                        <title>RE: UFH downstairs and radiators upstairs balancing question</title>
                        <link>https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-52658</link>
                        <pubDate>Sun, 16 Nov 2025 17:52:40 +0000</pubDate>
                        <description><![CDATA[Yes thats true, but that cant happen unless the room temperature is 28C!
Its best in most circumstances to think of DT as a consequence of other things, not something you control.  The emis...]]></description>
<p>Can you explain the DT comment a bit more.  If the temp is coming in at say 28 degrees to the rads and leaving at 28, then the energy transfer must be zero.</p>
<p>Yes thats true, but that cant happen unless the room temperature is 28C!</p>
<p>Its best in most circumstances to think of DT as a <em>consequence</em> of other things, not something you control.  The emissions from a radiator are determined by its average surface temperature in relation to the room temperature.  The first of these is principally determined by the flow temperature.  So a radiator of a given area with an average surface temperature of 28C and a room temperature of 20C will emit a certain amount of heat.  This, together with the <em>flow rate</em> will <em>determine</em> the DT.  There is a bit of circularity here because a higher DT means a lower <em>average</em> surface temperature for any given <em>flow</em> temperature, so to do the calculation you have to iterate a few times (nature of course does the iteration for you).  Thats why a lower DT (which, if all else stays the same, can be achieved by increasing the flow rate) will actually result in a <em>higher</em> emission from the radiator in any given set of circumstances.</p>
<p>To complicate matters further some heat pumps have a DT control loop.  This secondary control loop modulates the water pump to target a specific system level DT.  However the DT variations as described above will still occur at the level of the individual emitters, so balancing for room temperature is still effective.</p>
<p>The rads are sized a bit small for the flow temp the UFH needs, so I need a little more temp.  I've closed 2-3 of the UFH heating loops as suggested but its not cold enough really to see it its helped. </p>
<p>Yes.  So you can:</p>
<li>reduce the DT across the rads by increasing the flow rate through them.  This increases their average surface temperature for any given FT.  The effect is limited though - if you start with a DT of 5 then the best you can get (at flow rate = infinity) is a DT of 0, 2.5C higher average temp</li>
<li>increase the DT across the UFH by reducing the flow rate through it.  This reduces the average surface temperature for any given FT.  The effect is essentially unlimited, with zero flow rate (ie closing loops), the average surface temp falls to the room/slab temp so there are no heat is emitted</li>
<li>increase the radiator area</li>
<li>reduce the UFH area (which you are doing by closing loops)</li>
<p>One thing to be careful with if you close loops completely is that it reduces the system volume - ie the volume of water in the active sysem.  This will reduce the 'on' period when the heat pump is cycling, which reduces efficiency.  Its probably better to turn them all down very low than switch some off completely, but of course that depends on practicality.  In extremis if you reduce the system volume too far you can get into a problem with defrost, where there isn't enough hot water in the system to melt the ice that forms on the compressor.  This can cause a death spiral.  Heat pump manufacturers specify a minimum system volume for this purpose (in reality you want a larger system volume so that cycling is more efficient).</p>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-52658</guid>
                        <link>https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-52654</link>
                        <pubDate>Sun, 16 Nov 2025 17:30:31 +0000</pubDate>
Hi, thanks for getting back to me. 
this week will be more interesting as its getting colder here is Sheffield.
Can you explain the DT comment a bit more.  If the temp is coming...]]></description>
<p>Hi, thanks for getting back to me. </p>
<p>this week will be more interesting as its getting colder here is Sheffield.</p>
<p>Can you explain the DT comment a bit more.  If the temp is coming in at say 28 degrees to the rads and leaving at 28, then the energy transfer must be zero. So if the DT is 1, then is it not that only a bit of heat is transferred to the room at any given flow rate.  The rads are sized a bit small for the flow temp the UFH needs, so I need a little more temp.  I've closed 2-3 of the UFH heating loops as suggested but its not cold enough really to see it its helped. </p>
<p>I'll keep you updated </p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/">Thermostats, Volumisers, Buffer Tanks, TRVs, Pumps, Piping, Valves, Radiators &amp; Controls</category>                        <dc:creator>davidnolan22</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-52654</guid>
                        <link>https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-52573</link>
                        <pubDate>Sat, 15 Nov 2025 09:09:48 +0000</pubDate>
                        <description><![CDATA[I wonder what the logic of this was, that will be the cooler of the two whereas I would have thought you want the rad circuit on the warmer.
