                        <description><![CDATA[A quick update.After running the system for a full year with weather compensation my actual annual ASHP energy usage is 5280kWh.That&#039;s for both heating on 24/7 @22ºC indoors and hot water @4...]]></description>
                        <content:encoded><![CDATA[<p>A quick update.<br />After running the system for a full year with weather compensation my actual annual ASHP energy usage is 5280kWh.<br />That's for both heating on 24/7 @22ºC indoors and hot water @48ºC.</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/">Air Source Heat Pumps (ASHPs)</category>                        <dc:creator>MarkC</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/17/#post-10140</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/17/#post-8036</link>
                        <pubDate>Tue, 05 Apr 2022 12:24:48 +0000</pubDate>
                        <description><![CDATA[Posted by: @peterr 
@markc 
An interesting read and sounds like a good result in your swap from LPG to ASHP.
It sounds as though we have a very similar system to you, UFH downstairs and r...]]></description>
                        <content:encoded><![CDATA[<blockquote data-userid="1358" data-postid="8034" data-mention="peterr">
<div class="wpforo-post-quote-author"><strong> Posted by: @peterr </strong></div>
<p>@markc </p>
<p>An interesting read and sounds like a good result in your swap from LPG to ASHP.</p>
<p>It sounds as though we have a very similar system to you, UFH downstairs and radiators upstairs, just wondering if I could ask you a few questions:</p>
<p>1. Do you get much thermal gain, if so how does your system respond?</p>
<p>2. Do you notice much cooling effect on the internal temperature due to wind/rain?</p>
<p>3. What coverings do you have over your UFH?</p>
<p>We have solid oak flooring over our UFH in all rooms except the kitchen.  It was installed when we first moved in and were running an LPG boiler.  The kitchen has ceramic tiles and generally seems to hold a more consistent temperature.  The rest of the downstairs rooms fluctuate a lot more if the outside temperature drops.  I am thinking that the insulating layer of wood increases the latency of the UFH.  We are also running with weather compensation, but I am still tweaking it occasionally to try and get the curve right - currently 43C at -3C ambient going to 20C at 18C ambient.  I am beginning to wonder if the lower end could be dropped if we didn't have the wooden flooring!</p>
<p>Yes, we have 6m of glazed sliding doors on the south facing elevation of the property. So when it's sunny approx 1/5 of the main living area gets a bathed in sunlight. Pushes the room air temp up to 24/25ºC.</p>
<p>I imagine the system responds by stopping as the return flow will not be cooler than the flow out.</p>
<p>The ASHP is located on the north elevation so constantly in the shade.</p>
<p>No, however we are surrounded by trees so the effect of cold wind isn't as pronounced as it might be on an exposed property I suspect.</p>
<p>We have a 60mm slab of screed covered with ceramic tiling. Yes I suspect the wooden floor is insulating and also not able to retain the heat as well as a screed floor can do. I suspect this is why I'm able to run the heating 24/7 for the same cost as compared to turning it off over night and then having to reheat the slab.</p>
<p>With my 'curve' (actually a slope) I do have to manually adjust the heating down as the outside temp increases.</p>
<p>-5ºC to 10ºC outside the room temp is a stable 22ºC but as the outside temp goes over 10ºC I adjust the FTC. In this last spell of 20ºC daytime outside temp I was running the system at -6. Probably the solar gain effect.</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/17/#post-8036</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/17/#post-8034</link>
                        <pubDate>Tue, 05 Apr 2022 11:57:47 +0000</pubDate>
                        <description><![CDATA[@markc 
It sounds as though we have a very similar system to you, UFH downstairs and radiators upstairs, ju...]]></description>
                        <content:encoded><![CDATA[<p>@markc </p>
<p>We have solid oak flooring over our UFH in all rooms except the kitchen.  It was installed when we first moved in and were running an LPG boiler.  The kitchen has ceramic tiles and generally seems to hold a more consistent temperature.  The rest of the downstairs rooms fluctuate a lot more if the outside temperature drops.  I am thinking that the insulating layer of wood increases the latency of the UFH.  We are also running with weather compensation, but I am still tweaking it occasionally to try and get the curve right - currently 43C at -3C ambient going to 20C at 18C ambient.  I am beginning to wonder if the lower end could be dropped if we didn't have the wooden flooring!</p>]]></content:encoded>
						                            <category domain="https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/">Air Source Heat Pumps (ASHPs)</category>                        <dc:creator>Peterr</dc:creator>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/17/#post-8034</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/16/#post-7872</link>
                        <pubDate>Fri, 01 Apr 2022 11:30:29 +0000</pubDate>
                        <description><![CDATA[@morgan It&#039;s currently set at 40ºC flow @ -5ºC outside and 20ºC flow @ 20ºC outside.
