									I&#039;m new to all this. Am I setting off on the right foot? - Air Source Heat Pumps (ASHPs)				            </title>
            <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/</link>
            <lastBuildDate>Sat, 14 Nov 2026 18:30:37 +0000</lastBuildDate>
                        <title>RE: I&#039;m new to all this. Am I setting off on the right foot?</title>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/paged/2/#post-20251</link>
                        <pubDate>Sat, 08 Jul 2023 14:19:15 +0000</pubDate>
                        <description><![CDATA[Thanks, both. I knew that I had to validate getting the energy to the radiators but haven&#039;t yet set about analysing it. Presently, the boiler plumbing is 28mm which splits to 22mm for the tw...]]></description>
                        <content:encoded><![CDATA[<p>Thanks, both. I knew that I had to validate getting the energy to the radiators but haven't yet set about analysing it. Presently, the boiler plumbing is 28mm which splits to 22mm for the two CH and DHW valves. There is just over 2m of 22mm before splitting into two primaries, each of which supplies one 'wing' of the L-shaped property. If necessary, it would be relatively straight-forward to replace this section with 28mm when replacing the DHW cylinder. All branches from the primaries are 15mm, transitioning to 10mm for vertical drops in the walls to downstairs radiators. I am confident that there is only one radiator on each 10mm section but I need to investigate what is on each 15mm branch. There are 15 radiators in all and suspect that 12 will need replacing. The Kitchen/Diner has two tall 'Designer' radiators and I suspect that either a 3rd will need adding or the heating supplementing with an A-A heat pump, which would have the additional benefit of providing cooling in the summer months. Given the expense that all this will entail, should I consider a less efficient high temperature heat pump as an option?</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/">Air Source Heat Pumps (ASHPs)</category>                        <dc:creator>IanMK13</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/paged/2/#post-20251</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/paged/2/#post-20244</link>
                        <pubDate>Sat, 08 Jul 2023 08:13:39 +0000</pubDate>
                        <description><![CDATA[Good spot- I put kW then copied them. I suppose they amalgamated it with J/s]]></description>
                        <content:encoded><![CDATA[<p>Good spot- I put kW then copied them. I suppose they amalgamated it with J/s</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/">Air Source Heat Pumps (ASHPs)</category>                        <dc:creator>DougMLancs</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/paged/2/#post-20244</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20221</link>
                        <pubDate>Thu, 06 Jul 2023 07:14:06 +0000</pubDate>
                        <description><![CDATA[kW/s, that&#039;s not a real unit (yes I know it&#039;s what heat geek says).  You mean kW.
The heat geek figures are a bit better than I remembered, 10mm microbore must have a thin wall.  Good enoug...]]></description>
<p>This chart from Heat Geek shows the capacity of different pipe sizes. 10mm microbore is 1.15kW/s at a DT of 5. My heat pump is on the last day of install today  (9kW Panasonic) and I have 28mm put in to the split then 22mm primaries and 10mm drops to all the rads. System has been designed for 35C flow temp, open loop and a DT of 5 and the designer was happy to keep all the existing pipe work. It just depends on your heat loss results- mine was about 55W/m2.</p>
<p>kW/s, that's not a real unit (yes I know it's what heat geek says).  You mean kW.</p>
<p>The heat geek figures are a bit better than I remembered, 10mm microbore must have a thin wall.  Good enough for many cases then so long as it feeds a single rad.</p>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20221</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20219</link>
                        <pubDate>Thu, 06 Jul 2023 06:12:56 +0000</pubDate>
                        <description><![CDATA[This chart from Heat Geek shows the capacity of different pipe sizes. 10mm microbore is 1.15kW/s at a DT of 5. My heat pump is on the last day of install today  (9kW Panasonic) and I have 28...]]></description>
                        <content:encoded><![CDATA[<p> </p>
4137
<p>This chart from Heat Geek shows the capacity of different pipe sizes. 10mm microbore is 1.15kW/s at a DT of 5. My heat pump is on the last day of install today  (9kW Panasonic) and I have 28mm put in to the split then 22mm primaries and 10mm drops to all the rads. System has been designed for 35C flow temp, open loop and a DT of 5 and the designer was happy to keep all the existing pipe work. It just depends on your heat loss results- mine was about 55W/m2.</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20219</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20218</link>
                        <pubDate>Thu, 06 Jul 2023 04:57:48 +0000</pubDate>
                        <description><![CDATA[We are slightly confusing two things here, the total system capacity (~12kW?) and the emitter capacity (linked to pipe size).  They are separate but linked.