Never mind it shouldn&#039;t matter that much, how is...]]></description>
<p><a style="color: #993366" title="Toodles" href="https://renewableheatinghub.co.uk/participant/toodles/">@toodles</a> </p>
<p>sorry, my bad. Its a 6 port LLH.  of the 2 higher ones, the rad circuit is the lower of those 2. </p>
<p>I wonder what the logic of this was, that will be the cooler of the two whereas I would have thought you want the rad circuit on the warmer.</p>
<p>Never mind it shouldn't matter that much, how is the balancing going, are you getting closer?  From what I recall your problem is that its too cool upstairs where you have radiators, and too warm downstairs, where you have UFH.  More flow through the radiators and less flow through the UFH should sort this unless the radiators are too far undersized in the first place; has adjusting the relative flows made any difference? </p>
<p>Say my flow/return is 30/25, the DT of the rads is only 1, and the UFH slightly over 5.  I’ve spoken to my installer about getting more DT off the rads.</p>
<p><em>Dont! </em> The adjustment you need to make <em>will</em> reduce the DT through the rads and <em>will</em> increase the DT through the UFH.  Thats the mechanism by which the UFH emits less (because the <em>average</em> temperature is reduced) and the rads emit more (because their <em>average</em> temperature is increased), which is what you are trying to achieve.  DT is much misunderstood!</p>
<p>Just to be clear the way the balancing works is this: </p>
<p>The loss from an emitter (to the room) is determined by the <em>average</em> temperature of the emitter. </p>
<p>If you <em>increase</em> the flow through an emitter then the average emitter temperature will <i>increase</i> because the DT across the emitter <em>decreases </em>as a result of the increased flow.  This will <em>increase</em> the loss from the emitter to the room (which will cause the DT to increase a bit, so if you are calculating it you need to iterate, but the real world does this for you). </p>
<p>Conversely</p>
<p>If you <i>decrease </i>the flow through an emitter then the average emitter temperature will <em>decrease </em>because the DT across the emitter <em>increases </em>as a result of the reduced flow.  This will <em>decrease</em> the loss from the emitter to the room.</p>
<p>Thus, given what you have told us, Im expecting your system to be in balance (for temperature) when the DT across the radiators is relatively low and the DT across the UFH relatively high.</p>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-52573</guid>
                        <link>https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-52055</link>
                        <pubDate>Thu, 06 Nov 2025 10:52:29 +0000</pubDate>
                        <description><![CDATA[@toodles 
sorry, my bad. Its a 6 port LLH.  of the 2 higher ones, the rad circuit is the lower of those 2.]]></description>
                        <content:encoded><![CDATA[<p>@toodles </p>
<p>sorry, my bad. Its a 6 port LLH.  of the 2 higher ones, the rad circuit is the lower of those 2. </p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-52055</guid>
                        <link>https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-52053</link>
                        <pubDate>Thu, 06 Nov 2025 09:34:50 +0000</pubDate>
                        <description><![CDATA[@davidnolan22 If I understand you correctly, you are saying that the output to the  radiators is being fed from the lower port on the LLH.