Although at the moment the overriding offset is at -5.]]></description>
                        <content:encoded><![CDATA[<p><span>@morgan </span>It's currently set at 40ºC flow @ -5ºC outside and 20ºC flow @ 20ºC outside.</p>
<p>Although at the moment the overriding offset is at -5.</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/16/#post-7872</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/16/#post-7864</link>
                        <pubDate>Fri, 01 Apr 2022 09:39:23 +0000</pubDate>
Nice1.  What temps did you set your weather compensation curve at?]]></description>
<p>Nice1.  What temps did you set your weather compensation curve at?</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/16/#post-7864</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/16/#post-7862</link>
                        <pubDate>Fri, 01 Apr 2022 09:02:11 +0000</pubDate>
Good results and looks like you made the right decision. Even allowing for the warmer November you&#039;re still using a lot less power.  I did the same sort of experiment and reckoned w...]]></description>
<p>Good results and looks like you made the right decision. Even allowing for the warmer November you're still using a lot less power.  I did the same sort of experiment and reckoned weather compensation was 15-20% less but I was using 45 deg fixed flow. I also kept the temperature the same all day in both scenarios. </p>
<p>The other thing you've mentioned that isn't often talked about is comfort.  I prefer a constant temperature rather than ups and downs and weather compensation does this better than thermostats, even when maintaining a constant temperature.  </p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/16/#post-7862</guid>
                        <title>RE: Annual running figures are in!</title>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/16/#post-7859</link>
                        <pubDate>Fri, 01 Apr 2022 08:46:05 +0000</pubDate>
                        <description><![CDATA[I now have a full years metered ASAP energy usage that I can report on.
The headline is that energy usage has come in just about bang on what was expected.
And the system is performing ...]]></description>
                        <content:encoded><![CDATA[<p>I now have a full years metered ASAP energy usage that I can report on.</p>
<p>The headline is that energy usage has come in just about bang on what was expected.</p>
<p>And the system is performing very well. We have had no issues with the pump.</p>
<p>According to the MCS estimates that were produced, the energy requirements for heating and DHW were 21,571 kWh.</p>
<p>And the estimated energy usage for the ASHP was 6765 kWh.</p>
<p>For the year the system has actually used 6441kWh for DHW and heating.</p>
<p>Comparing ASHP to LPG which is what I moved from:</p>
<p>2020 I spent £1500 on LPG. This was with the heating set at 18ºC from 22:00 until 17:00 and 22ºC 17:00 until 22:00.</p>
<p>At the time of commissioning (the good ol’ days!) I was paying 15p per kWh for electricity. Assuming prices would have remained stable.</p>
<p>£0.15 x 6441 = £966 for a house that is constantly 22ºC.</p>
<p>So all things being equal and assuming all energy prices have risen a similar percentage, the move from LPG to ASHP does ‘seem’ to be the right move.</p>
<p>That being said:</p>
<p>Even with the RHI deducted the new system cost £3000. The installation was £14K, RHI is paying back £11K.</p>
<p>I had to pay £1000 to have the LPG tank removed.</p>
<p>I’ve pulled out a couple of months for comparison.</p>
<p>In April the system was running on a set flow temp of 50ºC and the heating was controlled with internal thermostats.</p>
<p>As discussed in other chats/threads this is done so the system matches the usage of a gas boiler type installation so customers are more comfortable with how to control it.</p>
<p>We also had the thermostats set to:</p>
<p>22:00 - 6:00 = 16ºC</p>
<p>06:00 - 18:00 = 18ºC</p>
<p>18:00 - 22:00 = 22ºC</p>
<p>22ºC feels comfortable for us so the house did feel cool and I was attempting to use as little energy as possible. Not a comfortable setting for us.</p>
<p>The heating used 838.4 kWh and delivered 2285 kWh of heating.</p>
<p>April COP was 2.6</p>
<p>Average outside temp was 6.38ºC</p>
