I remember thats where you started (conservatism in heat loss). What do you actually know in total about heat loss. Do you have any consumption fig...
Once its running at lowest possible FT you might be able to reassess the operating mode when its mild. Depending on your house, when its mild (which ...
Fair enough. Obviously you understand that you will take a running cost hit but all designs are a trade off. 45 is often a good compromise for radia...
I still am not sure you get the point of volumiser tanks. They add water volume to the system. They don't need power. Grant and others take the op...
Are you saying your design flow temperature (at the lowest oat) for the ashp system is 55C? Fans on fancoils do run constantly, but with a decent...
I'm sorry but I don't understand your maths. If you need 2.4-3kW output then you will need a radiator rated for about 6kW at 50C DT. That's a very bi...
I think that's very likely. Thus if you set all external controls to be permanently on you should be able to optimise the wc curve to the lowest poss...
Please post back on how you get on. You need to give some thought to those ufh loops, they can't be allowed to suck energy out during dhw cycle. Re...
They will run without a fan but output is then less than a radiator of same size. I thought you were struggling to fit a passive radiator in hence w...
Could a fan coil be suitable. I had a similar problem which was solved with a fan coil.
Ok that's clearer. It's a pity about the manifold pumps, they effectively stop the ashp having the control it needs to make sure everything works pr...
Thanks, thats helpful. There seems to be a circular path around the upper volumiser, is this correct (it could be, perhaps the upper heat pump is the...
- 26 Forums
- 2,112 Topics
- 46.4 K Posts
- 17 Online
- 3,408 Members
Join Us!
Latest Posts
-
RE: Buffers, hot water and cooling
It is very unlikely to break, but of course it just mig...
By JamesPa , 11 hours ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 11 hours ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 15 hours ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 16 hours ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 22 hours ago
-
RE: Wood burner with ASHP - direct air?
@sune is ideal to answer this, but I think he's on vaca...
By Mars , 2 days ago
-
RE: Say hello and introduce yourself
Hi @topher - you might be interested to see this very r...
By Transparent , 2 days ago
-
RE: No-code, plug-and-play monitoring for your heat pump
We've got a svenar heat pump controller en route and lo...
By benson , 3 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 3 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 3 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 4 days ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 4 days ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 4 days ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 4 days ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 4 days ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 6 days ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 7 days ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 1 week ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 1 week ago
-
RE: Cleaning up after gas meter removed
@agentgeorge Likewise in the loft space; we have 300mm ...
By Toodles , 1 week ago