									IVT Greenline high pressure switch and electrical cassette errors - Ground Source Heat Pump (GSHPs)				            </title>
            <link>https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/</link>
            <lastBuildDate>Sat, 14 Nov 2026 17:29:40 +0000</lastBuildDate>
                        <title>RE: IVT Greenline high pressure switch and electrical cassette errors</title>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/paged/2/#post-64762</link>
                        <pubDate>Tue, 30 Jun 2026 18:22:16 +0000</pubDate>
                        <description><![CDATA[&nbsp;
Can you post pics of the cassette and heat pump set up, pipe work between them if possible? High pressure trips, assuming temp sensors and pressure sensors are reading correctly are ...]]></description>
<p>I have an IVT Greenline HT Plus C heat pump that is continually having errors when heating the hot water cylinder.</p>
<p>Both “Electrical cassette” and “High pressure switch” errors are happening several times a day. Acknowledging the error lets the heat pump continue, but clearly something is wrong. Previously I had problems with “High HTF Delta” that seemed to be this problem, which seemed to be fixed by changing the pipes.</p>
<p>Any thoughts on what needs to be done?</p>
<p><a href="https://youtu.be/Bs2WULUaMxM?si=KdKUWXKaHrQhE6Tg">https://youtu.be/Bs2WULUaMxM?si=KdKUWXKaHrQhE6Tg</a></p>
<p>Can you post pics of the cassette and heat pump set up, pipe work between them if possible? High pressure trips, assuming temp sensors and pressure sensors are reading correctly are pretty much always flow related. Is there a strainer in line with the hot water tank? Is the tank heating as quickly as it used to? If you start up your rads, does the system run normally? </p>
						                            <category domain="https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/">Ground Source Heat Pump (GSHPs)</category>                        <dc:creator>alincork</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/paged/2/#post-64762</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/paged/2/#post-49868</link>
                        <pubDate>Mon, 06 Oct 2025 07:42:44 +0000</pubDate>
                        <description><![CDATA[OK.  You dont say whether it is from the feeds to/from the DHW cylinder carrying hot liquid from the heat pump, or from the cylinder itself.  Either way its a simple plumbing issue.
If its ...]]></description>
<p>Hi, thanks for the reply. The air is from the domestic hot water cylinder that is contained inside the heat pump. </p>
<p>OK.  You dont say whether it is from the feeds to/from the DHW cylinder carrying hot liquid from the heat pump, or from the cylinder itself.  Either way its a simple plumbing issue.</p>
<p>If its from the hot tank itself then most likely something is wrong with either the input valves (normally a pressure reducing valve and a pressure relief valve) or the (normally white) expansion vessel, or alternatively your mains pressure has dropped to below the level set by the pressure reducing valve.  This is regular plumbing and any plumber used to UVCs <em>should</em> be able to sort it out.  </p>
<p>If its from the feeds to the hot tank then it depends on whether, in your heat pump, these are somehow separate from or connected to the system that feeds the space heating.  If the latter (most likely) then the system needs a top up or the expansion vessel (normally red) needs repressurising.  Again nothing that any plumber used to central heating systems of all types shouldn't be able to sort out. </p>
<p>If the hot feeds to the tank are somehow separate from the hot feed to the space heating (or even refrigerant not water, which is just possible) then its a bit more heat pump specific and you <em>may</em> need someone familiar with heat pumps and preferably ground source heat pumps.  The installer who put my ashp in also does repairs for GSHPs so Im guessing that at least some other installers do similar, the basic components are little different so someone with a bit of intelligence who can read should be able to work it out (I realise that excludes some installers, sadly).</p>
<p>Hope that helps, the manual might point you in the right direction to distinguish between the cases above if you dont already know.</p>
						                            <category domain="https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/">Ground Source Heat Pump (GSHPs)</category>                        <dc:creator>JamesPa</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/paged/2/#post-49868</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-49860</link>
                        <pubDate>Sun, 05 Oct 2025 20:37:12 +0000</pubDate>
                        <description><![CDATA[Hi, thanks for the reply. The air is from the domestic hot water cylinder that is contained inside the heat pump.]]></description>
                        <content:encoded><![CDATA[<p>Hi, thanks for the reply. The air is from the domestic hot water cylinder that is contained inside the heat pump. </p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/">Ground Source Heat Pump (GSHPs)</category>                        <dc:creator>Get</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-49860</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-49859</link>
                        <pubDate>Sun, 05 Oct 2025 20:18:18 +0000</pubDate>
                        <description><![CDATA[I know absolutely nothing about this unit but it sounds like either it needs topping up with water or the expansion vessel needs to be repressurised.  Is the air from the heating side or the...]]></description>
<p>. I noticed it low and let air out of the water tank by loosening the nut at the front. The air is all out but I noticed the gauge dropping even lower after doing this. I have no idea how to get the air pressure back up to the correct setting. Would anyone be able to advice how to reset the pressure. Thank you.</p>
<p>I know absolutely nothing about this unit but it sounds like either it needs topping up with water or the expansion vessel needs to be repressurised.  Is the air from the heating side or the ground loop side?</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-49859</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-49855</link>
                        <pubDate>Sun, 05 Oct 2025 18:56:26 +0000</pubDate>
