Real world running cost estimate for 20KW ASHP
Posted by: @thebarnYes, it is very confusing to have been quoted 11kw, (16kw when I looked into it a few years ago), then 18kw and then 20kw! Go in too low and be cold and too high and be wasting electricity and money.
The ideal is to go for for something that just exceeds your heat loss at design temp (-2 or thereabouts depending on where you are) when running at those outside air temperatures. Any more, and you will get more cycling at warmer weather, as the heat pump can't reduce it's output below a certain level, and less and you will be likely to feel cold when it is very cold outside. That is what I ended up with: nominal 14kW unit, but only coughs up a little over 11kW at around zero outside, estimated heat loss 12.3 kW, result is actual indoor air temp falls a bit below desired indoor air temp during cold weather.
As others have said, heat loss calculations are not an exact science, and in some cases I suspect involve the use of random numbers. But a tolerably thorough assessment should usually give you a reasonable ball park figure. That said, there has been a lot of debate in other threads about empirical measurements (albeit rather crude, because of the surfeit of variables involved), and how these often do not agree with the heat loss calculator estimates.
Midea 14kW (for now...) ASHP heating both building and DHW
- 22 Forums
- 2,097 Topics
- 46.2 K Posts
- 43 Online
- 3,385 Members
Join Us!
Latest Posts
-
RE: Weather compensated secondary circuits with Biomass
@sune thanks for the LK link, looks like a possible opt...
By AndyCoo , 9 hours ago
-
RE: Heat pump solutions and/or installer recommendations for France
No idea, but Google-Fu leads me to Bon chan...
By Scalextrix , 11 hours ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 23 hours ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 1 day ago
-
RE: Mitsubishi cycling while on chilled water output
I absolutely wouldn't remove the buffer altogether, I'd...
By JamesPa , 2 days ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 2 days ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 3 days ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 4 days ago
-
RE: Say hello and introduce yourself
Yes please do Suggesting a loss in the region...
By JamesPa , 4 days ago
-
As I have reported elsewhere we turned on the cooling o...
By downfield , 5 days ago
-
-
@el3b Hi, sorry to hear that, it is advisable to instal...
By ASHP-BOBBA , 5 days ago