Pipes to individual emitters mus...]]></description>
                        <content:encoded><![CDATA[<p>We are slightly confusing two things here, the total system capacity (~12kW?) and the emitter capacity (linked to pipe size).  They are separate but linked.</p>
<p>Pipes to individual emitters must have sufficient diameter to take the demand from that emitter (which must be physically large enough to emit the required power at the temp difference between it and the room - note for rads this is non linear - the power emitted varies as (emitter temp-room temp)^1.3).  Where several pipes join in a manifold or through branches, the feed to the branch must have sufficient capacity to accommodate the total, culminating in the pipes at the output of the heat pump ('primarie's) which must be able to accommodate the total system capacity.</p>
<p>The key parameters are:</p>
<p>1.Flow temp, which defines emitter temp, which defines how much power is lost by the emitter to the room (strictly its the <em>average </em>temp of the emitter, its colder at the output end than at the input end).  Typically 35-55C for ASHP, 55-75 for boiler.  </p>
<p>&amp;</p>
<p>2.Emitter delta T (temp loss across emitter or between flow and return) which is a result of the above and the flow rate through the emitter.  Typically 5C-7C for <i>ASHP,</i> 20C for boilers.  The principal reason ASHPs are designed for a lower emitter deltaT is that it means that the <em>average</em> emitter temp is nearer to the flow temp, meaning that the flow temp can be lower for a given emitted power, and ASHPs are more efficient at lower flow temps</p>
<p>So because the delta T is less for an ashp, you need larger pipes, because the heat transferred from the pipes to the emitters) is flow velocity*cross sectional area*deltaT*volumteric heat capacity, and velocity is limited because of pipe erosion and noise.  So a 22mm pipe which is good for perhaps 30kW at a deltaT of 20C, is good for only 6-8kW at a deltaT of 5C.  </p>
<p>I <em>think</em> a 10mm pipe is good for about 2.5kW at a deltaT of 20 and 1.5m/s (which is at the upper end), so thats only 625W at a deltaT of 5, insufficient for many rooms in a typical house.  You could run at a deltaT of 7 maybe, upping it a bit, but its still not going to get to 1kW+ which is likely to be needed if your total demand is 12kW.  Realistically many rads need 15mm.  But you also have to think about manifolds/junctions and the sizing of the pipes to them.</p>
<p>For a 12kW total demand you will need, I think, 28mm from the pump to the point it first splits.  if it splits about equally (eg upstairs/downstairs) then 22mm each should be good.  Then 15mm to the emitters (but 10mm will be sufficient for small/well insulated rooms).  this is rough and ready though, you need to do the calcs on room demand etc.</p>
<p>Hope that gives you some high level pointers, in the end there is however no substitute for doing the spreadsheet!</p>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20218</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20216</link>
                        <pubDate>Wed, 05 Jul 2023 19:39:40 +0000</pubDate>
                        <description><![CDATA[@ianmk13 The pipework replacement was easier for me as I live in a bungalow. Your house does sound better insulated than mine so maybe you could get away with the 10mm pipework. I think John...]]></description>
                        <content:encoded><![CDATA[@ianmk13 The pipework replacement was easier for me as I live in a bungalow. Your house does sound better insulated than mine so maybe you could get away with the 10mm pipework. I think John Cantor talks about that on his webiste somewhere but it may mean running at a higher temperature and hence lower COPs. However if your heat loss is low enough the cost may not be prohibitive.]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20216</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20215</link>
                        <pubDate>Wed, 05 Jul 2023 19:22:43 +0000</pubDate>
                        <description><![CDATA[What would you like to know?
