal expansion and contraction! There have been suggestions that it could invalidate house insurance, but I haven’t yet seen it specifically mentioned in conditions or exclusions. That is to say, I wouldn’t be installing an R290 system in my own home!
Building regulations
Building regulations are separate from Planning Permission or Permitted Development. They are concerned with the standards of the work rather than the permission to do it.
Heat pump installations usually require Building Regulation approval, whereas mini-split air conditioners typically do not. However, as with Permitted Development and Planning Permission, I recommend checking with your local Building Control department.
Your installation should meet all Building Regulation requirements, including Part P for electrical work and equivalent regulations for plumbing, especially if there are components under pressure. The relevant Government documents are listed at the bottom of the page.
Conclusion
In summary; yes, you can do a DIY heat pump installation. Knowing that you have researched and are meeting all the legal and regulatory requirements will give you confidence going forward. Especially when you know that some professional installers don’t pay as much attention to the finer details surrounding PD and Planning Permission.
Unfortunately, if you want (and are eligible) to claim a government grant you almost always have to go down the MCS certified installer route. The process was designed to ensure the government wasn’t giving grant money to rogue installers, but it has introduced its own issues as detailed above.
Finally, the rules around PD are likely to change. From February to April 2024 there was a Government consultation proposing the relaxation of some requirements (including removing the ‘heating only’ condition that excludes air conditioners from PD). The outcome is awaited – see https://www.gov.uk/government/consultations/changes-to-various-permitted-development-rights-consultation for full details.
Good luck if you decide to DIY! It’s very rewarding and can save a lot of money too – especially if you aren’t eligible for a Government grant.
Written by Justin Macklin from Checkmark: https://check-mark.co.uk
Checkmark provides an F-gas commissioning service for DIY installations. Their website provides lots of information about DIY installation of ASHPs and air-conditioners.
Links: Permitted Development
England: https://www.legislation.gov.uk/uksi/2015/596/schedule/2/part/14/crossheading/class-g-installation-or-alteration-etc-of-air-source-heat-pumps-on-domestic-premises/paragraph/G
Northern Ireland: https://www.legislation.gov.uk/nisr/2015/70/schedule/part/2 and amended by https://www.legislation.gov.uk/nisr/2023/95
Scotland: https://www.gov.scot/publications/householder-permitted-development-rights-guidance-updated-2021/pages/8/
Wales: https://www.gov.wales/planning-permission-heat-pumps
Links: Building Regulations
Part L – Conservation of Fuel and Power: https://www.gov.uk/government/publications/conservation-of-fuel-and-power-approved-document-l
Part F – Ventilation: https://www.gov.uk/government/publications/ventilation-approved-document-f
Part O – Overheating (new residential building only) https://www.gov.uk/government/publications/overheating-approved-document-o
Part P – Electrical Safety: https://www.gov.uk/government/publications/electrical-safety-approved-document-p
Join the conversation
17 Comments
That’s an excellent overview. Thanks @Justin
Such delays shouldn’t be the case any more.
Low Carbon Technology installations (heat-pumps and EV chargers) do indeed require notifying the DNO, usually via their website.
But LCT requires much less checking to be done in comparison to devices which have the potential to export to the grid. Network Planners sometimes need to use in-house software to verify that solar inverters and storage batteries may be permitted to export, but that’s unnecessary for LCT.
The four regions for which NGED is the DNO expect to respond within 24hours of an online notification. In practice it can be as little as one hour.
I’m amused that installation of a heat-pump cannot be undertaken under PD Rights if there’s a wind-turbine at the property. Do you have a source reference for that nugget of information?
I wonder if that restriction applies to GSHPs as well as ASHPs?
Just what do we imagine could go wrong?
Is it related to potential noise nuisance?
Or do the PD Authors imagine that a wind-turbine might be on a particularly low tower such that there might be disturbed air too close to the heat pump?
@Transparent I thought you would spot that wind turbine oddity.. However that pearl landed on the planning portal. I wonder what distance from the dwelling would be required in order for the restriction to not apply?
Mind you, it could be more of a distraction than anything else, given the millions of homes that should be getting heat pumps. Those DNOs must be getting pretty busy totalling all the 2kW load per pump for each individual dwelling. Hopefully it should not take many electricians to check if a single supply can handle a heat pump..  🙂
I am not trivialising the topic, but these processes need to scale.
Ian
Are monobloc R290 really so dangerous given that the installer never has to touch the internal refrigerant loop?
Given that I have 13kg of R290 (ie propane) in a cylinder at the front of my narrowboat, most boats with a cooker will have similar, and the typical refrigerant fill for a heat pump is <2kg, you can reach your own conclusion on that one!
The source legislation is here and is definitive
The exclusion for permitted development is where a wind turbine is on the property or within the curtilage
Thanks for the reference @JamesPa
I can’t see any technical reason why PD Rights aren’t extended to dwellings with an existing wind turbine. There are many farms in my area of the Rural West Country which have wind turbines. They range from 6kW units which provide power solely to the farm, through to a 500kW unit intended to supply power for the grid.
I’ve written to the Councillor at my LPA who has oversight of all planning matters. I’m hoping they can find a planning officer who can enlighten us.
I’m guessing it’s a visual amenity consideration.  Don’t forget that permitted development means no opportunity for the lpa to review/intervene so tends to be conservative.  Personally I cant see that there is much of a visual argument against heat pumps unless very badly sited or very large.
