                        <description><![CDATA[@jamespa I think many installers feel that they have not completed an installation if they haven’t fitted an LLH, TRV’s on every radiator (without leaving instructions to leave them wide ope...]]></description>
                        <content:encoded><![CDATA[@jamespa I think many installers feel that they have not completed an installation if they haven’t fitted an LLH, TRV’s on every radiator (without leaving instructions to leave them wide open as they are only really to tidy up the look of the emitter in most rooms!&#x1f609;) a secondary pump plus an on/off thermostat to knacker the heat pump when it has a hysteresis of 0.1 degree C and has no pity at all on that heat pump’s life; extra satisfaction may be gained by these same installers if they can include a third pump and a buffer tank too! &#x1f609; Ruefully, Toodles.]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/6/#post-42757</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/6/#post-42742</link>
                        <pubDate>Fri, 21 Feb 2025 11:15:59 +0000</pubDate>
                        <description><![CDATA[The spec for your model calls for a total of 39l for &#039;cooler climates&#039;.  I think we are in the &#039;warmer climate&#039; region according to the relevant EU directive, but since we are also very damp...]]></description>
<p>And then the defrost. I’m if the secondary circuits are meant stay open due to the lower temps and not enough volume and the primary loop, is there a way to protect the system during heavy defrost conditions. I assume it’s total system volume. </p>
<p>I’ve got 65L in the UFH that I know from the UFH design. I’ve got 6 big rads, so maybe another 60 to 80. The the pipes to and from things. </p>
<p>maybe 175L total volume for 11.2kw systems. Is that optimal? I know paul Spence put a post about 25L per KW, which is 280L for me.  Or is this overkill?  Again, I’m told so many different things it’s hard to make heads or tails of it. </p>
<p>The spec for your model calls for a total of 39l for 'cooler climates'.  I think we are in the 'warmer climate' region according to the relevant EU directive, but since we are also very damp I would be wanting 39l plus.  There is absolutely no harm in 'additional' volume; 175l should be fine. </p>
<p>I dont know about 25l/kW, this might be a figure to reduce cycling but you haven't yet posted a problem with cycling and, since your heat pump appears to be well matched size wise to your house you most likely wont!</p>
<p>There should be no need to 'protect' the system, if it needs <em>so</em> much heat for defrost that it is going to materially cool the house then something radical needs to be done (like a very large volumiser which can somehow be separated) but again no evidence you need this nor have I heard of a case where it is needed.  The amount of energy required for defrost is pretty predictable so it shouldn't be a problem.</p>
<p>For now Id balance the system as best you can, adjust the WC curve if needed to get the house at the right temperature with everything running constantly and all the stats set above the desired temperature, and see how it goes.  We may not get another deep frost until next season, so you may not know for a while!  </p>
<p> Again, I’m told so many different things it’s hard to make heads or tails of it. </p>
<p>Heating systems, not just those with heat pumps, can be quite complex, because there are so many variations and variables.  That said, the underlying physics, and it <em>is </em>physics, is actually very simple, so a little genuine <em>understanding</em> goes a long way.  However only a proportion of 'professionals' actually seem to understand it, many go 'by experience' and some spout pure BS.  That's just how it is.  The simple test is to ask for an explanation and, if one isn't forthcoming, or it doesn't make sense, or its 'because we have been doing it like that for 40 years, then doubt the advice!</p>
<p>Not content with that problem, we make heating systems <em>more</em> complex by trying to impose control that, in reality, we dont have because of the thermal mass of the house and the fact that rooms within the house aren't thermally separated to any material extent.  This is counter-productive to cost in many, perhaps most, cases with a heat pump (and even in at least some cases with a boiler).  However the manufacturers of 'smart' controls would go out of business if they told us that!</p>
<p>Time and time again we find on this forum that KISS applies (Keep it simple, stupid).  Most houses, including, Im fairly certain, yours, would be best (cheapest <em>and</em> most comfortable) run on a single zone (with <em>perhaps</em> TRVs on a small minority of emitters, eg in some bedrooms), 24*7 on pure weather compensation and without system separation.  Unfortunately only some installers currently do this!</p>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/6/#post-42742</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/6/#post-42736</link>
                        <pubDate>Fri, 21 Feb 2025 10:07:15 +0000</pubDate>
                        <description><![CDATA[@jamespa thanks again. It makes sense. Before the new bigger LLH, I had a 35mm piped distribution header. There was no blending there, only when I put the UFH flows too high, past I assume t...]]></description>
                        <content:encoded><![CDATA[@jamespa thanks again. It makes sense. Before the new bigger LLH, I had a 35mm piped distribution header. There was no blending there, only when I put the UFH flows too high, past I assume the 28l a min on the primary, and this was only on the rad circuit. As soon i turned down a flow on the UFH a bit, the rads went straight back to the primary temp sensor. That was kind of my guide of when to stop increasing flows in the UFH]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/">Air Source Heat Pumps (ASHPs)</category>                        <dc:creator>davidnolan22</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/6/#post-42736</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/6/#post-42735</link>
                        <pubDate>Fri, 21 Feb 2025 09:41:35 +0000</pubDate>
                        <description><![CDATA[Hi Gary,
Yes, I think I’m getting the hang of it and whats gone on this winter. And yes, during the cold snap previously there was not enough energy going into the floor constantly. But ...]]></description>
                        <content:encoded><![CDATA[<p>Hi Gary,</p>
<p>Yes, I think I’m getting the hang of it and whats gone on this winter. And yes, during the cold snap previously there was not enough energy going into the floor constantly. But I’ve been told to set the flow to 45 and use the stats.</p>
<p>After I set the flow much lower, in the low 30s and ran it constant, it ran so much better. I think my system design temp is 36 at -3 not 45. Despite that not being the plan…..<br /><br /></p>
<p>Anyhow, the new header has not helped matters much, but I’ll get it back balanced as best I can and I think I will be able to get it to work.</p>
<p>And then the defrost. I’m if the secondary circuits are meant stay open due to the lower temps and not enough volume and the primary loop, is there a way to protect the system during heavy defrost conditions. I assume it’s total system volume. <br /><br /></p>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/6/#post-42735</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/6/#post-42729</link>
                        <pubDate>Fri, 21 Feb 2025 08:49:41 +0000</pubDate>
                        <description><![CDATA[@davidnolan22 I will continue to think about this. 