                        <description><![CDATA[Hi, apologies for piggybacking on this thread. I also have a C11 IVT Greenline Heat pump. The company that I got to install it back in 2011 are no longer in business and I always find it dif...]]></description>
                        <content:encoded><![CDATA[<p>Hi, apologies for piggybacking on this thread. I also have a C11 IVT Greenline Heat pump. The company that I got to install it back in 2011 are no longer in business and I always find it difficult to get anyone to service the pump or even ask for advice on the pump. I am having an issue at the minute with low pressure registering on the pressure gauge at the top of the pump. It is currently sitting at around 1/2 a bar and I think it is supposed to be set between 1 and 2 bar. I noticed it low and let air out of the water tank by loosening the nut at the front. The air is all out but I noticed the gauge dropping even lower after doing this. I have no idea how to get the air pressure back up to the correct setting. Would anyone be able to advice how to reset the pressure. Thank you.</p>
12048
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-49855</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-46084</link>
                        <pubDate>Mon, 12 May 2025 08:50:21 +0000</pubDate>
                        <description><![CDATA[Your system seems to be more modern than mine, mine was installed in 2011. My advice would be to speak to Zak @Alto Energy. zak.crozier@altoenergy.co.uk, www.altoenergy.co.uk. www.altoenergy...]]></description>
                        <content:encoded><![CDATA[<p>Your system seems to be more modern than mine, mine was installed in 2011. My advice would be to speak to Zak @Alto Energy. <span>zak.crozier@altoenergy.co.uk, www.altoenergy.co.uk. www.altoenergy.co.uk Tel: 01993 220699. They were extremely helpful if you can't get hold of Zak try Sam Keats who is their design manager. They also sell spare parts. I got my hoses direct from them and saved over £500 from what a 'so called' heat pump expert maintenance company tried to charge me.</span></p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/">Ground Source Heat Pump (GSHPs)</category>                        <dc:creator>abbote</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-46084</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-46007</link>
                        <pubDate>Fri, 09 May 2025 16:12:03 +0000</pubDate>
                        <description><![CDATA[OK, so when the HP comes on it becomes obvious.It&#039;s on the setting on the right (one one where the curves are curves, not straight lines).]]></description>
                        <content:encoded><![CDATA[<p>OK, so when the HP comes on it becomes obvious.<br />It's on the setting on the right (one one where the curves are curves, not straight lines).</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/">Ground Source Heat Pump (GSHPs)</category>                        <dc:creator>tdudgeon</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-46007</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-46006</link>
                        <pubDate>Fri, 09 May 2025 15:35:24 +0000</pubDate>
                        <description><![CDATA[I looked at increasing the pump flow. Presumably this is the pump you refer to?
There seem to be 3 settings, controlled by the green button. The symbols suggest the are something related ...]]></description>
                        <content:encoded><![CDATA[<p>I looked at increasing the pump flow. Presumably this is the pump you refer to?</p>
11374
<p>There seem to be 3 settings, controlled by the green button. The symbols suggest the are something related to the heat curves. It's not obvious which is the current setting</p>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-46006</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-46003</link>
                        <pubDate>Fri, 09 May 2025 09:54:47 +0000</pubDate>
                        <description><![CDATA[@abbote thanks for that advice.There was a bit of air in the cylinder, but removing it hasn&#039;t helped.The trip on the electrical cassette seems OK (in that it can&#039;t be pressed in).The hoses w...]]></description>
                        <content:encoded><![CDATA[<p>@abbote thanks for that advice.<br />There was a bit of air in the cylinder, but removing it hasn't helped.<br />The trip on the electrical cassette seems OK (in that it can't be pressed in).<br />The hoses were changed last summer.</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-46003</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-45983</link>
                        <pubDate>Thu, 08 May 2025 10:57:53 +0000</pubDate>
                        <description><![CDATA[Here are the reported most common causes for both.
Common Causes High Pressure Switch error:Blocked or dirty condenser coil (insufficient airflow)Faulty fan (not expelling heat from the con...]]></description>
                        <content:encoded><![CDATA[<p>Here are the reported most common causes for both.</p>
<p>Common Causes High Pressure Switch error:<br />Blocked or dirty condenser coil (insufficient airflow)<br />Faulty fan (not expelling heat from the condenser)<br />Overcharged refrigerant<br />Non-condensable gases in the system<br />Faulty high-pressure switch<br />Closed or restricted water circuit (e.g., blocked heat exchanger)<br /><br />Troubleshooting Steps:<br />Check outdoor fan operation – Is it running when the unit is on?<br />Inspect and clean condenser coils – Remove debris and dust.<br />Verify flow in water circuit – Check for pump operation, airlocks, or valve closures.<br />Measure refrigerant pressure – Requires a licensed technician.<br />Reset the system – Some models allow manual reset after the pressure drops.</p>
<p>Common Causes: Electrical Cassette<br />Faulty PCB<br />Loose or corroded electrical connections<br />Power fluctuations or unstable voltage<br />Failed sensor input or internal relay<br /><br />Troubleshooting Steps:<br />Power cycle the unit – Turn off power for a few minutes, then restart.<br />Check cable connections – Look for loose terminals or moisture in connections.<br />Inspect PCB for burnt spots or corrosion.<br />View error code specifics – IVT systems often display a numeric code; let me know the code for detailed steps.<br />Check fuse and power supply – Ensure stable voltage and no blown fuses.</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-grounds-source-heat-pump-gshps/ivt-greenline-high-pressure-switch-and-electrical-cassette-errors/#post-45983</guid>