I suppose it could be a noise argument?
Rob of York
Posted by: @JamesPa
That’s right, you can have a wind turbine (subject to restrictions) as permitted development if you don’t have an ASHP and vice-versa. Installing either a wind turbine or an ASHP with the other already present, or both at once, requires that sound level calculations are done and planning permission is required. This had some rationale to it when the same was true of multiple ASHPs, first permitted development, second needed planning permission. That was changed for detached properties allowing two ASHP as permitted development, but not for a wind turbine and an ASHP.
Noise nuisance was my first thought. All wind-turbines require noise specifications to be provided to the LPA when submitting the application. That’s tricky because it’s not just the blades and generator which could be a source of noise, but the vibration of wire stays when wind-speed just happens to be at a certain velocity.
However I think the legislation is too wide in scope.
Imagine a rural farm on raised ground with an upslope from the direction of the prevailing wind. It’s a good location for a turbine. But that could be anything from a small domestic unit mounted on a 21-foot scaffold pole to a commercial turbine supplying to grid. The nearest neighbour could be well over a mile away.
These medium-sized turbines are widespread on farms across the West Country. They might generate up to 500kW.
I can’t see any overlap of constraints between this sort of turbine and an ASHP at the adjacent farmhouse!
Are the civil servants thinking of a domestic turbine within  a suburban garden?…
… in which case the definition of “curtilage" needs specifying.
Rob of York
Posted by @Justin
The system must be for heating purposes only.PD excludes systems that are capable of cooling – i.e. air-conditioners.
That was changed. It is now the case that The system must not be for cooling purposes only. So air-to-air heat pumps that both cool and heat fall under permitted development.
Yes. The pd is for heat pumps on ‘domestic premises’.  The term curtilage is frequently used on planning law and, to the best of my knowledge, just means the property boundary.
So a farmhouse isn’t “domestic premises"?
Is that being defined because there is or isnt a boundary wall between the house and the agricultural buildings?
Or because it may or may not have its own electricity supply?
I do have a wind turbine within the curtilage of my own home. But the farm buildings are ¼mile away in the valley.
TurbineWestMd
Without doing some research I can’t immediately answer that question in planning law, but I would think it almost certain that the matter has been settled by one or more cases, albeit that case law continues to evolve.
The meaning of curtilage (also in practice a matter for case law) is discussed here
@Transparent
Further to the above the actual text, describing what is permitted, reads
G.  The installation, alteration or replacement of a microgeneration air source heat pump—
(a)on a dwellinghouse or a block of flats; or
(b)within the curtilage of a dwellinghouse or a block of flats, including on a building within that curtilage.
Thus, although the title uses the word domestic, the actual text doesn’t refer to ‘domestic premises’, it refers to ‘dwelling houses’ and ‘flats’.
The interpretation section of the same order has something to say about the meaning of these terms and the Use Classes Order 1987 will also be relevant, possibly definitive.
A farmhouse, if principally designed for living in, would be a dwelling house in my reading.  If it were designed for mixed use it may be questionable.  The definition of curtilage therefore becomes relevant and I posted a link where there is discussion and links to some relevant case law.  In essence it’s context dependent.  Hopefully this may give some indication whether a turbine 0.25 miles away on land in the same ownership would negate the installation of a heat pump or not under pd.
I’d be surprised if it wasn’t a noise consideration. Neither wind turbines nor heat pumps are intrinsically noisy but both have come under attack in the past for the potential to be so in certain circumstances. In that light, it would be a pretty bold stance to allow two potentially noise-creating items to be installed close by one another without requiring some sort of sanity check that they won’t compound each other’s problem.
This is, of course, only permitted development. The fact remains that heat pumps and wind turbines can still be installed close to each other with planning permission.
All my own supposition, of course…
Rob of York
Sound level calculation for air source heat pump permitted development noise compliance using MCS 020 a) against the fixed 37 dB(A) limit.
See this useful online calculator:
https://tradecalculator.co.uk/renewables/heat-pump-noise-calculator/
For example, my two Daikin A2A outdoor units (sited side-by-side) have a maximum sound power of 60dB each, they are on the ground with a wall behind them (Q4).
There are two assessment positions that need to be considered: (i) 1m perpendicular in front of the neighbour’s back door, which is 9m away, and (ii) 1m perpendicular in front of the neighbour’s nearest first floor window, which is 14m away. Position (i) is completely obscured by a solid fence (<18mm thick) and position (ii) is in full view. Due to the sound damping effect of the fence (-5dB) both positions need to be checked.
The calculated noise levels are (i) 34dB and (ii) 35.1dB, so both are within the 37dB limit.
Note, if the fence wasn’t there, then the noise level would be 39dB at position (i) and would not be compliant. Having a single heat pump and no fence, the maximum noise level would be 35.9dB, which would again be compliant.
The calculator is useful for checking compliance in simple situations i.e. one or two heat pumps. If you scroll down on the webpage, it explains the assumptions of the model and the formula that MCS 020 a) uses.
In practice as a courtesy to my neighbours, and for maximum efficiency, I only ever run the heat pumps in eco mode which drops the maximum sound level substantially by reducing the maximum compressor and fan speeds. That does not however make any difference to the compliance calculation required.
The idealist in me says pioneers in this space should be rewarded!
17