We could do with a comment from @bobtskutter on the pump arrangement  , he is good on the hydronics.  It feels like there is the potentia...]]></description>
                        <content:encoded><![CDATA[<p>@davidnolan22 I will continue to think about this. </p>
<p>We could do with a comment from @bobtskutter on the <a href="https://renewableheatinghub.co.uk/forums/postid/42689" target="_blank" rel="noopener">pump arrangement</a>  , he is good on the hydronics.  It feels like there is the potential for the 4 pumps on the emitter side to create a racetrack around the LLH which could exclude or inhibit energy from transferring across from the heat pump side. </p>
<p>Furthermore since, at max output, you need a DT of 6 there is the likelihood of  quite a sizable penalty due to the mixing.  Given that you appear to have separate returns from the various emitter loops, I can see an easy way to get a handle on flow rates either side. </p>
<p>I would also imagine that its impossible to keep this in balance with zones opening/closing, so treating the whole house as a single zone, which you are currently doing, may well be sensible.</p>
<p>Its good that it is at least almost working, and agree it shouldn't be this difficult.  The installer really needed to think about why it was sensible to have 5 separate pumps in the system and how they were going to work seamlessly together, but evidently he didnt.</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/6/#post-42729</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/5/#post-42724</link>
                        <pubDate>Fri, 21 Feb 2025 06:38:18 +0000</pubDate>
                        <description><![CDATA[How were you running it before the cold snap.  If it was setback overnight your screed would cool down and depending on how thick it is could take an enormous quantity of heat.  The heat pum...]]></description>
                        <content:encoded><![CDATA[<p>How were you running it before the cold snap.  If it was setback overnight your screed would cool down and depending on how thick it is could take an enormous quantity of heat.  The heat pump will be able to get to a higher temp but as the return is cool it will be running flat out so the heat is going somewhere.  That’s either into tonnes of concrete or to the outside if it’s badly insulated which doesn’t sound like the case </p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/5/#post-42724</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/5/#post-42711</link>
                        <pubDate>Thu, 20 Feb 2025 21:57:59 +0000</pubDate>
                        <description><![CDATA[That’s a really thoughtful reply. Thank you. It’s a great help. 
