Toodles
(@toodles)
Illustrious Member Contributor
Joined: 3 years ago
Posts: 2096
 

@burtis I’m still waiting for my Octopus Mini (18 months or so and counting) and have to rely on the Enphase and Tesla apps but can’t help feeling the mini (which is, after all, what I will be metered by) might give me a better indication. As best I can ascertain, my Daikin performs in a similar ballpark wattage range to your Midea. Regards, Toodles.


Toodles, he heats his home with cold draughts and cooks his food with magnets.


   
👍
1
ReplyQuote
 RobS
(@robs)
Estimable Member Member
Joined: 11 months ago
Posts: 55
 

@johnmo

The effect of cycling is very different with different heating systems too. If modulation was not an important factor heat pumps would still use fixed speed compressors. All modern ASHPs use modulating inverter compressors, no matter how good their control strategy, so it seems a little foolish to dismiss modulation range from consideration. 



   
ReplyQuote
 NJT
(@njt)
Estimable Member Member
Joined: 1 year ago
Posts: 57
 

@toodles 

Just register again, I waited ages for my mini so registered again and got it about a week later. 

My 8kw Daikin bottomed out at about 280w according to my newly installed Shelly energy meter clamped around the heat pump feed cable.



   
ReplyQuote
Toodles
(@toodles)
Illustrious Member Contributor
Joined: 3 years ago
Posts: 2096
 

@njt Ooh! Thank you, for both pieces of information. 😊 Toodles.


Toodles, he heats his home with cold draughts and cooks his food with magnets.


   
ReplyQuote
 RobS
(@robs)
Estimable Member Member
Joined: 11 months ago
Posts: 55
 

Posted by: @jamespa

That's an interesting development, are mitsubishi the first to do this?

 

As far as I know yes. 

 



   
ReplyQuote
SUNandAIR
(@sunandair)
Noble Member Member
Joined: 3 years ago
Posts: 501
 

@robs, and other contributors 

I have been working on our minimum operating output using these charts for about a year now. There is no notes on how to interpret this chart especially where  the chart states “Capacity”. 
(example if I have a bucket which has a capacity of 2 gallons there is nothing stopping me from just putting a pint in it but the capacity is still 2 gallons)

I might be wrong but this thread seems to be interpreting/reading capacity as minimum output whereas I’ve been reading this word as the top output at a given  compressor setting with some modulation below that capacity. 
So I’m interested to hear how to interpret this chart. 

Also, while Capacity is one side of the question, the other issue is maintaining a sustained, modulated output. This second part of sustained operation does not appear to be answered in these charts. Especially at +10c ambients.

While we have found flow temperatures which offer  reduced cycling at these warmer ambients, it has invariably been at higher outputs than the chart implies. Ie typically 300 to 500watts higher output than the chart stated capacity. 

Has anyone got a definitive way to interpret this chart?

HP Output:Ambient

incidentally @robs this chart is for the ecodan R32 model 8.5. It was rumoured that this model also had a split compressor.


This post was modified 11 months ago 2 times by SUNandAIR

   
ReplyQuote



 RobS
(@robs)
Estimable Member Member
Joined: 11 months ago
Posts: 55
 

Posted by: @sunandair

@robs, and other contributors 

I have been working on our minimum operating output using these charts for about a year now. There is no notes on how to interpret this chart especially where  the chart states “Capacity”. 
(example if I have a bucket which has a capacity of 2 gallons there is nothing stopping me from just putting a pint in it but the capacity is still 2 gallons)

I might be wrong but this thread seems to be interpreting/reading capacity as minimum output whereas I’ve been reading this word as the top output at a given  compressor setting with some modulation below that capacity. 
So I’m interested to hear how to interpret this chart. 

I'm pretty sure it just means output, using the word capacity in this way isn't unusual in Japanese documents (and if something has a capacity then it will have a minimum and maximum capacity). So max is maximum output (from max compressor speed) at those conditions and min is minimum output (from min compressor speed) at those conditions. The capacity-ambient temp graphs on page 109 show this quite well, your ASHP at 35C flow temp and 10C ambient has a range of about 3kW to 10.6kW (min compressor speed to max compressor speed). 

Posted by: @sunandair

Also, while Capacity is one side of the question, the other issue is maintaining a sustained, modulated output. This second part of sustained operation does not appear to be answered in these charts. Especially at +10c ambients.

While we have found flow temperatures which offer  reduced cycling at these warmer ambients, it has invariably been at higher outputs than the chart implies. Ie typically 300 to 500watts higher output than the chart stated capacity. 

If the heat pump can achieve it, and the document suggests it can, then that would suggest that the rest of the heating system may be the cause. I believe the need for a higher flow temperature at high ambient temperatures implies that the emitters can't shed the heat they are being fed fast enough (due to the emitter to room deltaT being so low). And as a result the return temperature rises to a level that causes the heat pump to shut off, hence you get cycling. Bigger emitters (radiators or UFH) make it easier to shed heat even with low emitter-room deltaT values, so maybe with larger emitters a stable low output is possible. 

Posted by: @sunandair

incidentally @robs this chart is for the ecodan R32 model 8.5. It was rumoured that this model also had a split compressor.