Normal practice is that the top port opposite the ...]]></description>
                        <content:encoded><![CDATA[<p>@davidnolan22 If I understand you correctly, you are saying that the output to the  radiators is being fed from the lower port on the LLH.</p>
<p>Normal practice is that the top port opposite the flow from the heat pump would feed the heating circuit. The lower ports are for the return from the end of the heating pipework into the LLH and the port on the opposite side feeds back to the heat pump (return). This means that the flow from the heat pump enters one side at the top of the LLH and the flow out to the radiators is on the opposite side, also at the top; the return enters the LLH on the same side as the port that flows to the radiators but at the bottom, and the fourth port at the bottom is the return to the heat pump. This is the normal route to reduce distortion (mixing) to the minimum; at this point it is advantageous to minimise any difference in temperature across the ports by controlling the pump’s flow rate to further reduce didtortion.  Regards, Toodles.</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/">Thermostats, Volumisers, Buffer Tanks, TRVs, Pumps, Piping, Valves, Radiators &amp; Controls</category>                        <dc:creator>Toodles</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-52053</guid>
                        <link>https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-52050</link>
                        <pubDate>Thu, 06 Nov 2025 09:16:26 +0000</pubDate>
                        <description><![CDATA[@ashp-bobba 
Hi, thanks for reply. 
I&#039;ve started to play, its still very warm outside so need it to get cooler, but I&#039;ve closed 2 loops out of 9 where we are most overpowered with the UFH,...]]></description>
                        <content:encoded><![CDATA[<p>@ashp-bobba </p>
<p>Hi, thanks for reply. </p>
<p>I've started to play, its still very warm outside so need it to get cooler, but I've closed 2 loops out of 9 where we are most overpowered with the UFH, This did increase the flow temp to the rads by a degree (I was getting a small amount of blending at the LLH, the rads is the lower out from the header so got blended by a degree). the rads are now seeing the primary flow temp. So I assume i've just nudged the secondary flow (hard to measure) to slightly below the primary flow (31 l/min) </p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-52050</guid>
                        <link>https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-51985</link>
                        <pubDate>Wed, 05 Nov 2025 09:30:26 +0000</pubDate>
                        <description><![CDATA[Isn&#039;t this a great example of KISS!]]></description>
<p><a title="davidnolan22" href="https://renewableheatinghub.co.uk/participant/davidnolan22/">@davidnolan22</a> Hi, ok first of all it very hard to truly balance duel UFH circuits and rads when they have a shunt, Splan valve and a manifold pumps, usually we would want an open loop system to have one pump controlled by the ASHP supplying the whole balanced system. </p>
<p>Isn't this a great example of KISS!</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-51985</guid>
                        <link>https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-51963</link>
                        <pubDate>Tue, 04 Nov 2025 20:47:45 +0000</pubDate>
                        <description><![CDATA[@davidnolan22 Hi, ok first of all it very hard to truly balance duel UFH circuits and rads when they have a shunt, Splan valve and a manifold pumps, usually we would want an open loop system...]]></description>
                        <content:encoded><![CDATA[<p>@davidnolan22 Hi, ok first of all it very hard to truly balance duel UFH circuits and rads when they have a shunt, Splan valve and a manifold pumps, usually we would want an open loop system to have one pump controlled by the ASHP supplying the whole balanced system. one pump inline with another is a different challenge. Also its unlikely unless your radiator is a K3 and very large it will heat a medium sized room of say 4x4m2 at 30/25. </p>
<p>Brands Like Ecodan and many others have duel zone control and can modulate the flow slightly to different circuits but you would need to run the system hotter and unfortunately blend back down at the UFH manifolds to control the flow temperature which then can also cause a higher return on the flow and short cycle the ASHP. </p>
<p>You may find that if the UFH loops are over designed for a flow rate of 40℃ and the rads are under designed for a flow rate of 30℃, so if you choose 30 the rads are short and if you choose 40 the UFH is over.  </p>
<p>Some tricks that may work. </p>
<p>If you have multiple loops on the UFH example: lets say you have 4 loops in the dining area spread out like loops 123and 4 in order left to right you could close down loops 2 and 4 or 1 and 3, this would half the power of the UFH but keep it kind of spread out, if it is slightly over designed, this would then let you run the system at 40/35 and add more power to the rads.</p>
<p>Just make a note by taking pictures or videos of where settings are before adjusting anything so you can always put it back where it was.</p>
<p>Any heating system has little chance of working correctly if it is not balanced.</p>
						                            <category domain="https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/">Thermostats, Volumisers, Buffer Tanks, TRVs, Pumps, Piping, Valves, Radiators &amp; Controls</category>                        <dc:creator>ASHP-BOBBA</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-51963</guid>
                        <link>https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-51889</link>
                        <pubDate>Tue, 04 Nov 2025 07:43:29 +0000</pubDate>
Can I pick you brain about mine
260m2 house. 
