RE: Do setbacks save energy without compromising comfort?

Thank you! I think the fall takes as long as it does because as the LWT/RWT fall, and they approach room temp, the delta t between them and the room t...

2 years ago
Reply
RE: Do setbacks save energy without compromising comfort?

The last 24 hours data, showing another setback and recovery, with minimal extra energy in during the recovery boost. This time the actual room temp f...

2 years ago
Reply
RE: Grant Aerona Setback

@allyfish - I posted my first overnight setback plus recovery boost data earlier today and it shows pretty convincingly that in my house in last night...

2 years ago
Reply
RE: Grant Aerona Setback

That's fine, it is just it would have been interesting to see the data if it was available. Given my modbus setup, I should now be able to get minute ...

2 years ago
Reply
RE: Grant Aerona Setback

I think this is an interesting question. In both cases, the intention is to lower output, though the reasons are slightly - but are they materially? -...

2 years ago
Reply
RE: Grant Aerona Setback

I've just read the Grant link above ("Blog | How to control your heat pump") and it seems the terminology is somewhat confused as to what a setback is...

2 years ago
Reply
RE: Grant Aerona Setback

Isn't this possibly over-complicating things, as I pointed out earlier, using a room stat setback acts in effect as a timer (at least it does in my ho...

2 years ago
Reply
RE: Grant Aerona Setback

@derek-m I didn't quote you (no quotation marks, and my wording is 'appear to be firmly of the opinion', not X said Y), I paraphrased you, or you mi...

2 years ago
Reply
RE: Grant Aerona Setback

Just to add an observation on this: I did in fact manage to do this, in the cold snap last December, by using the room stat: normal target IAT is 19 d...

2 years ago
Reply
RE: Heat pumps and on/off working - starting to quantify it

That sounds very plausible, except for the fact the LWT rise appears to start just before the RWT rise, see at around 0703h. The four phase pattern is...

2 years ago
Reply
RE: Heat pumps and on/off working - starting to quantify it

Here are the minute by minute energy values alongside the minute by minute temp values I posted earlier. Note they are Wh, not kWh, and, as a sanity c...

2 years ago