lots to ponder. My view has been consistently that i don’t need much more than 35 to 38 degrees at -3, and that’s the most i...]]></description>
                        <content:encoded><![CDATA[<p>That’s a really thoughtful reply. Thank you. It’s a great help. <br /><br /></p>
<p>lots to ponder. My view has been consistently that i don’t need much more than 35 to 38 degrees at -3, and that’s the most it will ever get to. all the pumps and balancing has been tough and the defrost were definitely a problem. <br /><br /></p>
<p>I think the pump outside can keep me warm, and, I’ll get to a point where it will. But, it should not be this hard.  The new header has not current helped. But I’ll try to get to learn it better in the next few days. </p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/5/#post-42711</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/5/#post-42708</link>
                        <pubDate>Thu, 20 Feb 2025 20:41:51 +0000</pubDate>
                        <description><![CDATA[Fundamentally emitter output increases with flow temperature.  Once the system has got to the point where flow temperature is such that the emitters are emitting 11.2kW, the flow temperature...]]></description>
<p>I mean, if I put in 45 on fixed flow as the flow temp, open all Zones and leave it,  it will never get there, spends hours ( I’m mainly UFH in screed) and it won’t ever reach a temp higher than 38. But, what temp would I expect a 11.2kw heat pump to reach on a 16kw emitter surface at dt 25. I think 38 might be the highest it can get to and needs. Or am thinking about this wrong. </p>
<p>Fundamentally emitter output increases with flow temperature.  Once the system has got to the point where flow temperature is such that the emitters are emitting 11.2kW, the flow temperature can go no higher because the return temperature is such that 11.2kW is needed to get it back up again.  </p>
<p>So if your emitters are 'oversized' and your heat pump 'right sized' then you will end up 'capping' your flow temperature.</p>
<p>The fact they cant go higher doesn't matter, so long as your house is warm, which you say it isnt.  </p>
<p>If some bits of the house are warmer than others it might be a balance problem, but balancing when you have so many pumps sounds like a nightmare.</p>
<p>Of course another possibility is the 11.2kW never reaches the emitters, unfortunately we cant tell easily because of the LLH.  Whats the deltaT when its 'maxed out'?  Your primary flow rate 28l/min will move 9.8kW at DT5 (Im assuming system is filled with water not glycol, if its glycol then the amount moved is less).  So you should be seeing DT6 or thereabouts when maxed out.</p>
<p>I trust your UFH screed has plenty of insulation underneath it, otherwise some of the energy delivered from the heat pump is lost downwards.</p>
<p>260sqm isnt enormous, my house is 200 sq m and runs on a single radiator zone directly from the pump inside the (Vaillant) heat pump casing.  Would it be practical to bypass the LLH and all but one of the pumps (ideally switchably so you could 'try' it.  Then you could guarantee that all the heat produced by the heat pump was ending up in the house at maximum efficiency, and that you had plenty of water for defrost.  Or do you know for certain that all the pumps are necessary to overcome flow resistance (seems unlikely!)- I guess what I'm really asking is - was there a good reason to make this installation so complex?</p>
<p>From what you have said so far there is no obvious cause, except possibly that the heat pump is pretty much right-sized but the losses in the LLH combined with balance issues prevent the heat getting to where it is needed, while the system separation reduces the volume of water for defrost, the effect of which is exacerbated by large emitters even though this is normally good news</p>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/5/#post-42708</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/5/#post-42700</link>
                        <pubDate>Thu, 20 Feb 2025 17:36:45 +0000</pubDate>
                        <description><![CDATA[I mean, if I put in 45 on fixed flow as the flow temp, open all Zones and leave it,  it will never get there, spends hours ( I’m mainly UFH in screed) and it won’t ever reach a temp higher t...]]></description>
                        <content:encoded><![CDATA[<p>I mean, if I put in 45 on fixed flow as the flow temp, open all Zones and leave it,  it will never get there, spends hours ( I’m mainly UFH in screed) and it won’t ever reach a temp higher than 38. But, what temp would I expect a 11.2kw heat pump to reach on a 16kw emitter surface at dt 25. I think 38 might be the highest it can get to and needs. Or am thinking about this wrong. </p>
<p>I hear what you’re saying about system volume. I think they may have just needed a volumiser on the return and not the LLH they put in. But who am I….. ahhhh this is driving me nuts </p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/5/#post-42700</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/mitsubishi-ecodan-8-5kw-monobloc-ftc5-defrost-mode/paged/5/#post-42699</link>
                        <pubDate>Thu, 20 Feb 2025 17:00:03 +0000</pubDate>
                        <description><![CDATA[if 38 at -3 is specified as an end point on the curve, the target temp will never go above 38.  If however you shut zones down then it may overshoot because it cant modulate down.  Is it jus...]]></description>
<p><strong>What are your weather compensation settings, is there a maximum target flow temperature specified somewhere in the settings</strong></p>
<p>weather comp 38 at -3 to 25 at 12.  It can get to 45 degree flow no problem if I sort closing zones off, so the machine is capable of getting there</p>
<p>if 38 at -3 is specified as an end point on the curve, the target temp will never go above 38.  If however you shut zones down then it may overshoot because it cant modulate down.  Is it just this that is the reason you cant get above 38? </p>
10498
<p>Not just defrosts, If i put in 45 degrees and leave it, it will top out after a few hours at 36-37, even in mild weather if all zones are open. I think this is because my emitter sizing is big I have a lot of surface area. My heat loss is 11kw, but my emitters to 50% bigger than that, and no evenly so which is annoying.  When it defrosts, this makes it a bit worse </p>
<p>Emitters bigger = good, you can run at a lower flow temperature = higher COP</p>
<p>Not sure why it takes hours to get to 45 if you 'put in' 45 (where are you putting in 45?).  How long the flow take to get to temperature when you are doing DHW?</p>
<p>I have a faint hunch that, because you have large emitters, you are running at a low flow temperature, which of course means more water is needed to supply the energy for defrost.  Linked to this I suspect that for some reason to with the balancing, although primary and secondary are connected, defrost water is effectively being drawn from the primary only or principally from the primary</p>
<p>32mm pex has wall thickness 3mm so has an ID of 26mm.  16m contains only 7l water, no way thats going to be enough at 35C</p>
<p>However the 'hours to get to 45 when set to 45' needs teasing out.</p>]]></content:encoded>