2 x UFH manifold, one 150m2 manifold in new extension, one 50m2 in old ground floor. 110m2 rad run for bedrooms above....]]></description>
<div>
<p><span>Can I pick you brain about mine</span></p>
</div>
<div>
<p><span>260m2 house. </span></p>
</div>
<div>
<p><span>2 x UFH manifold, one 150m2 manifold in new extension, one 50m2 in old ground floor. 110m2 rad run for bedrooms above. </span></p>
</div>
<div>
<p><span>Ive a LLH, 2 primary circuit pumps, one pump off the header for rads, one shunt pump to the manifolds and one pump on each manifold. </span></p>
</div>
<div>
<p><span>Its now running all open with only one stat, no UFH stat control.  The design has not been great and its been a struggle, this is my second winter.  The UFH can heat those areas at very low flow temps, rarely above 30 degrees unless its close to zero or below outside. </span></p>
</div>
<div>
<p><span>The temp gap to rooms above can get quite wide, sometimes a bit too wide. </span></p>
</div>
<div>
<p><span>Say my flow/return is 30/25, the DT of the rads is only 1, and the UFH slightly over 5.  I’ve spoken to my installer about getting more DT off the rads. The advice has been in increase the speed of water through the UFH, turn all pumps to max. My UFH is a mix mainly 12mm low profile pipes and some 16mm traditional.  Putting the pumps to max does nothing unless I also open the flows the UFH loops, but if I do that, parts of the house that only need 20% of the heat loss can consume much of the flow of the primary and get even warmer.  Am I best to start to restrict flows into the house that get too much heat. My installer warmed me not to do this the water would be flowing to slowly in that part and the return would be too cold</span></p>
</div>
<div>
<p><span>Any before you ask, no they have not balanced it for me, they have offered to come back at some point.  </span></p>
</div>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/paged/2/#post-51889</guid>
                        <link>https://renewableheatinghub.co.uk/forums/thermostats-trvs-pumps-valves/downstairs-to-upstairs-balance-question/#post-51887</link>
                        <pubDate>Tue, 04 Nov 2025 07:13:08 +0000</pubDate>
                        <description><![CDATA[@walnut-tree-cottage So you have no stats on any of the UFH and its fully open loop? if this is the case you need to make sure the Rads are DT5 and the UFH is DT5 and get them as balanced as...]]></description>
                        <content:encoded><![CDATA[<p>@walnut-tree-cottage So you have no stats on any of the UFH and its fully open loop? if this is the case you need to make sure the Rads are DT5 and the UFH is DT5 and get them as balanced as you can and work from there. if the UFH loop has a 130% of the design heat loss in the area it is designed for and the rads say only have 100% then the UFH area will over heat quicker and you would need to find a way to restrict the UFH output. This may be possible by reducing the DT lower on the UFH and reduce its output or control 1 loop if there is 2 UFH loops in the hallway.</p>
<p>I know its confusing, I am half guessing how your system is set up and assembled so I may be making some assumptions, also balancing the systems needs quite a few measurements.</p>
<p>If you can get an actuator and UFH stat in the hall way and close down 1 loop in the hallway this would control half the output in the hall and control this area if it over heats.</p>
<p>If there are 2 loops in the UFH hallway you may be able to close one down to reduce the output. they system then could have the curve raised and allow more power to the rads and less would be in the UFH circuit in this one area.</p>
<p>I am hopefully giving you options here if the system is out of design.</p>