The document I linked to has the details of the compressors in the heat pumps, the PUZ-WM85 has a single SVB220FEGMC-L1 model compressor (see page 9 and the refrigerant system diagram on page 77).

 

 

 

 

 

 



   
ReplyQuote
SUNandAIR
(@sunandair)
Noble Member Member
Joined: 3 years ago
Posts: 501
 

Posted by: @sunandair

@robs, and other contributors 

I have been working on our minimum operating output using these charts for about a year now. There is no notes on how to interpret this chart especially where  the chart states “Capacity”. 
(example if I have a bucket which has a capacity of 2 gallons there is nothing stopping me from just putting a pint in it but the capacity is still 2 gallons)

I might be wrong but this thread seems to be interpreting/reading capacity as minimum output whereas I’ve been reading this word as the top output at a given  compressor setting with some modulation below that capacity. 
So I’m interested to hear how to interpret this chart. 

point1. I'm pretty sure it just means output, using the word capacity in this way isn't unusual in Japanese documents (and if something has a capacity then it will have a minimum and maximum capacity). So max is maximum output (from max compressor speed) at those conditions and min is minimum output (from min compressor speed) at those conditions. The capacity-ambient temp graphs on page 109 show this quite well, your ASHP at 35C flow temp and 10C ambient has a range of about 3kW to 10.6kW (min compressor speed to max compressor speed). 

Posted by: @sunandair

Also, while Capacity is one side of the question, the other issue is maintaining a sustained, modulated output. This second part of sustained operation does not appear to be answered in these charts. Especially at +10c ambients.

While we have found flow temperatures which offer  reduced cycling at these warmer ambients, it has invariably been at higher outputs than the chart implies. Ie typically 300 to 500watts higher output than the chart stated capacity. 

point2. If the heat pump can achieve it, and the document suggests it can, then that would suggest that the rest of the heating system may be the cause. I believe the need for a higher flow temperature at high ambient temperatures implies that the emitters can't shed the heat they are being fed fast enough (due to the emitter to room deltaT being so low). And as a result the return temperature rises to a level that causes the heat pump to shut off, hence you get cycling. Bigger emitters (radiators or UFH) make it easier to shed heat even with low emitter-room deltaT values, so maybe with larger emitters a stable low output is possible. 

Posted by: @sunandair

incidentally @robs this chart is for the ecodan R32 model 8.5. It was rumoured that this model also had a split compressor.

Point3. The document I linked to has the details of the compressors in the heat pumps, the PUZ-WM85 has a single SVB220FEGMC-L1 model compressor (see page 9 and the refrigerant system diagram on page 77).

  

Hi @robs 

I thought I'd post the pages in the data book you referred to:

Point1.

Capacity to ambient temp graph ; page105 the 4 lines on this graph show Max output, Partload1 output, Partload2 output and Min output. at a specific water outlet temperature. the discussion relates to the lowest output and how it changes depending on the outdoor ambient temperature. 

Regarding our installation it is stable operating in 10 to 12c ambient at an outlet temp of 35c. It operates with 25 minutes on-cycles and roughly 5 minutes off-time. It modulates when on between DT3 to DT5.

HP min;maxoutput;ambient graph

The issues become apparent when operating at 30c outlet temperature, when our weather comp curve was set that low. It was clear that excessive cycling became an issue.

Point2.

Of course you are right; The sizing of our emitters (total capacity) appear to be restricting the heat loss into the living space at these very low demand levels. This must be a challenge for many Rads-only installations.

I wonder how frequently installations get designed with maximum heat demand criteria when it is -3 outside and never designed for minimum operating capacity of the heat pump at the moderate weather days?

  We have a total rad capacity of 21kw (at DT50+room temp21) but by the time that is calculated down to a flow temp 30c in a room temp21 the heat loss is miniscule.  Our TRVs are now fully open. So we are left with a min WC setting of 35c which gives us a CoP of somewhere between 3.9 and 4.2, which is ok but we could squeeze a bit more efficiency out.

Point 3.

It was interesting to see the diagram on the new twin compressor on the latest R190 model PUZ-WZ80VAA. Complete with its twin plate heat exchangers.

4B7B65B3 E9EC 465B BA27 57FA72EF7C54

 

 


This post was modified 11 months ago 3 times by SUNandAIR
This post was modified 11 months ago by Mars

   
ReplyQuote
 RobS
(@robs)
Estimable Member Member
Joined: 11 months ago
Posts: 55
 

Posted by: @sunandair

Regarding our installation it is stable operating in 10 to 12c ambient at an outlet temp of 35c. It operates with 25 minutes on-cycles and roughly 5 minutes off-time. It modulates when on between DT3 to DT5.

HP min;maxoutput;ambient graph

The issues become apparent when operating at 30c outlet temperature, when our weather comp curve was set that low. It was clear that excessive cycling became an issue.

 

You have clearly found your system's sweet spot! 

Posted by: @sunandair

Point2.

Of course you are right; The sizing of our emitters (total capacity) appear to be restricting the heat loss into the living space at these very low demand levels. This must be a challenge for many Rads-only installations.

