So plumbers have sent over adjusted calcs………
This puts all rooms basically bar my office, the main bathroom and downstairs toilet at watt deficits with current rads even at delta 20 (which might explain a lot!).
I've looked at delta 20, the MCS correction factor of 0.2325 (think that's basically 16.5 as Derek pointed out).
Doubling the eskimo heights should fix downstairs (including doubling the width of the hall rad), but MCS calc would still put the Living 2 down by 400W if ignored Eskimo's correction factor. I'll have to have a think about that, I suspect the Eskimos are actually quite good, but they've got such a deficit atm due to poor calcs in first place. For context Living 2 is down by 382W if delta 210 atm, 1286W at delta 16 and 2520W using MCS factor.
Upstairs is down other than my office as per above (explains why it's 21C in here quite easily). The deficits at delta 20 look around 300-370W between bedrooms, going up to 920W using the MCS factor (Basically 4.3x oversize).
They could be fixed with K2 up sizing, but the landing would suffer still according to the calcs.
I wonder if upstairs would just get away with it with the heat rising.
Problem I have is it's hard to judge the system as it is in mild weather etc.
@crimson With our system being commissioned on 19th. February last year - with a very mild spell for some days, I had to approximate the balancing work until the winter arrived. November of last year cooled down so I commenced the rounds of tweaking and all is well now. (I even query over 0.5 degrees C. between rooms now!) This difference is nearly always due to solar gain on the south side of the house and the ‘node’ that senses being in the living room that faces north east. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @toodles@crimson With our system being commissioned on 19th. February last year - with a very mild spell for some days, I had to approximate the balancing work until the winter arrived. November of last year cooled down so I commenced the rounds of tweaking and all is well now. (I even query over 0.5 degrees C. between rooms now!) This difference is nearly always due to solar gain on the south side of the house and the ‘node’ that senses being in the living room that faces north east. Regards, Toodles.
Thanks Toodles, hopefully I can get there.
Does look like a lot of rad changes incoming however due to a complete mess up by the plumbers but will see. Glad that calcs show even using delta 20 everything is off. I didn't things were so badly off, but maybe explains why the ASHP cycles like crazy.
4 days later, with guests over the weekend I left things mostly alone. I did end up changing the secondary pump speed to 1/3 as lock shields became a bit noisy in the living room. Temps seemed to have stabilised around 19.5-20C downstairs. 20.5C upstairs mostly (with lockshields right down). TRVs essential upstairs as rooms get too warm (19.5C is ideal really) unless windows open a crack. What's clear is the office is the most performant room and that I guess reflects the updated calcs that imply it's the only correctly sized one currently rad-wise.
I'm still awaiting confirmation when radiators will be swapped out. I'll have a bit of time next week to try the method of using a heater timed off and on to broadly see how many watts down we are.
All looks a bit of a mess, where's the lagging.
I was working on a Grant this week and I’m ripping out all those valves, extra pumps and low loss header.
Installing a new 3 port making the system open loop.
Technical Manager & Professional Installer: Ultimate Renewables
Posted by: @kenboneAll looks a bit of a mess, where's the lagging.
I was working on a Grant this week and I’m ripping out all those valves, extra pumps and low loss header.
Installing a new 3 port making the system open loop.
Hi Ken, lagging is done just used an old photo for the detail of pipes. I’m hoping for rad upsize replacement then will look later in the year for removal of unnecessary parts. What areas do you work in?
I've ripped all these pumps and low Loss Header out the last few days. Just a spoiler, the system still works.
Technical Manager & Professional Installer: Ultimate Renewables
that’s ideally what I’d like to have done to (once current plumbers sort the rad sizing under the contract, I don’t want them touching anything else). Its clear temps drop across the plant room alone across all this mess. Hopefully I can find someone locally to do this later in the year ahead of next winter!
@kenbone bloody hell. That would have freed up a lot space in the utility/plant room 😂
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editorbloody hell. That would have freed up a lot space in the utility/plant room 😂
probably about a grand's worth as well. which could have been not spend during the original install.
its not just for laughs that we keep banging on about single loop....simpler, cheaper, more efficient
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
- 26 Forums
- 2,112 Topics
- 46.4 K Posts
- 70 Online
- 3,408 Members
Join Us!
Latest Posts
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 18 minutes ago
-
Buffers, hot water and cooling
I have a 13kW Grant ASHP, installed to the letter of Gr...
By Prunus , 27 minutes ago
-
@downfield That sounds like a very good idea to me, my ...
By Toodles , 4 hours ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 7 hours ago
-
RE: Wood burner with ASHP - direct air?
@sune is ideal to answer this, but I think he's on vaca...
By Mars , 24 hours ago
-
RE: Say hello and introduce yourself
Hi @topher - you might be interested to see this very r...
By Transparent , 24 hours ago
-
RE: No-code, plug-and-play monitoring for your heat pump
We've got a svenar heat pump controller en route and lo...
By benson , 2 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 2 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 3 days ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 3 days ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 3 days ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 3 days ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 3 days ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 5 days ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 6 days ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 1 week ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 1 week ago
-
RE: Cleaning up after gas meter removed
@agentgeorge Likewise in the loft space; we have 300mm ...
By Toodles , 1 week ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
This particular example is one of the worst I have seen...
By JamesPa , 1 week ago