It bodes the question "if 600mm high radiators will not fit, why were they specified"? Will 400mm high radiators fit?
Unless you instigated the changes, I would certainly question why the originally specified radiators were changed to the ones actually installed.
@crimson According to the heat loss calculations the design called for two K2 600mm x 1400mm radiators in both Living Room 1 and Living Room 2. Each...
As I have often told young Engineers, "If all else fails, read the instructions".
@crimson Please feel free to DM if you wish.
@crimson The other important aspect to confirm is that the total capacity of the heat emitters is capable of emitting 7.86kW of thermal energy with ...
From the information just provided, I suspect a 10kW heat pump would have been more than adequate. As @heacol has indicated it will be impossible to...
I would suggest that you start by reducing the frequency of cycling, by trying to balance the flow rate through the LLH. I suspect it will be necessar...
Try tapping the side of the valve and/or pulling the stem up.
@crimson The valve stem should be up to open and down to close. For living areas it may be best to remove the actuator and leave the valve fully ope...
@crimson Try removing the TRV heads and check that the valve stems move freely, and by approximately the same amount of travel. With regard to the...
If you read back in the thread I did suggest changing the LLH into a small volumiser rather than fully removing, but maybe something to consider once ...
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 33 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Powerwall 3 or Myenergi or something else?
Many of those tariffs are simple time of use tariffs, w...
By Temperature_Gradient , 4 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Yes thats the whole point of the flexis as regards tran...
By JamesPa , 4 hours ago
-
So far as I can tell designing for DT5, which is 'the n...
By JamesPa , 4 hours ago
-
Mitsu PAR-WT60R Wireless Controller - options
I hope I have satisfactorily installed the above wirele...
By DavidAlgarve , 6 hours ago
-
WC curve best discovered by experiment anyway as any lo...
By JamesPa , 11 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
@editor your engineer's attitude is truly horrifying. ...
By GrahamF , 1 day ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 1 day ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 1 day ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 1 day ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 2 days ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 2 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 2 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 2 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 2 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 3 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 3 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 3 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 5 days ago