 

Yes, radiator based systems are likely to be limited in stable low flow temperatures. But larger radiators should allow lower stable flow temperatures. 

Posted by: @sunandair

I wonder how frequently installations get designed with maximum heat demand criteria when it is -3 outside and never designed for minimum operating capacity of the heat pump at the moderate weather days?

 

Probably the vast majority, even though they will run at these low outputs most of the time (nicely described by:  https://protonsforbreakfast.wordpress.com/2023/12/17/variability-of-heating-demand-throughout-a-year/).  

Posted by: @sunandair

  We have a total rad capacity of 21kw (at DT50+room temp21) but by the time that is calculated down to a flow temp 30c in a room temp21 the heat loss is miniscule.  Our TRVs are now fully open. So we are left with a min WC setting of 35c which gives us a CoP of somewhere between 3.9 and 4.2, which is ok but we could squeeze a bit more efficiency out.

 

What was the total output capacity of your radiators at a flow temperature of 30C? Is it less than the minimum output of your heat pump at 30C flow temperature? 

Posted by: @sunandair

Point 3.

It was interesting to see the diagram on the new twin compressor on the latest R190 model PUZ-WZ80VAA. Complete with its twin plate heat exchangers.

4B7B65B3 E9EC 465B BA27 57FA72EF7C54

 

Indeed, but I think the dotted line around the plate heat exchangers indicates that these are a single item. There is a similar dotted line around the fans in the schematic but the unit only contains one fan. 

 

 


This post was modified 11 months ago by RobS

   
👍
2
ReplyQuote
(@lucia)
Prominent Member Member
Joined: 1 year ago
Posts: 317
 

@tomasmcguiness

Heating needs to go on when it's 12 or less outside. My gas boiler can keep the house warm with a 30 ish flow when it's that temp outside. Might work with an even lower flow temp, but due to the boiler being stupidly oversized, it would just cycle like crazy.

 

This is the Daikin monoblocs - 4/8/6 kw

This is the link for the Daikin EU data portal. If you choose a pump size and tank (mine is Altherma EDLA 6kw & 180litre tank) you can then play with temperatures, outputs, flow temps etc., In other words a capacity chart that is interactive. It's quite useful. Hope it helps. 



   
ReplyQuote
SUNandAIR
(@sunandair)
Noble Member Member
Joined: 3 years ago
Posts: 501
 

Posted by: @robs

 

 

Posted by: @sunandair

  We have a total rad capacity of 21kw (at DT50+room temp21) but by the time that is calculated down to a flow temp 30c in a room temp21 the heat loss is miniscule.  Our TRVs are now fully open. So we are left with a min WC setting of 35c which gives us a CoP of somewhere between 3.9 and 4.2, which is ok but we could squeeze a bit more efficiency out.

 

 

 

What was the total output capacity of your radiators at a flow temperature of 30C? Is it less than the minimum output of your heat pump at 30C flow temperature? 

it took me a while to learn how and to work out output correction factors for 30c and 35c flow temperatures. Here’s my best attempt as written back then…

B54AA00D 9F50 4ECC B330 4837AD438C96

At a 21kw combined rad load 

30c LWT = 1.785kw total output 

35c LWT = 3.47kw  total output

i also calculated outputs when all the TRVs were closed as can be seen.

We had various discussions on correct ways of calculating radiator outputs on this forum over the past 18 months. So I hope I can now do it justice and try and describe the method I used for working out the DT and correction factor.

see below

3F459F1C F9B1 4E67 85D5 73AF27B657DD

The first issue I recall, was to notice that the manufacturers correction charts do not go down low enough or fine enough to take account of 5c circuit DT (temp drop) and 30c LWT. 
See correction chart. I also hope my calc method looks about right

Output correction factors

So after a bit of trial and error I was left thinking the 30c outlet temperature at under 2 kw output it was the reason for the cycling we encountered. 



   
ReplyQuote
SUNandAIR
(@sunandair)
Noble Member Member
Joined: 3 years ago
Posts: 501
 

Posted by: @robs

Probably the vast majority, even though they will run at these low outputs most of the time (nicely described by: 

 

PROTONSFORBREAKFAST.WORDPRESS.COM "https://protonsforbreakfast.wordpress.com/2023/12/17/variability-of-heating-demand-throughout-a-year/)."
Variability of heating demand throughout a year. | Protons for Breakfast
Friends, as I drift off to sleep at night, I often reflect on the subtle wonder of heat pumps, and last night I imagined this article in my head. However writing the article has proved more difficult than I had envisaged in my sleepy reverie. There are lots of technical details, so in case you…

 

 

Interesting article… thanks for posting @robs.

So to summarise:- Of the 365 days of the year our heat pumps will try to operate for 160 days at less than 20% capacity. (If they can cope with the modulation, that is.)

3D298089 CCBD 4042 B14A 9FB5FB139DE8

great info.

would be interesting to see the split over autumn, winter and spring. 


This post was modified 11 months ago by SUNandAIR

   
ReplyQuote



Page 2 / 3
Share:

Join Us!

Latest Posts

Members Online

Click to access the login or register cheese
x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
ShieldPRO