The property is an unusual design : split level, L-shaped, 2 storey; not a rectangular box. Insulated cavity wall, outside skin mainly brick, but some wood clad...]]></description>
<p>Can you tell us something about your house and water usage pattern?</p>
<p>What would you like to know?</p>
<p>The property is an unusual design : split level, L-shaped, 2 storey; not a rectangular box. Insulated cavity wall, outside skin mainly brick, but some wood cladding. Glazing predominantly on the eastern side. Double glazing throughout, but 1990's standard apart from 3 sets of bi-folds we had installed a couple of years ago. I used my detailed knowledge of the construction to use the standard heat-loss spreadsheets to arrive at my figure of 13.8kW.  I suspect the boiler isn't working in condensing mode as it's normal to see plumes of steam from the boiler.</p>
<p>There are 2 of us in the house and we have showers rather than use the bath. I forgot to mention that the figure of 13.658kW will include use of the gas hob in the kitchen.  The gas stove in the lounge wasn't used last winter (the ultrasonic remote upsets the cat !)</p>
<p>@bontwoody</p>
<p>I don't relish the idea of having the first floor up and chopping the plasterboard walls to replace all the 10mm pipes. It will be hard enough to move the 10mm pipes to fit replacement radiators (both the pitch and distance to wall are wrong). I was tempted to reduce the flow temperature but thought it best to ask the plumber to do it when he services the boiler.  We have similar ideas regarding supplementary heating (and cooling).</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20215</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20214</link>
                        <pubDate>Wed, 05 Jul 2023 17:45:47 +0000</pubDate>
                        <description><![CDATA[@ianmk13 Sounds as if you have a lot of the same issues as I had. in the end i changed the 10mm pipes for 15mm and upped several radiators. I ran the gas CH at a low temperature during the w...]]></description>
                        <content:encoded><![CDATA[<p>@ianmk13 Sounds as if you have a lot of the same issues as I had. in the end i changed the 10mm pipes for 15mm and upped several radiators. I ran the gas CH at a low temperature during the winter to see how the house would cope when I switched to a HP. I have also put a A-A heat pump in the kitchen as the radiator gap was small without having a very long run, plus I get cooling in the summer if needed.</p>
<p>I have a small wood burning stove in the lounge to top up should we want to be extra toasty. You can see all I have done at my blog, the address is below.</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20214</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20213</link>
                        <pubDate>Wed, 05 Jul 2023 17:11:37 +0000</pubDate>
                        <description><![CDATA[OK 30MWh/yr is quite high.  Can you tell us something about your house and water usage pattern?]]></description>
<p>How embarrassing. I dropped a zero.  I must stop ignoring those Specsavers reminders 😉 </p>
<p>Thanks @JamesPa.  It looks as though my pessimistic approach was unnecessary, then.</p>
<p>OK 30MWh/yr is quite high.  Can you tell us something about your house and water usage pattern?</p>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20213</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20212</link>
                        <pubDate>Wed, 05 Jul 2023 16:32:46 +0000</pubDate>
                        <description><![CDATA[How embarrassing. I dropped a zero.  I must stop ignoring those Specsavers reminders 😉 
Thanks @JamesPa.  It looks as though my pessimistic approach was unnecessary, then.]]></description>
                        <content:encoded><![CDATA[<p>How embarrassing. I dropped a zero.  I must stop ignoring those Specsavers reminders 😉 </p>
<p>Thanks @JamesPa.  It looks as though my pessimistic approach was unnecessary, then.</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/im-new-to-all-this-am-i-setting-off-on-the-right-foot/#post-20212</guid>
Served from: renewableheatinghub.co.uk @ 2026-11-14 18:30:37 by W3 Total Cache