<p>As we got into October and the energy usage began to rise we started looking into optimising the system on the forum and changed the settings to weather compensation.</p>
<p>As part of this move we set the system up to deliver a constant 22ºC internal temperature, 24 hours a day. The thermostats no longer controlled the system as the weather compensation regulates the flow temperature.</p>
<p>The heating used 593.1 kWh and delivered 2339 kWh of heating.</p>
<p>November COP was 3.7</p>
<p>Average outside temp was 8.08ºC</p>
<p>Granted, April was slightly colder than Nov outside. Both months required a similar amount of heating.</p>
<p>But, when using a set 50ºC flow temp, April used a third MORE electricity to deliver a cooler, less comfortable internal temperature.</p>
<p>So with a set up like ours, (UFH downstairs and rads upstairs) my take is that weather compensation and 24/7 heating is the way to go.</p>
1160
1161
1162]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/16/#post-7859</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/16/#post-4656</link>
                        <pubDate>Mon, 13 Dec 2021 07:58:47 +0000</pubDate>
sorry, by external I meant 3rd party. Same set up as me then.
thanks]]></description>
<p>sorry, by external I meant 3rd party. Same set up as me then.</p>
<p>thanks</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/16/#post-4656</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/16/#post-4653</link>
                        <pubDate>Mon, 13 Dec 2021 07:27:25 +0000</pubDate>
                        <description><![CDATA[Posted by: @kev-m 
@markc 
really good data that supports what a lot of us are trying.  A couple of questions (1) I think you are using weather compensation but still using external thermo...]]></description>
                        <content:encoded><![CDATA[<blockquote data-userid="15" data-postid="4631" data-mention="kev-m">
<div class="wpforo-post-quote-author"><strong> Posted by: @kev-m </strong></div>
<p>@markc </p>
<p>really good data that supports what a lot of us are trying.  A couple of questions (1) I think you are using weather compensation but still using external thermostats; is that right?  To give my supplier credit, that's how they set up my system and (2) Do you have the total energy delivered over the two periods?  That would be another good comparison. (sorry if I've missed this)</p>
<p>I've also heard the 'people will complain if rads aren't hot' comment.</p>
<p>Kev   </p>
<p>I'm assuming by external you mean external to the ASHP, not outside in the fresh air.</p>
<p>1. I have 4 internal thermostats (Heatmiser and Nest) and they are all set to 25ºC (so effectively now calling for heat all the time). The ASHP uses it's own external (i.e. outside the house) thermistor to read ambient outside air temp and set the flow heat.</p>
<p>2. 8-9/12 produced 218.4kWh, 10-11/12 produced 255.9kWh</p>]]></content:encoded>
                        <guid isPermaLink="true">https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/16/#post-4653</guid>
                        <link>https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/fine-tuning-your-ashp-performance/paged/16/#post-4650</link>
                        <pubDate>Sun, 12 Dec 2021 18:29:20 +0000</pubDate>
                        <description><![CDATA[@adaml 
The modelling tool that I produced appears to give reasonably accurate results for Ecodan 14 kW ASHP&#039;s, provided that fairly accurate data for heat demand and total heat emitter out...]]></description>
                        <content:encoded><![CDATA[<p>@adaml </p>
<p>The modelling tool that I produced appears to give reasonably accurate results for Ecodan 14 kW ASHP's, provided that fairly accurate data for heat demand and total heat emitter output capacity is entered. It could be used for other sizes of Ecodan heat pumps and those from other manufacturers, provided that operating data obtained from standard testing procedures can be obtained and entered into the spreadsheets to replace that for the 14 kW Ecodan.</p>
<p>You could still do the modelling for your ASHP, by assuming that the gas boiler is not functioning, so only the heat pump was operating. The modelling tool would calculate the required water flow temperature for ambient air temperatures from 20C down to -15C.</p>]]></content:encoded>